3" underground conduit question
Junkman
Northeastern CT
When the power company representative spoke to me about the underground conduit, he told me that 3" PVC was ok from the meter socket out to the pole; however, he wants a metal long sweep where it goes up the pole, and that sweep needs to be grounded to the ground rod at the pole. From the sweep, he said I can use PVC going up the pole.
I just don't understand why the long sweep needs to be metal and why it needs to be grounded. The only thing that I can think of is that it might be easier to pull the wire through. It is the grounding that has me baffled. Could you explain this to me? thanks
mm08822
The metal sweep is so your pull rope doesn't cut through the inside radius. When pulling tension is high ( long run, lots of bends) it can happen. For simple runs I wouldn't bother. However, POCO rules so just do it.
The grounding is to ensure the sweep has better contact with wet(ter) soil (yeah, I know!)
Also ensures a low resistance path back to the xformer neutral that it could take out the fuse on line side if fault occurs.
Bert_
NW Iowa
Plastic bends can rub through when pulling wire.
If it's buried deep enough the nec has no requirement to ground it. But it's the power company's conduit so they have the ultimate say
J
Junkman
Northeastern CT
Thank you for that information. This morning, I called the Power Company and spoke with the field engineer, who told me the same. When I went to the supply house to pick up the conduit, the fellow behind the counter told me not to use a poly rope for the pull rope, because it would cut into the PVC. The utility only requires a lightweight rope, so they can attach it at one end and pull it through the other.
The trench will be dug tomorrow, and the bottom will be lined with 6" of fine sand. On Wednesday, I will be setting the pipe into the trench. The electrical inspector said he would be there at 3 PM to inspect everything. On Thursday, the trench will be backfilled. Once backfilled, I can call for the utility to install the wires. Was told that they can't schedule the wire pull until it is inspected, backfilled, and certified by the inspector.
Chuckster in NJ
Hunterdon County NJ
Listen to the field engineer because they are responsible for pulling wire into this conduit.
There is a reason the "fellow behind the counter" is working there and most of the time it is because the guy couldn’t make it in the trade. ;)
We always installed long radius Galvanized Rigid sweeps at the pole even if it was on a "privately owned" run.
Adaylate
Washington
Just out of curiosity, how long is your run?
I just went through getting a new service and my local poco used a fiberglass or resin sweep 90. My run was 150' with a 90 at each end. They supplied the mule tape to pull.
Good luck with your project!
tarbellb
Oregon
Funny, my poco required me to run fiberglass long sweeps for my meter to pad vault
at $250/ea x3 I was a bit ticked until I pulled my 4/0 triple leg through my own 2" PVC run. Had a winch hooked up, was working hard....