Upon repair, I would not splice 3 conductors together. Instead splice onto the end of the 1/0 and into the center of the other conductor used to feed the 2 poles on the fuse block.....it's one less splice and the amount of material to compress in the split bolt connect is less.
FWIW, I'm planning on using a Polaris block like this one: https://www.zoro.com/polaris-insulated-multitap-connector-162-in-w-ipl10-3b/i/G4119254/

Thanks for the advice, but I'm not sure that I follow, specifically how to splice the connectors. I've spliced much smaller stranded wires via soldering but I can't imaging soldering something like this. How do you splice such large conductors?
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,775
Location
NW Iowa
This is a pretty typical scene. The original air handler had a single circuit and the new one needs to be split in two. I've spliced them plenty of times before. I use H crimps but if the HVAC guy does it himself it's going to be something like a split bolt.

Split bolts are fine but a lot of people don't get them tight enough. That's what this looks like, a loose connection. If you're splicing 1/0 it needs to be TIGHT with two wrenches.
 
OP
G

gba2331

Well-known member
Joined
Sep 22, 2021
Messages
782
I unwrapped the other connector, here are 2 shots. It doesn't look as bad, but there still seem to be scortch-marks. Whats really scary is that I was able to easily unscrew this connector. I'm assuming that they must have tightened it, but if so its hard to understand how I was able to unscrew it by hand. At least the AL feed wire had been coated with Noalox...

IMG_1541.jpgIMG_1546.jpg
 
OP
G

gba2331

Well-known member
Joined
Sep 22, 2021
Messages
782
Here is the install with the Polaris connectors, they seem really sturdy. I trimmed back all of the wires, coated the Al feeds with Noalox, then tightened all as much as I could with an Allen key (long handled). I don't have a socket hex wrench for this size, so I wasn't able to torque it - is tightening a much as possible sufficient or should I get the socket and "do it right"?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,878
Location
Richmond, VA
The funny thing on the bad install is that noalox is not a requirement across the board. Only if the wire manufacturer calls for it. So they used it, when they probably did not need to, and got the rest of it wrong.

Doesn't hurt, though

Considering the current, I'd Torque it, but don't loosen and retighten. That requires cutting the wire back
 