Lift is functional. I haven't changed the cord over to 30A yet but I figured it would have no issue lifting the Miata. I want to check it with a clamp meter to see the draw.
 

Attachments

  • IMG_9485.JPG
    IMG_9485.JPG
    1.2 MB · Views: 38
To avoid these ads, REGISTER NOW!

AffableCurmudgeon

Well-known member
Joined
Jan 26, 2009
Messages
1,906
Location
Triad Area NC
Lift is functional. I haven't changed the cord over to 30A yet but I figured it would have no issue lifting the Miata. I want to check it with a clamp meter to see the draw.
Looks good! You should try it with your heaviest vehicle @ 20 amp and check the draw with clamp meter. From the people who own that lift, I have heard that they don't have any issues. One person I know uses a high magnetic breaker, the rest don't.

PS: Are you going to put a bigger leveling piece under the rear left post?
 
OP
S

Sawbladz

Well-known member
Joined
Jun 9, 2009
Messages
103
Location
Collingwood, ON, Canada
I'll be checking that once I have a heavier vehicle available.

I used a couple scrap pieces of 3/4 plywood to shim up the columns to get them more level. I have a fair bit of slope front to back in the garage. Side to side is perfectly level. I will be cutting a few pieces of 2x10 bigger than the baseplates which should be the right thickness to make it perfectly level. Might need additional small shims under them to make the columns plumb. I will need to buy or build longer ramps since that will impact the approach angle. Too many low cars.
 

AC-WC

Well-known member
Joined
Jan 22, 2023
Messages
772
Location
NE, Indiana
I don't have your lift but my Triumph C7000 has the same electrical requirements. I installed the 10 ga wire, 30 amp 110 breaker, 20 amp plug because they don't make a 30 amp in standard plug format. Routinely lift 4000 lbs with 0 issues. Been working fine for 2 years. I really struggled with the wire coming from the pump to the plug as it can't be more than 12 ga but it works. I've read others statements it's the initial startup that can spike to 30 amps. Never investigated on my own as the lift works perfectly.
I wouldn't hesitate to do it again.
 

kbuhagiar

Well-known member
Joined
Dec 27, 2005
Messages
1,748
Location
Escondido, CA
I don't have your lift but my Triumph C7000 has the same electrical requirements. I installed the 10 ga wire, 30 amp 110 breaker, 20 amp plug because they don't make a 30 amp in standard plug format. Routinely lift 4000 lbs with 0 issues. Been working fine for 2 years. I really struggled with the wire coming from the pump to the plug as it can't be more than 12 ga but it works. I've read others statements it's the initial startup that can spike to 30 amps. Never investigated on my own as the lift works perfectly.
I wouldn't hesitate to do it again.
I'm glad this works for you but it just seems wrong. You have a 20-amp plug on a 30-amp breaker, that's gotta be against code, and even more so isn't providing you with the proper circuit protection.

I really think that this was a mistake in the instructions. There are thousands of these lifts, basically identical, that are working - and have been working - just fine with a 120V/20amp circuit. This 30 amp requirement doesn't make sense.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,268
Location
Coastal NJ
I don't have your lift but my Triumph C7000 has the same electrical requirements. I installed the 10 ga wire, 30 amp 110 breaker, 20 amp plug because they don't make a 30 amp in standard plug format. Routinely lift 4000 lbs with 0 issues. Been working fine for 2 years. I really struggled with the wire coming from the pump to the plug as it can't be more than 12 ga but it works. I've read others statements it's the initial startup that can spike to 30 amps. Never investigated on my own as the lift works perfectly.
I wouldn't hesitate to do it again.
Not sure what you mean by standard plug format. But these will carry 30A and meet code on a 120V circuit.

1713293373696.png

TT-30R


1713293411575.png

5-30R
 

blakeb1969

Member
Joined
Jan 19, 2025
Messages
7
Hi all, I read all the posts above but still not sure. I just bought a used Atlas 9000 2 post lift, it is currently wired for 220 on a 2 pull 30 amp breaker. I don't have 220 in my garage, and was wondering if I could run it on a 120 outlet. I am just going to be using it occasionally for oil changes etc. Three questions: !) will 120 run the hydraulic motor at all. 2) If so will it keep tripping a breaker. 3) Do I have to do anything special to convert or just use the white wire as as the neutral.
 

Attachments

  • 20250118_142906.jpg
    20250118_142906.jpg
    620.3 KB · Views: 15
  • 20250118_142919.jpg
    20250118_142919.jpg
    385.3 KB · Views: 20

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,826
Location
VT
Hi all, I read all the posts above but still not sure. I just bought a used Atlas 9000 2 post lift, it is currently wired for 220 on a 2 pull 30 amp breaker. I don't have 220 in my garage, and was wondering if I could run it on a 120 outlet. I am just going to be using it occasionally for oil changes etc. Three questions: !) will 120 run the hydraulic motor at all. 2) If so will it keep tripping a breaker. 3) Do I have to do anything special to convert or just use the white wire as as the neutral.
  1. Probably better to start your own thread
  2. Going to need to post a pic of the motor/ wiring diagram
  3. If you can convert it the wire(s) need to be moved somewhere, likely at the motor
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,013
Location
Modesto, CA
No way to answer that without a pic of the motor nameplate.

What is the rating of the breaker that feeds the garage?

Regardless, if the motor is 240v only, your options are, run a new feeder to the garage or use a 120v to 240v transformer. However, if the 120v feeder to your garage is power limited you may have issues with nuisance trips of the feeding breaker

And i agree with above

Start a new thread instead of hi-jacking this one
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
A TT-30 receptacle is for travel trailers only, there are other choices for 30A receptacles.
 

blakeb1969

Member
Joined
Jan 19, 2025
Messages
7
Thanks for all the responses and help!!!
I got some more information about the Atlas 9000 Motor and attached some pictures.
Motor = 2hp
factory wired at 230VAC.
60HZ,
15-18AMP,
208-230 Volt,
See pictures

The wiring to my garage is the Ameron Green Box ran to a 20amp breaker then 250ft of buried 10-2 wire brought into the barn. From there I have several outlets ran off of the 10-2 feed with 12-2 and 14-2 wiring.
Not a very good setup, I am considering rerunning a larger wire and putting a breaker box into the garage. I assume that I could put a much larger breaker than 20amp on the temp pole. At this time though I am wanting to run the lift off one of outlets or straight to the 10-2 wiring.
 

Attachments

  • 20250120_105519.jpg
    20250120_105519.jpg
    537.2 KB · Views: 16
  • 20250120_105546.jpg
    20250120_105546.jpg
    651.8 KB · Views: 16
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,013
Location
Modesto, CA
Hi all, I read all the posts above but still not sure. I just bought a used Atlas 9000 2 post lift, it is currently wired for 220 on a 2 pull 30 amp breaker. I don't have 220 in my garage, and was wondering if I could run it on a 120 outlet. I am just going to be using it occasionally for oil changes etc. Three questions: 1) will 120 run the hydraulic motor at all. 2) If so will it keep tripping a breaker. 3) Do I have to do anything special to convert or just use the white wire as as the neutral.

if you dont have 240v available in the garage how did you wire the lift to a 240v 30a circuit? where did you put the 30a DP breaker if you dont have a breaker box in your garage per your reply below?

1. no you cant run it on 120v. the motor is 208-230v only

2. the breaker is tripping because you are running a 240v motor on 120v. that just isnt gonna work.

3. this motor cannot be converted to 120v operation. you need to run a new feeder.

Thanks for all the responses and help!!!
I got some more information about the Atlas 9000 Motor and attached some pictures.
Motor = 2hp
factory wired at 230VAC.
60HZ,
15-18AMP,
208-230 Volt,
See pictures

The wiring to my garage is the Ameron Green Box ran to a 20amp breaker then 250ft of buried 10-2 wire brought into the barn. From there I have several outlets ran off of the 10-2 feed with 12-2 and 14-2 wiring.
Not a very good setup, I am considering rerunning a larger wire and putting a breaker box into the garage. I assume that I could put a much larger breaker than 20amp on the temp pole. At this time though I am wanting to run the lift off one of outlets or straight to the 10-2 wiring.
oh boy this is a huge mess

no you cant use a much larger breaker. you have #14 NM which should be on a 15a breaker. not to mention 250' of #10 with a motor load is gonna have massive voltage drop on startup. another reason for tripping breakers

honestly this is way over your head. get an electrician to set this up properly for you before you burn the house down.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,538
Location
Richmond, VA
if you dont have 240v available in the garage how did you wire the lift to a 240v 30a circuit? where did you put the 30a DP breaker if you dont have a breaker box in your garage per your reply below?

1. no you cant run it on 120v. the motor is 208-230v only

2. the breaker is tripping because you are running a 240v motor on 120v. that just isnt gonna work.

3. this motor cannot be converted to 120v operation. you need to run a new feeder.


oh boy this is a huge mess

no you cant use a much larger breaker. you have #14 NM which should be on a 15a breaker. not to mention 250' of #10 with a motor load is gonna have massive voltage drop on startup. another reason for tripping breakers

honestly this is way over your head. get an electrician to set this up properly for you before you burn the house down.
He's buying the lift... It isn't hooked up to 120v and tripping a breaker.

@blakeb1969 you need to run a new electrical service to make this work.

I'd start your own thread with specifics and we can help advise
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,013
Location
Modesto, CA
He's buying the lift... It isn't hooked up to 120v and tripping a breaker.

@blakeb1969 you need to run a new electrical service to make this work.

I'd start your own thread with specifics and we can help advise
huh? he literally said he bought it wired it to a double pole 30a breaker and showed pics of it installed. also stated its tripping breakers.

agreed on starting a new thread
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,538
Location
Richmond, VA
huh? he literally said he bought it wired it to a double pole 30a breaker and showed pics of it installed. also stated its tripping breakers.

agreed on starting a new thread
Reread it. The previous owner has it on a 30a 240v and he's asking if it will trip the breaker on 120v in his shop. He didn't say he's trying to run it on 120
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,013
Location
Modesto, CA
Reread it. The previous owner has it on a 30a 240v and he's asking if it will trip the breaker on 120v in his shop. He didn't say he's trying to run it on 120
he didnt say anything about previous owner and he specifically said "will it keep tripping a breaker." which leads one to believe that it is tripping the breaker right now...
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,826
Location
VT
Reread it. The previous owner has it on a 30a 240v and he's asking if it will trip the breaker on 120v in his shop. He didn't say he's trying to run it on 120

he didnt say anything about previous owner and he specifically said "will it keep tripping a breaker." which leads one to believe that it is tripping the breaker right now...

I got a warning the other day for a very similar situation where an ancient thread got bumped and I was trying to figure out what another user was talking about. Perfect reason why the new user should start his own thread...

@wyliesdiesels what post are you looking at? See number 51
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,268
Location
Coastal NJ
Three questions: !) will 120 run the hydraulic motor at all. 2) If so will it keep tripping a breaker. 3) Do I have to do anything special to convert or just use the white wire as as the neutral.
It sure does change when the "If so" is removed.
I'm sure my English teacher could explain the phraseology. Something about the sequential dependency of the 3 clauses.
Bottom line is ain't no way that 240V motor gonna run onna buck twenty volts. Boy would she be pissed.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,013
Location
Modesto, CA
It sure does change when the "If so" is removed.
I'm sure my English teacher could explain the phraseology. Something about the sequential dependency of the 3 clauses.
Bottom line is ain't no way that 240V motor gonna run onna buck twenty volts. Boy would she be pissed.
the incorrect word he used was "keep"

if he had just said 'if so, will it trip the breaker', it would have had an entirely different implication and context.
 
Last edited:

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,826
Location
VT
@wyliesdiesels fair enough.

I guess @mike93lx and I both took this to be the used lift was wired from the previous owner for 220

Hi all, I read all the posts above but still not sure. I just bought a used Atlas 9000 2 post lift, it is currently wired for 220 on a 2 pull 30 amp breaker. I don't have 220 in my garage, and was wondering if I could run it on a 120 outlet. I am just going to be using it occasionally for oil changes etc. Three questions: !) will 120 run the hydraulic motor at all. 2) If so will it keep tripping a breaker. 3) Do I have to do anything special to convert or just use the white wire as as the neutral.

Certainly a lot to be desired with how this is phrased if we're being pedantic. Wth is a 2 pull breaker?
 
Last edited:

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,826
Location
VT
2 pole. he misspelled it
I know.

Back to the question, I don't see anyway to wire this for 120v, do you?

1737493909518.jpeg


Assuming not, then the questions about breaker tripping are moot, he cannot run a 240v motor in his 120v shop.*


*Barring options that we shouldn't discuss here to keep it uncluttered
 