4 post lift wiring recommendation

Poolshark314

Well-known member
Joined
Jul 5, 2021
Messages
658
Location
MD
I've got an Atlas Pro 9000 4-post lift with the 120v motor and the manual states it requires a 30 amp breaker, even though the plug is a standard 120v outlet 3 prong. I called support and they only recommended worrying about it if you notice the breaker tripping a lot. So far, it seems to be tripping a fair amount.

I think what I'd like to do is build an extension cord with 2 duplex outlets and mount it with a magnet on the post with the pump. I was thinking to get an RV 30 amp extension cord, chop the end off, and wire it to a 4x4 box, mounting it to the post with neodymiuim magnets. I would then need to run a 10/2 outlet on the back wall to plug into. Is this overkill?

Should I just use a 20 amp cord since it's really the initial surge from the lift that causes the tripping? What are other folks doing in this situation?
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,065
Location
NJ
Easier and safer to replace the existing cb with a "High Magnetic" version.

I believe Square D QO, Homeline, Siemens and Eaton all make this style cb. They allow for the high inrush current without tripping but provide overload protection In either 15 amp or 20 amp versions.

What panel do you have?
 
OP
P

Poolshark314

Well-known member
Joined
Jul 5, 2021
Messages
658
Location
MD
Easier and safer to replace the existing cb with a "High Magnetic" version.

I believe Square D QO, Homeline, Siemens and Eaton all make this style cb. They allow for the high inrush current without tripping but provide overload protection In either 15 amp or 20 amp versions.

What panel do you have?
Ahh thanks! Didn't know this existed. I have a Square D Homeline and I see they have one. Now I can pivot to a 20 amp extension cord. Thanks @mm08822 !

 