400 service upgrade with meter socket marked 320?

vlocci

Well-known member
Joined
Sep 13, 2005
Messages
115
Location
boston
I'm neck deep in a 400 amp service upgrade that will go from the pole, to an outdoor meter socket with a pair of 200a disconnects/breakers (one to my home panel, and the other to the shop panel)

This is being handled by an electrical contractor and is permitted work in cooperation with my town electrical utility.

What gave me pause was the meter socket side of the outdoor panel /disconnect has a sticker that clearly says "for use with a 320 amp meter"

I asked my contractor, who tells me this is no big deal and completely acceptable. He mentioned that this is on the utility side of the panel and is to their code.

Any reason to doubt him?

Vin
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA
yup 400a service is 320a continuous. if you want 400a continuous you most likely have to upgrade to a CT meter socket and cabinet.

i doubt you need 400a continuous. the load calc that should've been done will show what you need.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,863
yup 400a service is 320a continuous. if you want 400a continuous you most likely have to upgrade to a CT meter socket and cabinet.

i doubt you need 400a continuous. the load calc that should've been done will show what you need.

pfft. my driveway looking all CT meter socket like.

1640133032690.png
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,735
Location
NW Iowa
Some utilities will ct meter a 400A service, others want direct meter. Direct meter in that size means a 320A socket. This usually isn't a choice for the guy putting it in. The utility tells you what to use.
 
To avoid these ads, REGISTER NOW!

Diesel Dan

Well-known member
Joined
Jul 21, 2013
Messages
2,460
Location
TN
That's what I currently have.
400A service (320A socket) two 200A disconnects on a H-frame.
 

86turbodsl

Well-known member
Joined
Jul 1, 2005
Messages
6,558
Location
Michigan
Same as what i have. 320A meter socket with dual lugs, 200A to each breaker panel, one in house, one in barn.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,592
Location
BC
Be thankful you can have 320A direct metering into two 200A panels.

My utility requires the CT setup (above 200A), and a 400A main switch or breaker. Its expensive.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA
sounds like a conflict of interest to me.

PoCos out here dont supply meter pans or mains nor do they have manufacturer spec'd units and they allow 400a (320a) pans without CTs
 