4500 watts on 20 amps

flat350

Well-known member
Joined
Jan 1, 2009
Messages
1,006
Location
illinois
First off I'm a Plumber not an electrician,I want to run a 4500 watt water heater element on a 220/20 amp circuit.Am I pushing it with 18.75 amps on the circuit,it won't be 4500 watts all the time it gets dialed down after an hour or so with a controller to probably 1500-2500 watts.
 
To avoid these ads, REGISTER NOW!

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
I personally would not do it. I always put them on a 2-pole 30. Im not sure if this falls under the 125% rule, if it does, you cant do it anyway. 18.75x125%=23.44. You might want to change that 220 volts to 240
 
OP
F

flat350

Well-known member
Joined
Jan 1, 2009
Messages
1,006
Location
illinois
A 30a circuit would be better,is there a reason you can't run a 30a circuit to feed it?

I have an existing 20a circuit there now,it would be easier I guess to get a 3500 watt element or lower.It's not in a water heater it's in a 1/2 barrel............
 
To avoid these ads, REGISTER NOW!
OP
F

flat350

Well-known member
Joined
Jan 1, 2009
Messages
1,006
Location
illinois
A friend of a friend said I could run 2-4500 watt elements on 240v in series and get 2250 watts at 9.4 amps,is this possible and safe?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,717
Location
NW Iowa
How long will it be on? Doesn't sound like your actually using it for a water heater.

You can load it to 100% if it's less than 3 hours.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,585
Location
BC
A friend of a friend said I could run 2-4500 watt elements on 240v in series and get 2250 watts at 9.4 amps,is this possible and safe?

Possible and safe. Have done similar before. Code legit?... not sure.

How long will it be on? Doesn't sound like your actually using it for a water heater.

You can load it to 100% if it's less than 3 hours.

That was my thinking. He says 1hr at full load. I'd give it a go for a personal project. Worst case the breaker trips on thermal.
 
OP
F

flat350

Well-known member
Joined
Jan 1, 2009
Messages
1,006
Location
illinois
Ran some numbers on the heat I need to make and I'll only need 3000w,that should make things OK on the existing 20a circuit.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,942
Location
Coronado, CA
I often run into territory where what will work is different from what is permitted to be done.

Sometimes I just let my sense of decency be my guide, If the risks are acceptable and the probability of loss is negligible, I just might accept the risk and liability of doing what I can get away with.
 