50 amp welder circuit

dwp99

Well-known member
Joined
Apr 18, 2012
Messages
167
Location
West Coast of Florida
Hello, I have a couple questions about the running of a dedicated circuit for a 200 amp welder.

The welder has a 3 prong plug 2 hot legs and a ground. The 3rd prong is grounded to the chassis of the welder. I want to run 6-2 with a ground from the breaker box to the outlet which is approximately 40 feet away as the romex is routed. I plan to run the romex overhead in the attic and then into 3/4" conduit as it comes out of the ceiling to the outlet.

1. Would this be the correct way to do this?

2. Is 6-2 heavy enough to carry the load of 50 amps?

Thanks
 
To avoid these ads, REGISTER NOW!

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
6 gauge is heavy enough for 50 amps. Note that your welder cord is very light gauge in comparison.

Running the 6 gauge romex through a conduit is legal but you need a big enough conduit. 3/4" pretty dinky.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,243
Location
SE MI
Running the 6 gauge romex through a conduit is legal but you need a big enough conduit. 3/4" pretty dinky.

Right on ! The issue with Romex® in conduit is "fill ratio" or how much air is left around the cable, Hopefully some one will chime in here what the proper size conduit is.

6 gauge Romex® is stranded, but it will be hard to bend. Depending on how many bends you have you might want to use THHN, which means conduit all the way from the box to the receptacle. THHN has more strands which means it is more flexible and easier to pull.
 

DesertSparky57

Well-known member
Joined
Apr 12, 2013
Messages
92
Location
Las Vegas
You could choose to use 8Awg as well. 8/2 is a bit smaller than 6/2. I'd have to check to be sure, I think conduit fill is 4 6awg or 6 8awg in 3/4" EMT, but that is for single THHN. A piece of one inch conduit would be your friend in this case. A nice deep box for the receptacle to go in would be a good idea too. I have always disliked stuffing big dryer or appliance plugs in standard size boxes, just a personal preference though.
 
OP
D

dwp99

Well-known member
Joined
Apr 18, 2012
Messages
167
Location
West Coast of Florida
Thanks for all the help. I'm going to use about 3.5' - 4 ' of conduit the only bend will be at the outlet and it will be in an offset bend. It should slide in with no problem.

I'll use 1" conduit.

Thanks again
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Be sure to use a plastic press on bushing on the cut end of the conduit where the NM enters up in the attic.
 

DesertSparky57

Well-known member
Joined
Apr 12, 2013
Messages
92
Location
Las Vegas
I was just about to mention the bushing where you transition into the pipe. Good call pattenp. Little press on bushings work very well.
 
OP
D

dwp99

Well-known member
Joined
Apr 18, 2012
Messages
167
Location
West Coast of Florida
Be sure to use a plastic press on bushing on the cut end of the conduit where the NM enters up in the attic.

That was going to be my next question. what type of bushing do I use on the raw end of the conduit?

Thanks.

I went back out in the garage and had another look at the cord coming out of the welder. It's 8-2 10-1.
 

Attachments

  • Welder.jpg
    Welder.jpg
    119.2 KB · Views: 40

DesertSparky57

Well-known member
Joined
Apr 12, 2013
Messages
92
Location
Las Vegas
Yup. That sounds right for the cord on a 50A machine. The bushings are a press on type. Wherever you are getting your electrical supplies from should have them.
 