mike93lx
ALLIANCE MEMBER
50ft really isn't long, but it all depends on your loads.
What is running on this service?
What is running on this service?
The water heater and a/c's are what matter.The camper has an electric water heater, lights inside, lights on the deck, radio, ceiling fans, air conditioner, bathroom fan, microwave, fridge.
The furnace uses propane along with the stove
The camper has an electric water heater, lights inside, lights on the deck, radio, ceiling fans, air conditioner, bathroom fan, microwave, fridge.
The furnace uses propane along with the stove
I found 8/4 in a 100 foot length for $150
Says 600V SEOOW Water Resistant
Not sure if this is even an option to consider
Why are you not using the "standard" RV cable which is 6 gauge? 8/4 will "work" but it's not rated for the typical 50A breaker on an RV pedestal. If I was going to do that, I'd de-rate the breaker.Yes it would be plugged into the back of the travel trailer/camper and run under the frame via loop hooks.
Then at the front of the camper it would have to go to the ground and lay on the ground about 7 feet to the outlet pedestal
I want to help, but I'm not digging for appliance specs on your rv
Why are you not using the "standard" RV cable which is 6 gauge? 8/4 will "work" but it's not rated for the typical 50A breaker on an RV pedestal. If I was going to do that, I'd de-rate the breaker.
ThisWhy are you not using the "standard" RV cable which is 6 gauge? 8/4 will "work" but it's not rated for the typical 50A breaker on an RV pedestal. If I was going to do that, I'd de-rate the breaker.
Got it, I was confused by the post above where you said it was going to go about 7 feet to the pedestal.Again, I'm not sure a standard 50 foot premade cord/cable will work and be long enough . It's a possible option for $200 on Amazon
The 100 foot premade cable will definitely be too long and they are like $400
What type?I have a twist lock end connection plug on the camper
the NM-b is not kosher and you will have issues eventually. use the right stuff or dont do it at allI'd rather error on the side of caution and use 50amp with 6/3
That's what's currently installed and there's been zero issues
Take a look. Is it a 50A inlet? It’s good to be sure.No idea never unplugged it and never had to look at it