Planning to install a 60 amp subpanel in the detached garage. It's about 60 ft and would like to run it underground. What size wire? Conduit? How deep? thx
Conduit is not required if you purchase "direct burial" cable like 2-2-2-4 Aluminum Mobile Home Feeder (MHF). If you are do direct burial I would go at least 24" deep.
mm08822
Consider a 100amp panel with main cb on the end of the 60a feeder.
This should ensure enough branch cb space.
mike93lx
Richmond, VA
2-2-4-6 MHF is great for this application. you can breaker it up to 90a (or keep it at the 60 you are desiring) and it comes already bundled.
it will probably be a wash to do #4 al xhhw, so up to you if you want the extra capacity.
i agree on the panel size, get something around 20 spaces, 100a main. you will need to unbond the neutral, so make sure to get something that either includes a ground bar or has one available
something like this
you also need two ground rods or to tie into a UFER.
do not buy URD wire, unless it has a rhw-2/use-2 rating as it is not allowed inside a structure.
matt151617
New Jersey
Just plan for 100 amp and save yourself the trouble of having to do it again in the future. So run MHF in 2" conduit. Don't forget to consider if you'll need Ethernet or cable out there (will the wifi signal reach?); it's easy to add another conduit run while the trench is open.
Also don't forget you need 2 ground rods.
mike93lx
Richmond, VA
Can't do 100a on #2 mhf...max of 90a. That said, it's not easy for a one person shop to exceed 60a
matt151617
New Jersey
Right. 100 amp subpanel/service. Breaker it for 90 at the main panel.
And I thought the same thing until I got an electric vehicle. Charge a car, run a compressor, and turn on a saw and you're already over 60 amps.
Crazyjake8493
Upstate NY
When I did this 10 years ago I ran 2-2-2-4 MHF in 1.5" PVC conduit all the way. 2" would've been a tad easier with the bends. 100-amp 20-space panel in the garage, fed by a 60-amp in the house. 60A was the largest breaker Lowes had in the store at the time. Never felt the need to go up to 90A working by myself, but it's there if I need it.