60 amp Sub Panel Feed?

Buckaroo5

Well-known member
Joined
Oct 18, 2012
Messages
810
Location
Central Ohio
Planning to install a 60 amp subpanel in the detached garage. It's about 60 ft and would like to run it underground. What size wire? Conduit? How deep? thx
 
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,072
Location
SE MI
Conduit is not required if you purchase "direct burial" cable like 2-2-2-4 Aluminum Mobile Home Feeder (MHF). If you are do direct burial I would go at least 24" deep.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,839
Location
NJ
Consider a 100amp panel with main cb on the end of the 60a feeder.
This should ensure enough branch cb space.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,330
Location
Richmond, VA
2-2-4-6 MHF is great for this application. you can breaker it up to 90a (or keep it at the 60 you are desiring) and it comes already bundled.

it will probably be a wash to do #4 al xhhw, so up to you if you want the extra capacity.

i agree on the panel size, get something around 20 spaces, 100a main. you will need to unbond the neutral, so make sure to get something that either includes a ground bar or has one available

something like this

you also need two ground rods or to tie into a UFER.

do not buy URD wire, unless it has a rhw-2/use-2 rating as it is not allowed inside a structure.
 
To avoid these ads, REGISTER NOW!

matt151617

Well-known member
Joined
Dec 17, 2011
Messages
488
Location
New Jersey
Planning to install a 60 amp subpanel in the detached garage. It's about 60 ft and would like to run it underground. What size wire? Conduit? How deep? thx
Just plan for 100 amp and save yourself the trouble of having to do it again in the future. So run MHF in 2" conduit. Don't forget to consider if you'll need Ethernet or cable out there (will the wifi signal reach?); it's easy to add another conduit run while the trench is open.

Also don't forget you need 2 ground rods.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,330
Location
Richmond, VA
Just plan for 100 amp and save yourself the trouble of having to do it again in the future. So run MHF in 2" conduit. Don't forget to consider if you'll need Ethernet or cable out there (will the wifi signal reach?); it's easy to add another conduit run while the trench is open.

Also don't forget you need 2 ground rods.
Can't do 100a on #2 mhf...max of 90a. That said, it's not easy for a one person shop to exceed 60a
 

matt151617

Well-known member
Joined
Dec 17, 2011
Messages
488
Location
New Jersey
Can't do 100a on #2 mhf...max of 90a. That said, it's not easy for a one person shop to exceed 60a
Right. 100 amp subpanel/service. Breaker it for 90 at the main panel.

And I thought the same thing until I got an electric vehicle. Charge a car, run a compressor, and turn on a saw and you're already over 60 amps.
 

Crazyjake8493

Well-known member
Joined
Sep 26, 2014
Messages
3,948
Location
Upstate NY
When I did this 10 years ago I ran 2-2-2-4 MHF in 1.5" PVC conduit all the way. 2" would've been a tad easier with the bends. 100-amp 20-space panel in the garage, fed by a 60-amp in the house. 60A was the largest breaker Lowes had in the store at the time. Never felt the need to go up to 90A working by myself, but it's there if I need it.
 