Well-known member
You haven't given us any proof that there have been problems caused by the wire being sized at minimum either... Show me pictures of damage, wire temp readings, anything at all and we might listen...
What you are preaching is AN acceptable practice, there are others.
What the manufacturer recommends is clearly spelled out on the nameplate. It does not back up your logic. Safest would be to not install the A/C at all, no worries then. Better yet don't install any electric or gas in your house.
I am concerned with installing the most practical circuit I can. Many times I have installed #10 on for a unit that only pulls 15A but calls for a 30A breaker, often times because nobody knows the specs for the unit until it's sitting there. I have also ran 10's for a unit that called for a 50A breaker. What I won't do is support your BS logic.
I told you I have seen the results...
I am doing exactly what the nameplate requires. Exactly.
Over sizing wire is fine, under sizing is NEVER okay.
Never EVER install #10 with 50 amp breaker, EVER. You are not protecting the wire.