Seeing as how this guy is basically saying the NEC is wrong, this has gotten to troll level status.
Wheres a ban hammer when you need one?
![]()
He uses the Urban Legend Code, & the Workplace Gossip Code.

Seeing as how this guy is basically saying the NEC is wrong, this has gotten to troll level status.
Wheres a ban hammer when you need one?
![]()

If it worked here's one of a couple videos from Mike Holt explaining the code
I assume Eddiek is not a reincarnate of Eddie1278 that was banned. Anyone else remember Eddie1278?
From your link -
TA DA !!!
"If a 40A protection device is not capable of carrying the starting current, you can size the protection device up to 225 percent of the equipment load current rating (24A x 2.25 = 54A, next size down 50A)."
It is ALWAYS safer to up size and NEVER safer to down size electrical circuit wiring for HVAC equipment.
I'm just saying the NEC will allow #10 copper to be protected by a 50A breaker on a HVAC condenser unit when needed even though you never see it done or would do it yourself. It seems you are stuck on determining breaker sizes base on conductor size for general purpose circuits. If I was running a 30A circuit for a resistive heating load then the breaker would be 30A because the rule is different.
Water heaters are not part of the discussion, A/C equipment is. The rules for A/C equipment allow for different wire / breaker combos then what is required for other circuits.
Just checking, you realize that describes upsizing the breaker without upsizing the conductors, right?
I am stuck on that. Absolutely stuck on it.
Why? Who reads this forum? Think about it, do you want Joe garage to think he can wire any circuit with a smaller than standard practice?
My situation? I have never once stated I am a certified electrician, in the HVAC trade we install home run circuits and as such because this is not our #1 specialty, we err on the safer side...I would want owners to think this way too.
Locked rotor amp surges are protected well all over the states with 30 amp circuits and 30 amp breakers (typical 24 - 36k Btu systems - the most common), there is no need to up size breaker to 50, all that does in NOT protect the wire.
If you are going to under size wire, you better be a cert. sparky. If you are going to be arguing that you can do this, you need to bring in all the variables, Type wire specifically, conduit and it's material, home run un-interrupted, length of run etc etc
The problem is you were not there. I was. The failure at the bus bar was because the compressor failed, common and run winding shorted.
I am in line completely with what the manufacturers authorize.
It is not safer to under size wiring. The only examples I have been shown is for motors...A condensing unit contains a motor and a compressor, when compressors have liquid refrigerant introduced to them amperage and the associated heat ramp up rapidly, that is why it is important to properly size the wiring.
I not only follow the code I exceed the recommendations.
You can use larger breakers (max over current protection) BUT if you do, you must size the wire accordingly or that breaker is not protecting the wire.
And the electricians have been specific about the conditions that are allowed to use different size wire and breaker ratings. Who is reading the forum doesn't change what the code says.
Why did the bus bar fail? It is rated for way more than the branch circuit breaker. The circuit breaker would trip long before there was enough current going through the bus stab to melt it from over current.
Excessive amperage. That is the entire point, enough excess amperage and heat to melt the breaker and the bus bars...all breakers in a new service panel because the bus bars sustained over extended over amperage.
The point is the wiring in the circuits sustained no damage because they could handle the excessive heat/amps ...appropriately wired. Had there been a #10 copper conducter that wire would have failed and possibly caused a fire.
Excessive amperage. That is the entire point, enough excess amperage and heat to melt the breaker and the bus bars...all breakers in a new service panel because the bus bars sustained over extended over amperage.
The point is the wiring in the circuits sustained no damage because they could handle the excessive heat/amps ...appropriately wired. Had there been a #10 copper conducter that wire would have failed and possibly caused a fire.
My point is that the bus stab is rated way higher than that wire is. If there was enough current to damage the bus then the wire would have melted as well. It was not over current that damaged the bus bar.
Since were back on the topic of melted buss bars, its clear that EddieK also lacks a basic understanding of high resistant connections and the high heat resulting from those...
Wrong again.
When a bus stab is rated for 100a and a 20a breaker is melted on that stab, its logically obvious(well i guess not for some) that high amperage is NOT the cause of the failure.
The cause of the failure is always a high resistant connection.
Read Note "a" of Eddie's table.
60 degree C is used for #1 and smaller. It must very old to be based on TW wire.
All in normal usage today are rated 75 degree or higher (except NM).
For instance they consider #2 the smallest size for 100 amps, but #3 can be used and is perfectly acceptable.
I recommend you consult your CODE book before you put your foot in your mouth yet again.
I assume Eddiek is not a reincarnate of Eddie1278 that was banned. Anyone else remember Eddie1278?
This thread is beyond absured now.
PM has been sent to an admin.