Yeah, there's plenty of rust in there. Not sure there's anything I can do about that.Looking at your pan, it's almost impossible to believe that the drain is perfectly clear
Done. It all drains out as it should.Pour a few quarts of water in the pan and see if it goes down the drain.
Hmm, It's been about 6-8 months since last filter change and it is dirty. I just put everything back together with a clean filter and turned the system back ON. Not sure if I should cancel the service call now.Have you checked your air filter? A plugged filter could cause lack of airflow resulting in the evaporator coil freezing up. This further reduces airflow. The coil will thaw in the off cycle and could allow water to run elsewhere besides the drainpan. This could be the source of the water leaks from the cabinet. The condensate from a condensing furnace is indeed acidic. That is why the flue system must be PVC. Metal pipe will degrade with corrosion from the flue gas.