u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,086
Good point about closing vents. The tstat is in the dining room, which is great for the half dozen times a year we entertain, but is worthless most of the time. I found that closing registers in the dining room has helped regulate temperature in the other rooms downstairs but the upstairs is about 5 degrees warmer than downstairs.

I wonder if a motorized damper that closes downstairs vents at night and an upstairs tstat is a viable option.
problem with that is you've basically zoned it but without proper zoning you now have uncontrolled cooling upstairs. so zone panel and 1 thermostat per zone it is!
 

danski0224

Well-known member
Joined
Jan 29, 2005
Messages
13,921
Location
Near Naperville, IL
Look for the guy that talks technical on his website
Those guys don't have a or much of a website.

99.3% of the people I talk to will have their eyes glaze over after any of those other phrases are mentioned.

It is hard enough to even begin to try to explain why the price is higher. Everybody complains about their ****** HVAC system, but so very few want to pay to fix it... and let's not mention drywall work, eh?
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,372
Location
Michigan
Zoning an existing system is a major crapshoot and turns out poorly more often then not. Normally you end up with a 4 ton unit trying to move only 2 tons of air through ductwork big enough for 1 ton.
Multi stage and modulating equipment can fix that but not many manufacturers make modulating equipment and zone controls that can work together to provide the needed airflow for each zone. Without it you end up using bypass dampers or dump zones to either recirculate air or send it somewhere it's not needed.

Zone systems with that have a zone that can only handle a small portion of the airflow tend to be a nightmare .


Is there room and access in the basement to run another truck line to feed the second floor if you were to zone it? How many runs and what size to the second floor?
What is the current system as far as size, age etc?
Would you consider replacing it if needed to zone the house properly?

Honestly what type of budget do you have in mind?
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,086
I have yet to see one of those installs that actually works.
mine seems to work fine. what're they doing wrong?
Zoning an existing system is a major crapshoot and turns out poorly more often then not. Normally you end up with a 4 ton unit trying to move only 2 tons of air through ductwork big enough for 1 ton.
Multi stage and modulating equipment can fix that but not many manufacturers make modulating equipment and zone controls that can work together to provide the needed airflow for each zone. Without it you end up using bypass dampers or dump zones to either recirculate air or send it somewhere it's not needed.

Zone systems with that have a zone that can only handle a small portion of the airflow tend to be a nightmare .
I have a unit picked out (mitsubishi 17" cased coil, 4 ton hyperheat ODU) for if/when my 20 year old AC takes a dump.
Dump zones (dumb) and bypass dampers (utterly pointless) are bandaids for poor engineering, and waste energy at best. if you can't put the cold (or hot) air where you need it, your system is wrong.

as of now, here's mine in the two "stages" on a very hot day. there's also a DATS tied to the panel for freeze protection, but i've never gotten that cold.
delta T test low.jpeg1752803672907.jpeg
stage one is on the low side of allowable airflow, stage 2 on the higher end of things for better throw. the smallest zone cannot call for stage 2, but any other zone can kick up the system.
 
OP
W

Wiz02

Well-known member
Joined
Jul 13, 2007
Messages
2,399
Location
Southeastern PA
Zoning an existing system is a major crapshoot and turns out poorly more often then not. Normally you end up with a 4 ton unit trying to move only 2 tons of air through ductwork big enough for 1 ton.
Multi stage and modulating equipment can fix that but not many manufacturers make modulating equipment and zone controls that can work together to provide the needed airflow for each zone. Without it you end up using bypass dampers or dump zones to either recirculate air or send it somewhere it's not needed.

Zone systems with that have a zone that can only handle a small portion of the airflow tend to be a nightmare .


Is there room and access in the basement to run another truck line to feed the second floor if you were to zone it? How many runs and what size to the second floor?
What is the current system as far as size, age etc?
Would you consider replacing it if needed to zone the house properly?

Honestly what type of budget do you have in mind?
Yes basement is unfinished and could handle another trunk line. I don't know how to get new ductwork to the second floor without major surgery. Only two 2 x 6 interior walls. Exterior walls are 2 x 4. Most of the second floor registers have flex ducts, but I have no idea of how the ductwork gets to the second floor.

Existing system is less than 5 years old. Heat pump single stage cooling, 2 stage heat with high efficiency propane furnace backup. I would hope that the existing system can be retained but I try to keep an open mind.

Budget SWAG right now before I talk to any contractors is $15K. But that assumes retaining existing equipment.

Thanks
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,086
Yes basement is unfinished and could handle another trunk line. I don't know how to get new ductwork to the second floor without major surgery. Only two 2 x 6 interior walls. Exterior walls are 2 x 4. Most of the second floor registers have flex ducts, but I have no idea of how the ductwork gets to the second floor.

Existing system is less than 5 years old. Heat pump single stage cooling, 2 stage heat with high efficiency propane furnace backup. I would hope that the existing system can be retained but I try to keep an open mind.

Budget SWAG right now before I talk to any contractors is $15K. But that assumes retaining existing equipment.

Thanks
What thermostat do you have currently?
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
12,036
Location
Fargo, ND
I have yet to see one of those installs that actually works.
If the installer knows what he is doing they will work. We installed many zone systems. One thing we did was up size all the duct work. Plus you need a bypass damper to relieve the air flow if only a smaller zone is calling for heat of cooling.The OP mentioned his duct work to the upstairs was questionable. I wouldn't recommend a zone system in this case. A zone system often doesn't work on an older system unless duct sizes are changed. Also, if you have one room that gets hot, OP mentioned a hot bathroom, it is a bad deal to try cool one small room when the rest of the house doesn't need it.
 

Junkman

Well-known member
Joined
Dec 18, 2006
Messages
6,752
Location
Northeastern CT
I had a similar problem, and I resolved it by installing an air handler in the attic with metal ductwork extending into the second-floor rooms. After the installation was complete, I had the underside of the attic roof sprayfoamed with a foot of insulating foam, and they also sprayfoamed all of the ductwork where it exited the air handler and extended to the ceiling of each room. That keeps the conditioned air going to where it needs to be with minimal temperature losses.
 

AA/FC

Well-known member
Joined
Dec 9, 2010
Messages
2,080
Sadly 4 inch in most cases
Yeah, that is undersized for A/C.

You mentioned the house was built 35 years ago.... I was in the HVAC business 35 years ago and I can tell you that contractors did know how to properly size air ducts back then. So, just because the house is 35 years old does not automatically mean the HVAC system was undersized by default. (or designed wrong)

Sounds like the contractor or installer cut corners for whatever reason. Sorry to hear that...
 
To avoid these ads, REGISTER NOW!

AA/FC

Well-known member
Joined
Dec 9, 2010
Messages
2,080
If your register supply ducts are 4" flex with no hard pipe, you're really not getting enough airflow for proper air conditioning. Even if it was 4" hard pipe all the way to the register it would be insufficient, but flex duct restricts the flow even worse. It's fine for short connections, but entire runs of flex duct is what lazy people (contractors/installers) do who are in a hurry to get in and out of a job.
 

AA/FC

Well-known member
Joined
Dec 9, 2010
Messages
2,080
Was your house originally designed for "heat only" and the central A/C was added sometime after the house was built?

I ask because 35 yeas ago most (all?) new houses were probably built with central A/C. (around here anyway) I'm sure it varies by geographical location. But I have seen older houses that were built in the 50s or 60s (for example) that were built with force air heat only. These older "heat only" houses were generally built with 4" supply ducts to the registers because back then 4" was considered sufficient enough for heat only. Then, when you later add central A/C, that old 4" potentially becomes a problem.

Again, I am sure what I just typed above greatly depends on geographical location.
 

danski0224

Well-known member
Joined
Jan 29, 2005
Messages
13,921
Location
Near Naperville, IL
You mentioned the house was built 35 years ago.... I was in the HVAC business 35 years ago and I can tell you that contractors did know how to properly size air ducts back then.
Air duct sizing was known way more than 35 years ago.

In my area, a load calculation, equipment selection or duct drawing was NOT part of the residential HVAC permit process until at least 2012.

Duct sealing was not part of a residential job until 2012.

Blower door testing and duct leakage... same thing.

2012 refers to the international energy code. All of it was not adopted in 2012.

Using building stud or joist cavities as return ductwork was allowed until the 2012 code, unless the local AHJ didn't allow it.

Until the 2012 code adoption, pretty much anything went in residential new construction HVAC. It only had to last a year... or whatever warranty that the builder specified.

And that's without the slam it in and leave early "hours booking" that was going on in my area.

**** it in and get it done, move on to the next one. Union or not.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,086
Yeah, that is undersized for A/C.

You mentioned the house was built 35 years ago.... I was in the HVAC business 35 years ago and I can tell you that contractors did know how to properly size air ducts back then. So, just because the house is 35 years old does not automatically mean the HVAC system was undersized by default. (or designed wrong)

Sounds like the contractor or installer cut corners for whatever reason. Sorry to hear that...
That depends on how many there are feeding each room.
 
OP
W

Wiz02

Well-known member
Joined
Jul 13, 2007
Messages
2,399
Location
Southeastern PA
@danski0224 , @u3b3rg33k , @AA/FC

House was built with a heatpump (AC) and electric backup heat because electric utility was trying to increase usage to justify the nuke that they built, according to my neighbor, and I never checked his story.

Builder went out of business according to my neighbors for not paying his subs according to the original owners. I bought the house when it was 5 years old.

The drywall guys did a horrible job, not that I can blame them if they weren't paid. The electrical in the house was competently installed and the plumbing is fine. The HVAC is where things got ugly.

Main ductwork in the basement has flex running from the main run a good 20+ ft to a vent in the foyer. The flex duct takeoff to feed the tiny powder room is located on the end of the main duct instead of the sides / top / bottom. It had more airflow into the powder room than any other vent in the house.

I don't have a good way of finding out how the ductwork gets upstairs and how the ducts are distributed to each room. I do know that when I tore out bedroom carpet, the 4×10 vent outlet elbow connected to 4 in flex.

Master bedroom has 2 vents. One cleverly placed under the bed which is due to how the house is built, but what were they thinking?

All other upstairs rooms have one vent.
 
Last edited:

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
3,039
Location
Peace Valley,mo
The only way to cool a two story from working in the industry and my personal house. Put a cooling only unit in the attic return in the hallway with a filter grill. Ceiling diffusers in the ceiling two in the master one in each of the bedrooms. Insulate trunk line with flex off of it 16" flex return for a 2 ton unit with safety pan under complete unit with condensate safety switch and thermostat in master. Refrigerant lines followed the flue to the basement and out as well as the wiring. Mini splits work ok but when having a few head units there is a lot of maintenance. Cleaning them once a year. Look at a you tube video on cleaning them. 1900 ' two story 3 bed house by having two units had a total of 5.5 tons which when your entertaining it could be 95° and could have 20+ people and the house was cool. Had ceiling fan at top of the stairs blowing down. At night set back the 1 floor.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,086
@danski0224 , @u3b3rg33k , @AA/FC

House was built with a heatpump (AC) and electric backup heat because electric utility was trying to increase usage to justify the nuke that they built, according to my neighbor, and I never checked his story.

Builder went out of business according to my neighbors for not paying his subs according to the original owners. I bought the house when it was 5 years old.

The drywall guys did a horrible job, not that I can blame them if they weren't paid. The electrical in the house was competently installed and the plumbing is fine. The HVAC is where things got ugly.

Main ductwork in the basement has flex running from the main run a good 20+ ft to a vent in the foyer. The flex duct takeoff to feed the tiny powder room is located on the end of the main duct instead of the sides / top / bottom. It had more airflow into the powder room than any other vent in the house.

I don't have a good way of finding out how the ductwork gets upstairs and how the ducts are distributed to each room. I do know that when I tore out bedroom carpet, the 4×10 vent outlet elbow connected to 4 in flex.

Master bedroom has 2 vents. One cleverly placed under the bed which is due to how the house is built, but what were they thinking?

All other upstairs rooms have one vent.
a single 4" flex duct isn't going to cool much.

a system of small ducts is different:

1752853738956.png1752853760119.png1752853783415.png

but it sounds like you have a single dryer vent trying to cool an entire room.
 

AA/FC

Well-known member
Joined
Dec 9, 2010
Messages
2,080
The builder decides the quality of the job based upon the bid that's accepted.
Not on every job. If I hire a contractor to build a house specially for me, I make all the decisions. When a developer builds houses that will be for sale to a customer once they have been competed, sure the builder makes decisions. We don't know the history of the OP's house. (at the time of my post, anyway)
 
Last edited:

AA/FC

Well-known member
Joined
Dec 9, 2010
Messages
2,080
Air duct sizing was known way more than 35 years ago.

In my area, a load calculation, equipment selection or duct drawing was NOT part of the residential HVAC permit process until at least 2012.

Duct sealing was not part of a residential job until 2012.

Blower door testing and duct leakage... same thing.

2012 refers to the international energy code. All of it was not adopted in 2012.

Using building stud or joist cavities as return ductwork was allowed until the 2012 code, unless the local AHJ didn't allow it.

Until the 2012 code adoption, pretty much anything went in residential new construction HVAC. It only had to last a year... or whatever warranty that the builder specified.

And that's without the slam it in and leave early "hours booking" that was going on in my area.

**** it in and get it done, move on to the next one. Union or not.
I never said duct sizing was invented 35 years ago.... I said contractors knew HOW to properly size ducts 35 years ago. I never specified when it was originally invented.

Like I said, I was in the HVAC business 35 years ago. Our family owned two large commercial HVAC companies. (one on my Mon's side, one on my Dad's side. Both companies competed with each other.) We did 99.8% large union commercial/industrial jobs.
 

AA/FC

Well-known member
Joined
Dec 9, 2010
Messages
2,080
@danski0224 , @u3b3rg33k , @AA/FC

The flex duct takeoff to feed the tiny powder room is located on the end of the main duct instead of the sides / top / bottom. It had more airflow into the powder room than any other vent in the house.
That is one of the first things I learned as a young Tinner apprentice. It's basically day #1 of HVAC Tinner 101..... "NEVER put a take-off on the end of a trunk line."

It's a good indicator of the quality of installers that worked on your house. Unfortunately.
 
OP
W

Wiz02

Well-known member
Joined
Jul 13, 2007
Messages
2,399
Location
Southeastern PA
That is one of the first things I learned as a young Tinner apprentice. It's basically day #1 of HVAC Tinner 101..... "NEVER put a take-off on the end of a trunk line."

It's a good indicator of the quality of installers that worked on your house. Unfortunately.

It's an interesting situation IMHO, as the flow of an opening on the end of a trunk line is noticeably higher than the same size opening on the sides of the trunk line.

Yet when I think of it as a physics problem where I have a pressurized box, intuitively I expect the flow to be the same no matter where the opening is made.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,086
It's an interesting situation IMHO, as the flow of an opening on the end of a trunk line is noticeably higher than the same size opening on the sides of the trunk line.

Yet when I think of it as a physics problem where I have a pressurized box, intuitively I expect the flow to be the same no matter where the opening is made.
it's velocity pressure.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,982
It's an interesting situation IMHO, as the flow of an opening on the end of a trunk line is noticeably higher than the same size opening on the sides of the trunk line.

Yet when I think of it as a physics problem where I have a pressurized box, intuitively I expect the flow to be the same no matter where the opening is made.

It's easier for the air to go straight out the end, rather than turn a corner. It's pushed out the blower and is moving at pretty high speed.
 
To avoid these ads, REGISTER NOW!