Can I use 3 individual pieces of 12 GA THHN left over from the wiring in my shop? The outlet will be tied into an existing switch literally right on the opposite side of an interior wall. The run will be less than 1 ft so I don't want to buy a whole roll of Romex just for this.

What say you guys?
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
With out being in conduit? No most retail outlets should sell by the foot.
 

homebuilt burner

Well-known member
Joined
Dec 8, 2014
Messages
1,763
Location
central Wisconsin
If you ask around maybe a neighbor has some romex laying around. If you want I can throw a foot in a box and mail you some. pm if wanted Or maybe someone on here is closer.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,066
Location
Minneapolis
The individual wires need to be protected by some sort of raceway. It may require a short piece of conduit, or the two boxes may be close enough that you can simply use a fitting or two to connect them.
 
OP
A

aka Larry

Well-known member
Joined
May 2, 2012
Messages
8,029
Location
Eastern, NC
The individual wires need to be protected by some sort of raceway. It may require a short piece of conduit, or the two boxes may be close enough that you can simply use a fitting or two to connect them.

Not trying to sound like smarta** here, because I appreciate the help, but protected from what? The wires will be inside a wall...behind the sheetrock.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
I'd tape them together and use it. Romex type sheathing doesn't protect squat IMHO. Especially the home center stuff, you can go through the sheath with your fingernail. It sure as hell won't stop a nail from a picture hanger.
 

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,939
Location
Central New Jersey
If by protected people mean the wires have to be inside some type of sheathing, similar to Romex, then you could always create a short 3 wire bundle from your individual wires and wrap it with some electrical tape or something like that, to create the sheathing around it.

Jim

Opps, Falcon67 beat me to it by a minute!
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
If someone is too stingy to buy a short piece of NM cable in order to do the job right, they really should not do it at all.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,066
Location
Minneapolis
Not trying to sound like smarta** here, because I appreciate the help, but protected from what? The wires will be inside a wall...behind the sheetrock.

The short answer is because Article 310 of the National Electric Code says so...
Assuming the wire you have on hand is the typical THHN/THWN type you buy at the local home center, the insulation is rated for electrical protection but it's not rated for physical protection, which means it needs to be installed inside an approved raceway - a conduit, a wire channel or something of that sort.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
The short answer is because Article 310 of the National Electric Code says so...
Assuming the wire you have on hand is the typical THHN/THWN type you buy at the local home center, the insulation is rated for electrical protection but it's not rated for physical protection, which means it needs to be installed inside an approved raceway - a conduit, a wire channel or something of that sort.

This ^^^ It boils down to being NEC compliant. If you don't care about code then do it how ever you please.
 

signcrafter

Well-known member
Joined
May 9, 2012
Messages
12,334
Can you, yes. Would it be up to code, no.

Almost any store sells 10' rolls of romex or most stores will sell by the foot also. Grab 2 feet and add your outlet.

Can even place a want add on craigslist for a short piece of romex.
 

Trey T

Well-known member
Joined
Aug 3, 2011
Messages
3,749
Location
Houston, TX
Here's my take on it: I believe it's safer to run the THNN inside a wall than Romex for a given situation (not for all situation) like in OP. Let's assume the wire is ran vertically between the 16in-OC 2x4 studs with 3ft of wire (THNN or Romex) and you happen to set the picture frame fastener at the wire. The more likely hood of piercing either wire will be the Romex because the Romex is more ridged than the THNN.

If you can identify the potential issue using THNN, please state your case scenario for the OP so he can understand. It's pointless to cut-and-paste NEC when any OP has a unique question, it makes questions like these pointless to any online forums.
 

OzarkMan

Well-known member
Joined
Dec 3, 2014
Messages
556
Location
Ozark Missouri
The main answer for the OP is this.
Do it as you wish as it sounds like you may or may not follow proper advice to use a section of NM to do it code compliant. Fine.
The day there's a fire somewhere in the vicinity caused by anything other than the electrical connection/wiring methods will be the day the the OP will be answering to the insurance company who may be negotiating on a claim.
 
To avoid these ads, REGISTER NOW!

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,066
Location
Minneapolis
If you can identify the potential issue using THNN, please state your case scenario for the OP so he can understand. It's pointless to cut-and-paste NEC when any OP has a unique question, it makes questions like these pointless to any online forums.

I think I was fairly clear in my post:

the insulation is rated for electrical protection but it's not rated for physical protection, which means it needs to be installed inside an approved raceway - a conduit, a wire channel or something of that sort.

Sure, it's not likely that physical damage would occur to individual wires running a few inches between two electrical boxes that are back to back with each other, but I can't advise people to do something that's not per Code.
 

Slowgsr

Well-known member
Joined
Nov 14, 2014
Messages
610
Location
Southern ontario
You need to follow class 1 wiring methods. Your over 100VA.

Do not run the free-air, don't hack it. Buy a piece of romex, they sell it by the foot.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
The short answer is because Article 310 of the National Electric Code says so...
Assuming the wire you have on hand is the typical THHN/THWN type you buy at the local home center, the insulation is rated for electrical protection but it's not rated for physical protection, which means it needs to be installed inside an approved raceway - a conduit, a wire channel or something of that sort.

Bingo!

Tommy
 

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,213
Location
The UP, God's country
Are you really so poor that you can't go to Ace Hardware and buy 3 feet of romex?

My grocery store sells the stuff by the foot, for less than the price of a dozen eggs!

I bet it would cost less than your morning latte.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
I cant believe how cheap some people are!

:lol_hitti

If youre gonna do something the wrong way but first come on here to ask about how to do it, why are u surprised when several people including electricians tell u that your idea is the wrong way to do it? Why even bother asking for advise if u dont want to hear that your way is the wrong way? :headshake: :dunno:
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
I cant believe how cheap some people are!

:lol_hitti

If youre gonna do something the wrong way but first come on here to ask about how to do it, why are u surprised when several people including electricians tell u that your idea is the wrong way to do it? Why even bother asking for advise if u dont want to hear that your way is the wrong way? :headshake: :dunno:
Exactly!:beer::beer::beer::beer::beer:
 
OP
A

aka Larry

Well-known member
Joined
May 2, 2012
Messages
8,029
Location
Eastern, NC
Thanks for the replies guys. I didn't realize Romex was sold by the foot. I'll go to Lowes and get a short piece for the job.
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
Buy a 25' roll........then you will have it for the next project. Consider it an investment like money in the bank. Do not forget to buy the proper box fittings, staples, wire nuts that's all part of that pesky code compliance.
 
Last edited:

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,933
Location
Coronado, CA
I cant believe how cheap some people are!

Some folks, and I have been one myself, have just enough knowledge to be considered dangerous.

Someday they will have accumulated enough scars and experience to be able to say "Oh Hell, that will work" and then just hide their jury rig and move on to the next fiasco.
 

Trey T

Well-known member
Joined
Aug 3, 2011
Messages
3,749
Location
Houston, TX
I cant believe how cheap some people are!

:lol_hitti

If youre gonna do something the wrong way but first come on here to ask about how to do it, why are u surprised when several people including electricians tell u that your idea is the wrong way to do it? Why even bother asking for advise if u dont want to hear that your way is the wrong way? :headshake: :dunno:
It's not about cheap or not, right or wrong, it's about informing people. What I've learned over the years is that, it doesn't matter what we tell the OP, he/she will make his/her own decision regardless. The OP obviously know that using THNN is not the norm, but he just want some explanation why not. Pointing a code, for most people that are curious like the OP, doesn't help because a code requires interpretation; it's a reason why it's called a "code" not a "standard operating procedure".

That's the reason why I call a lot of you NEC-huggers; you're not understanding why people come on to forums to ask random questions when they already have a solution.

For this particular case, you can either tell the OP why it's not safe or not feasible, and let him decide. So far, the OP might decide that it's more feasible to go buy the foot Romex.
 
Last edited:
OP
A

aka Larry

Well-known member
Joined
May 2, 2012
Messages
8,029
Location
Eastern, NC
The OP obviously know that using THNN is not the norm, but he just want some explanation why not. Pointing a code, for most people that are curious like the OP, doesn't help because a code requires interpretation; it's a reason why it's called a "code" not a "standard operating procedure".

Well said. I knew what I wanted to do wasn't "per code", but I wanted to know an actual reason other than "because NEC said so". FWIW, unless I missed it, I didn't get an actual reason (for this situation) but I was probably foolish to think I might get one in the first place. Also, I'm not "too cheap" as I've spent $600 on this project already so I can afford a roll of Romex, but thought it would be wasteful to do so.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
Buy a 25' roll........then you will have it for the next project. Consider it an investment like money in the bank. Do not forget to buy the proper box fittings, staples, wire nuts that's all part of that pesky code compliance.

plastic boxes dont need fittings and NM-b fished in closed walls doesnt require staples.

....That's the reason why I call a lot of you NEC-huggers; you're not understanding why people come on to forums to ask random questions when they already have a solution.....

Nec huggers? :eek: :headscrat While some on here may be "nec huggers", I on the other hand have to abide by it at work.
 
Last edited:

Trey T

Well-known member
Joined
Aug 3, 2011
Messages
3,749
Location
Houston, TX
plastic boxes dont need fittings and NM-b fished in closed walls doesnt require staples.



Nec huggers? :eek: :headscrat While some on here may be "nec huggers", I on the other hand have to abide by it at work.
I don't think you followed what I said. to be blunt, general public doesn't care about codes, they want to do things based on what's feasible, whether it's the cheapest route or the most expensive route.

i.e. a buddy of mine purchased a 1950 home in a reviving neighborhood in Houston, where real estate prices have soared in the last 2-3yrs, (land value worth about 85% and improvement only 15%) and renovated about half of his home which includes electrical panel. When he was asked about upgrading all of his lines to 3-prong (currently no ground), he simply didn't think it was feasible (he's a electrical engineer in power distribution). Again, it's not about doing things by the code, it's what they feel comfortable with based on their knowledge or lack of knowledge.

I think a lot of you forget which country we live in, everybody got their own mind. Are their behavior dumb? No, they're just irrational. It doesn't help when someone throw NEC code at an irrational person, because codes, a language that requires interpretation, doesn't mean anything to them.
 