adding outlets in basement shop

dusterbd13

Well-known member
Joined
Mar 19, 2014
Messages
74
Location
Albemarle nc
my 17x24 basement shop has 4 outlets. that's it. obviously not enough.

the basement is constructed of block, filled with concrete and rebar.

it has a gcfi installed, and all the wires are currently run through pvc conduit. I have no idea if its up to code or not, but it has served me well for the last 10 years of living here.

I just want to add more outlets.

in my researching, I seem to just be confusing myself more and more. apparently I need to run thhn, in the proper gauge for my 20 amp circuit breakers, (which I think is 12 gauge?) but can also use romex in the same gauge as the pvc is only used to protect. (may be wrong, I've read WAY too much on this)

is it really this simple? just run the conduit, feed the wire through, connect, and run with it? im hoping to have a box every three feet or so, so excessive run lengths wont be an issue. also, just two plug in points in each box.

I've done tons of automotive electrical work, and replaced stuff in the house (fans, light switches, etc) but never done this kind of thing. cant afford an electrician, so its going to be me doing it and learning as I go. I figure if I can wire a fuel injection setup from c]scratch, I should be able to add an outlet or 20.
 
To avoid these ads, REGISTER NOW!

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
If your going to have them 3 feet apart then I would use separate thhn and not romex,takes up less space in pipe in case you want to add more wires later. I would run a 3/4 inch pipe if using pvc and 1/2 if using emt,that's just my preference. Emt you can get away without running a ground wire but need it with pvc. You are correct that you need 12 gauge for 20 amps
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
If u use MWBCs(multiwire branch circuits) u can save a little on wire. 2 hots sharing a neutral and a ground.

Make sure to use a handle tied breaker.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Put a couple power strips on where you need them.

Have taken apart some of power strips made today? Pure ****, there are some decent ones made if you want to spend some dough, rather use Plugmold® then power strips, myself.
 