I am closing on a house in August the first thing I plan on doing is building a deck just a simple 15 foot wide by 30 foot long deck with a pergola over head. I checked the local code and the frost line here in the northland is deep so they require you to go at least 5 feet deep for the footings. I am no carpenter I have no professional skills other than copying what I see on youtube. Has anyone else here built one or have any advise or tips and tricks that you learned while you built your deck? Thanks for your help
 
To avoid these ads, REGISTER NOW!

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,949
Location
New England
That size don't think it will be simple. Pergola requires adds forethought. How high off the ground?


Sent from my iPhone using Tapatalk
 

MushCreek

Well-known member
Joined
Jan 14, 2015
Messages
10,021
Location
Upstate South Carolina
If any part of the deck will be more than 30" off of the ground, it becomes a real game-changer. The rules on elevated decks have become pretty tough due to catastrophic failures over the years. Find out what code your area follows, then look it up.
 

cdestuck

Well-known member
Joined
Nov 13, 2013
Messages
1,464
Location
Altoona, Pa
Plenty of good books that have great info of deck building. Lowes has a nice selection. Worth the 15-20 bucks for a learning and idea guide
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,645
Location
SE MI
The biggest mistake most people make is bolting the beams to the SIDE of the posts. They should be notched into or placed ON TOP of the posts.
 

ford33

Well-known member
Joined
Feb 26, 2011
Messages
2,118
Location
Chicago, IL. USA
That's a large deck for a first timer with no previous experience. I suggest you consider a carpenter to build the basic deck and you do the finish work like the railing, lattice and trim.

Also make sure the deck is securely attached to the building and that flashing is used so water is directed away from this attachment point.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
That's no simple deck -- especially for a first timer. There are so many variables -- proceed with caution.

Also, measure it out .... make sure you don't want/ need more than 15' depending on the doors and steps .. a foot can make a huge difference.
 

LB-1911

ALLIANCE MEMBER
Joined
Sep 24, 2011
Messages
5,759
Location
Northwestern Il.
I am closing on a house in August the first thing I plan on doing is building a deck just a simple 15 foot wide by 30 foot long deck with a pergola over head. I checked the local code and the frost line here in the northland is deep so they require you to go at least 5 feet deep for the footings. I am no carpenter I have no professional skills other than copying what I see on youtube. Has anyone else here built one or have any advise or tips and tricks that you learned while you built your deck? Thanks for your help

Take the previously supplied information to heart - There are several questions you'll need to get answered.

Congratulations on the purchase of your home and good luck w/ your project.
:beer:
 

Denwood

Well-known member
Joined
Sep 22, 2014
Messages
4,315
Location
Thunder Bay, Ontario, Canada
If the deck is not attached to the house, you don't need footings...you can float it on pads. Keeping it under 2" makes this game simpler too. I did a similar project two yrs back. After two yrs with temps dipping to -35C in winter, this floating deck hasn't moved at all.

Detailed here from demolition onward:

http://www.garagejournal.com/forum/showthread.php?t=263351&page=26

2016door4.jpg


..after the new deck, HardieBoard siding, and brick painting:

2016door5.jpg
 
Last edited:

KenC

Well-known member
Joined
Dec 20, 2009
Messages
2,607
Location
oklahoma
first answer the how high question. That's critical as it governs a lot of things, even railing type.

IMO, if you can build without attaching to the house structure it will make it much easier. Attachment requires penetration which creates water entry/diversion probability. Depending on local code you may not need to go below the frost line if not attached. However, the pergola part may dictate that you do in order to wind-proof the structure.
 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
14,481
Location
West central Indiana
I would do anything to avoid a deck. Wild animals crawl under them to live (and die, worst are skunks), they are constant maintence (unless you use high dollar composites or brasiallian epe) and they are rarely attached and flashed right to the house doing serious water damage over time to the rim joist. Also be very considerate of deck loadings. Many have died or been injured when a party full of people overload the deck and collapse.

If you can I would suggest a concrete patio or pavers, or pavers over concrete.
 

Ryanbabz71

Well-known member
Joined
Jan 24, 2016
Messages
492
Plan it out. Come up drawings to map out post locations and determine materials required


Ryan B.
 

ducksface

Banned
Joined
Oct 25, 2012
Messages
2,477
1.Biscuits, not deck screws. Deck screws **** and nothing cheapens your work like those exposed screws.
2.Hire a pro.

When the inspector makes you tear it out the second time, you'll have wished you paid the labor.
Inspector:did you put the footings on a hay bed?
You:that sounds silly
Inspector:tear them out

I had never heard of such silliness until recently when I saw a set of plans with a
Add straw
Cloud.
 
Last edited:

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
We need a deck on the back and I've already decided that when I do it, the frame will be steel and not wood. The height in part of it will be ground level so it's not anything up in the air. No frost line here, but it'll be way easier IMHO to build and level a steel frame that sits on a few concrete piers. I can them put any sort of deck material on it that can be removed and replaced without damage to the framework. The posts supporting the roof can be clad with cedar or some such to look like posts. If I had to go 5' down for footers I'd for sure consider steel over anything else.
 

Jeff95TA

Well-known member
Joined
Aug 11, 2008
Messages
887
Location
Pittsburgh, PA
This is a good guide and will help you with determining proper sizing and layout:
http://www.awc.org/pdf/codes-standards/publications/dca/AWC-DCA62012-DeckGuide-1405.pdf

It will give you a lot of info on how to attach a beam to posts, joist & beam spans, hangers, etc.

Check with your municipality on rules, permits, inspections, etc. It varies a lot. Following the International Residential Code (IRC) is a good start. I recently did a 40x30 ipe deck around my pool, and submitted a binder of drawings and ledger/beam/joist/post/soil calculations to the inspector ahead of time. They stamped the drawings, and there were no problems during construction. Overplanning is your friend!

After you read through the document, I'd be glad to try to answer any questions.
 

Attachments

  • 20161115.jpg
    20161115.jpg
    119.8 KB · Views: 70
  • 20161106.jpg
    20161106.jpg
    110.9 KB · Views: 75
Last edited:

Todd.Brock

Well-known member
Joined
Jul 15, 2008
Messages
4,250
Location
Cincinnati
Not sure of your skill level in reality, so it would help to have a guiding voice on site to walk you the logistics of the deck frame, connecting to a rim joist, etc.

Get a permit. Read the span tables to know what you can and can not do.

Assuming you have some carpentry skills , experience on some smaller projects, or just really hell bent on doing this yourself, keep asking questions and read the materials you get with the permit for what is required. That will guide you on what to do, not necessarily how to do it. May not be able to pick that up from You tube.

My serious recommendation is to be honest with your skills, tools, etc. it ain't totally rocket science, but you do need to have some clue.

Good luck and keep asking questions
And you will have a hell of time getting a 5ft deep hole!
 

jd_1138

Well-known member
Joined
May 8, 2013
Messages
17,155
Location
NE Ohio
1.Biscuits, not deck screws. Deck screws **** and nothing cheapens your work like those exposed screws.
2.Hire a pro.

Camo and Kreg both make jigs so you can install fasteners at an angle into the beams for a nice concealed sturdy installation.


Maybe hire a carpenter to act as the lead, and you can be the assistant and you will learn a lot. Hopefully you can get a discount on his or her labor rate, since you're helping.
 
Last edited:
To avoid these ads, REGISTER NOW!

TractorJeff

Well-known member
Joined
Dec 8, 2013
Messages
3,309
Location
Elkhorn, WI
Post hole drill the piers for footings (rent a skid steer with a post hole drill).
I built a 16x32 foot Deck 12 feet off the ground with a roof 10 feet off the deck with 6x6 and 4x12 framing timbers. Took 2 years working on weekends and nights. Well planned drawings approved by your Local Inspector will take the headaches! Work with the Inspector if you question anything in the least as the Internet will give you their local opinion, not the whim of your local Inspector!
 

73RR

Blank Email
Joined
Dec 13, 2016
Messages
300
Location
Central Ory-Gun
A lot of good information but we still haven't heard from the OP as to the height of the deck. Everything hinges on that one detail.
The mention of using steel as the main framing members would certainly offer greater long term stability-longevity in an elevated design but, again, here the assembly is dependent on the OP's skill set.
Items not mentioned are budget and timeline. OP?
....so many questions......
 

Denwood

Well-known member
Joined
Sep 22, 2014
Messages
4,315
Location
Thunder Bay, Ontario, Canada
further to my previous post...I won't use wood on horizontal surfaces outside again. These pics also detail flashing the pressure treated supports, which will extend their life much, much longer as rot almost always starts topside where moisture sits. The clips and composite decking are self explanatory. My wife and girls do yoga / work out etc. all the time on this surface which as no fasteners exposed, and zero splinter risk :)

mantis1.jpg


mantis2.jpg


mantis3.jpg


mantis4.jpg


mantis5.jpg


mantis6.jpg
 

toolmiser

Well-known member
Joined
Sep 1, 2009
Messages
1,665
Location
La Crosse, WI
Why the hurry for building a deck, with any luck you will be in the house for many years. Usually there are tons of little things to do to a house that will be new to you. Also if you wait a while you might come up with a better design, or meet a neighbor who is a retired carpenter.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,645
Location
SE MI
I would do anything to avoid a deck. Wild animals crawl under them to live (and die, worst are skunks), ...
Not if the deck (or floor of a shed) is high enough to provide light and ventilation. A couple inches of ground and you are asking for residents ! (My son had a dead possum under his !)

If you can I would suggest a concrete patio or pavers, or pavers over concrete.

More money for sure but it will be there FOREVER ! You can DIY a raised paver patio without concrete ! You need the proper garden wall block for the height and lots and lots of fill, preferably sand or sharp gravel. It must be compacted every 3-6". The final lift (layer) should be stone dust/"slag"/decomposed granite. Make sure there is a small amount of pitch AWAY from the house.
 

Todd.Brock

Well-known member
Joined
Jul 15, 2008
Messages
4,250
Location
Cincinnati
A lot of good information but we still haven't heard from the OP as to the height of the deck. Everything hinges on that one detail.

The mention of using steel as the main framing members would certainly offer greater long term stability-longevity in an elevated design but, again, here the assembly is dependent on the OP's skill set.

Items not mentioned are budget and timeline. OP?

....so many questions......



I don't really think the principles change if you are talking 2'6 vs 4 ft. 30" is the magic number for hand rails, and then trying to explain stair stringer math/framing square stops.

The AHJ should dictate it cross bracing or corner bracing is required over s certain height, but thats doesn't change the core principles of building with a footer, beam, ledger, joistss, etc.
 

Tejay

Well-known member
Joined
Dec 29, 2014
Messages
105
42" is for guardrails on a raised deck ( 6'+) below 6' the guard height is 36"
30 -36 is height for handrails on stairs but these heights vary slightly with your area/jurisdiction correct terminology will help with what you are discussing
 

Todd.Brock

Well-known member
Joined
Jul 15, 2008
Messages
4,250
Location
Cincinnati
In our area a handrail is not required if deck surface is less than 30" from the ground, height to grade, I think my inspector called it. That's what I was referring to.
 

Tejay

Well-known member
Joined
Dec 29, 2014
Messages
105
Yes for low level decks - my area is 24" above grade for no guardrails so as you can see research in you specific jurisdiction is necessary
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
We need a deck on the back and I've already decided that when I do it, the frame will be steel and not wood. The height in part of it will be ground level so it's not anything up in the air. No frost line here, but it'll be way easier IMHO to build and level a steel frame that sits on a few concrete piers. I can them put any sort of deck material on it that can be removed and replaced without damage to the framework. The posts supporting the roof can be clad with cedar or some such to look like posts. If I had to go 5' down for footers I'd for sure consider steel over anything else.

Fine Homebuilding just had a recent article on Steel Deck Framing... Seemed interesting


Did like the idea of a deck that is NOT attached to the structure to avoid a frost proof footing. Choose your wood (or composite) decking with care. Understand the maintenance requirements and real world life expectancy based on where you live.
 

kbs2244

Well-known member
Joined
Nov 11, 2006
Messages
14,065
As has been said, that is a big project.
Too big for a first timer.

Check out the books and ads for design ideas and call a pro.

The OT hours spent to pay them will be well spent.

One of the most important things a DIY guy can learn is when not to DIY.
 

SH7mi

Well-known member
Joined
Feb 3, 2014
Messages
186
Location
SE Pennsylvania
Do not drop your support posts (wood) into the dirt. Bring your concrete footers above the ground level and set your posts on top. Wood, no matter the species, will rot in dirt or concrete.
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California

Personally I don't like clips or biscuits or whatever that sit between the boards, EXACTLY where you want clean, open air. And not debris and moisture.

I've used deck master rails. More work, to be sure. Apply the rails then all decking screwed from below. But for me, labor is cheap. ;)


Once decking is installed, the space between deck boards is open, can be power washed, blown out, cleaned with a scraper, etc. Not an issue here, but water then ice cannot get into that joint either.

I **DO** like the idea of a moisture barrier on the top of the joists, as you described. Even with PY lumber.


Here are some desk master brackets installed- lay boards on top, screw up. Two screws per board, easy to reposition if needed. I had a 12" pony clamp to hold them when son was in school (his job was to 'stand here') ;)


51hnlZjGHQL.jpg
 

Stowe Boy

Member
Joined
Jun 23, 2016
Messages
12
Location
Greater St. Louis area
If the deck is not attached to the house, you don't need footings...you can float it on pads. Keeping it under 2" makes this game simpler too. I did a similar project two yrs back. After two yrs with temps dipping to -35C in winter, this floating deck hasn't moved at all.

Detailed here from demolition onward:

http://www.garagejournal.com/forum/showthread.php?t=263351&page=26

2016door4.jpg


..after the new deck, HardieBoard siding, and brick painting:

2016door5.jpg



Love those steps/stairs.

Interested in seeing/learning more about them. Are they basically platforms, as opposed to stringers?




Sent from my iPhone using Tapatalk
 

Stowe Boy

Member
Joined
Jun 23, 2016
Messages
12
Location
Greater St. Louis area
1.Biscuits, not deck screws. Deck screws **** and nothing cheapens your work like those exposed screws.
2.Hire a pro.

When the inspector makes you tear it out the second time, you'll have wished you paid the labor.
Inspector:did you put the footings on a hay bed?
You:that sounds silly
Inspector:tear them out

I had never heard of such silliness until recently when I saw a set of plans with a
Add straw
Cloud.



Straw? Now you have my interest. Cannot tell where you live from your profile.


Sent from my iPhone using Tapatalk
 

Denwood

Well-known member
Joined
Sep 22, 2014
Messages
4,315
Location
Thunder Bay, Ontario, Canada
Personally I don't like clips or biscuits or whatever that sit between the boards, EXACTLY where you want clean, open air. And not debris and moisture.

I've used deck master rails. More work, to be sure. Apply the rails then all decking screwed from below. But for me, labor is cheap. ;)


Once decking is installed, the space between deck boards is open, can be power washed, blown out, cleaned with a scraper, etc. Not an issue here, but water then ice cannot get into that joint either.

I **DO** like the idea of a moisture barrier on the top of the joists, as you described. Even with PY lumber.

mantis4.jpg


Ard, the Moistureshield composite I used is rated for water submersion..so no worries there. The Mantis clips maintain controlled spacing between the boards (about 1/8") and also elevate the boards off the joists, so maintaining an air gap under. They are not inexpensive..but they are the best solution I've used yet :)
 

Denwood

Well-known member
Joined
Sep 22, 2014
Messages
4,315
Location
Thunder Bay, Ontario, Canada
Stowe boy, these are pulled from my thread around page 30 or so. I cantilevered the main support beams out a bit which more or less support the two stair/platforms. The deck has worked out pretty awesome. We've got winters here with temps down to -35C, and a forested yard that dumps a lot of organic material on the deck. Other than sweeping, there's been no maintenance to do. More or less my first composite deck..so no claims of expertise in that department.

deckprog1.jpg


deckframe1.jpg


deck_12_1.jpg


deck_12_2.jpg


seating2.jpg


deck_15_2.jpg


deckled_night.jpg


augdeck9.jpg
 
Last edited:
To avoid these ads, REGISTER NOW!
Top Bottom