AFCI breakers and the 2017 NEC

mrpizza

Well-known member
Joined
Nov 1, 2011
Messages
2,935
Location
IL
Got power completed to the meter today, so I will be running my electric service this weekend into my building. Looking at the new codes, it looks like I have to use AFCI breakers almost everywhere for 15 and 20 A except the kitchen and bath and other wet locations, where I will use GFCI outlets. These dang things are 35 bucks each!!!!Is there anywhere I wont need them, like the garage?
 
To avoid these ads, REGISTER NOW!

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
You do need AFCI for the kitchen. The only places you don't need them are bathrooms, garage, outside outlets and lights, and I believe unfinished basements and attics.
 

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,172
Location
AZ
I am by no means a resi guy but I can tell you that you need to find out what code year your municipality has adopted. If they have gone to the latest and greatest, well there you have it. But most are normally at least one or two revisions behind. It's worth asking your building department.
 

sherrod624

Well-known member
Joined
Apr 28, 2013
Messages
110
Location
Sims, NC
Take some advice I received from other gj professionals. Call your inspector. regardless of what code your following, since its for yourself he may let some things slide. I called my inspector and he said he would only be looking for afci breakers on receptacles that weren't gfci protected. He would not be looking for them on lighting circuits. Saved me $2-300 dollars.

That being said I have been amazed that since I had my power turned on, during my construction I've ran every power tool that goes along with trim out off of my afci circuits and haven't popped one yet. 30yr old belt sander that you can see the brushes arcing, shop vac, table saw, miter saw, sds hammer drills. So my opinion is that although pricey so far they've not been too cumbersome
 

rattle_snake

Well-known member
Joined
Jun 25, 2015
Messages
5,220
Location
Chandler, AZ
Step 1 is to see which revision is applicable to you, I bet it is not 2017, and you do not need them.

But, the company I work for supplies the microcontroller that detects the arc, so if you buy a bunch of them my stock should go up.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,054
Location
Modesto, CA
Take some advice I received from other gj professionals. Call your inspector. regardless of what code your following, since its for yourself he may let some things slide. I called my inspector and he said he would only be looking for afci breakers on receptacles that weren't gfci protected. He would not be looking for them on lighting circuits. Saved me $2-300 dollars.

That being said I have been amazed that since I had my power turned on, during my construction I've ran every power tool that goes along with trim out off of my afci circuits and haven't popped one yet. 30yr old belt sander that you can see the brushes arcing, shop vac, table saw, miter saw, sds hammer drills. So my opinion is that although pricey so far they've not been too cumbersome

:+1:

The OPs state, Illinois, doesnt have a statewide adoption of the NEC.

So OP needs ro check with his AHJ before planning or spending any money on things he may not need.

http://www.mikeholt.com/necadoptionlist.php
 
OP
M

mrpizza

Well-known member
Joined
Nov 1, 2011
Messages
2,935
Location
IL
I havent checked with the code department since I don't need any building permits or inspections for anything. Only permit was for the septic. I will call the county and the nearest town and see what they say and proceed accordingly.



I just checked the city website for the town I live in (but I am out of city limits so subject to the county) and it is NEC 2008.
 
Last edited:

klassenl

Well-known member
Joined
Feb 20, 2016
Messages
715
Location
Southern Alberta
Step 1 is to see which revision is applicable to you, I bet it is not 2017, and you do not need them.

But, the company I work for supplies the microcontroller that detects the arc, so if you buy a bunch of them my stock should go up.

Can you elaborate on this controller. I am in the trade and I like to learn about these things as much as possible.
 

Orionrising

Well-known member
Joined
Nov 16, 2012
Messages
960
Location
Western Maine
And can you tell us if there really is a technical reason they can't make say 60 amp 2 pole ones so you could just run a sub.. or even afci main breakers?...

Sent from my Moto G (4) using Tapatalk
 

grantw

Well-known member
Joined
Nov 10, 2016
Messages
249
Location
Bay Area, CA
And can you tell us if there really is a technical reason they can't make say 60 amp 2 pole ones so you could just run a sub.. or even afci main breakers?...

Sent from my Moto G (4) using Tapatalk


I'm having a kitchen sub installed and fear for the hell I am about to endure. under the 2014NEC California has adopted. I am not looking forward to nuisance tripping when I try to run any appliance. In the long run, I'd much rather have a branch AFCI/GFCI trip on me than the whole 100A kitchen sub.

I like the idea of a AFCI protected panel, in theory. But, AFCIs have a LONG way to go before they are no longer a nuisance.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
11,000
Location
Rhode Island
Take some advice I received from other gj professionals. Call your inspector. regardless of what code your following, since its for yourself he may let some things slide. I called my inspector and he said he would only be looking for afci breakers on receptacles that weren't gfci protected. He would not be looking for them on lighting circuits. Saved me $2-300 dollars.

That being said I have been amazed that since I had my power turned on, during my construction I've ran every power tool that goes along with trim out off of my afci circuits and haven't popped one yet. 30yr old belt sander that you can see the brushes arcing, shop vac, table saw, miter saw, sds hammer drills. So my opinion is that although pricey so far they've not been too cumbersome
That's actually a concern now. There are people who have tried to get the latest AFCI breakers trip, and they can't.
 

manwithtools

ALLIANCE MEMBER
Joined
Aug 24, 2015
Messages
14,006
Location
Lebanon, TN
Step 1 is to see which revision is applicable to you, I bet it is not 2017, and you do not need them.

But, the company I work for supplies the microcontroller that detects the arc, so if you buy a bunch of them my stock should go up.

Can you elaborate on this controller. I am in the trade and I like to learn about these things as much as possible.

Maybe he could just give you the name of their lobbyists? This is the most recent form of snake oil we have experienced. I'm all for making a buck via innovation, but these AFCI requirements are BS.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
11,000
Location
Rhode Island
Then how do you know they actually work?? Because it says so on the box??
I've seen more than one person simulating series and parallel arcs and newer AFCIs happily ignored them. It seems they fixed the "nuisance tripping", by making AFCIs insensitive to everything but the "test arc" used during design.
 

prostreetamx

Well-known member
Joined
Dec 19, 2016
Messages
222
Location
Las Vegas
Take some advice I received from other gj professionals. Call your inspector. regardless of what code your following, since its for yourself he may let some things slide. I called my inspector and he said he would only be looking for afci breakers on receptacles that weren't gfci protected. He would not be looking for them on lighting circuits. Saved me $2-300 dollars. QUOTE]
In Nevada we had to AFCI any light fixture in bedrooms with removable bulbs which was pretty much all fixtures back then.
 
OP
M

mrpizza

Well-known member
Joined
Nov 1, 2011
Messages
2,935
Location
IL
I will call the inspector, but he will never be at my property as there are no permits to pull and no inspections.
 

rattle_snake

Well-known member
Joined
Jun 25, 2015
Messages
5,220
Location
Chandler, AZ
I've seen more than one person simulating series and parallel arcs and newer AFCIs happily ignored them. It seems they fixed the "nuisance tripping", by making AFCIs insensitive to everything but the "test arc" used during design.

There is a microcontroller in the breaker that has several analog to digital converter channels to monitor both voltage and current at all times. There is an algorithm running that is looking for a certain set of V/I profiles, likely stored in lookup tables. When it detects a sequence of events that matches the fault conditions, it trips. I bet they continue to improve in many ways.

Same products are in smoke detectors and fire fighter safety gear so bases are covered. :)
 
Last edited:

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
All I can tell you is that they work. I had the very same arc fault these are designed for, but I didn't have them at the time. Lots of buzzing during a rain that got into a box. And then total failure. Why no fire, I'll never know. My whole house (AFA living space branch circuits are on AFCI breakers with GFCI's where indicated
.
I had an old ceiling fan go wonky and that was the only 'nuisance' tripping I've had. Replaced the old fan and not a trip since. It was the infinite controller in the fan housing. NLA for Casablanca fans and for good reason. They last 10 years and that's it. $800 fan.
 

OH_Varmntr

Well-known member
Joined
Apr 2, 2017
Messages
320
Location
Ohio
The combination GFCI/AFCI units are cheaper now than dedicated GFCI units. That's why I bought mine. It trips 4 out of 5 times I use it for my new 13-amp Delta table saw.
 
To avoid these ads, REGISTER NOW!

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
When talking about CAFI breakers tripping, it's helpful to say if the breaker tripped for AF or for GF. The ones I have (Homeline) can be tested for 30 days after a trip and they will indicate the nature of the last fault.

The 15A and 20A 120V breakers are about $40 each.
 

toplessHO

Well-known member
Joined
Oct 20, 2014
Messages
14,070
Location
central florida
Heres why its mandated to use arc flash
changed this one out that was behind a mattress
Relative said "well I had heard it sizzling for a while"
gezz could have burned the house down.
Had aluminum wire feeding it,but that wasnt the problem,it was the cheap outlet
and being under a strain pulled sideways,thereby losing the male plug/female outlet contact
 

Attachments

  • 20170805_080602[1].jpg
    20170805_080602[1].jpg
    140.3 KB · Views: 41
  • 20170805_080653[1].jpg
    20170805_080653[1].jpg
    140.9 KB · Views: 40

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
Heres why its mandated to use arc flash.

FYI "arc flash" is different - basically a metallic explosion resulting from a high-voltage arc - while "arc fault" is the idea of detecting poor connections by looking for their arc signature.

To expand a bit on the terminology for general interest there is parallel arcing (essentially short-circuit arcing) and series arcing (open-circuit arcing). Detecting both is called Combined Arc Fault Circuit Interrupt (CAFCI) and when combined with GFCI they are called Dual Function, at least in Schneider's terminology.

AFCI = parallel arc detection
CAFCI = parallel and series detection
DF = CAFCI + GFCI

So, I should have said Dual Function in my previous post, rather than CAFI. DF breakers are as inexpensive as any of them, so I don't really see a reason to buy anything else unless you specifically don't want GFCI.

Schneider has some decent FAQ pages about this stuff if you Google it.
 

toplessHO

Well-known member
Joined
Oct 20, 2014
Messages
14,070
Location
central florida
whoops yea had arc flash on my mind as its time to reup my card on it.
and to correct you arc flash doesnt have to be "high voltage" but it is high amperage
vaporization of metal.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
11,000
Location
Rhode Island
Heres why its mandated to use arc flash
changed this one out that was behind a mattress
Relative said "well I had heard it sizzling for a while"
gezz could have burned the house down.
Had aluminum wire feeding it,but that wasnt the problem,it was the cheap outlet
and being under a strain pulled sideways,thereby losing the male plug/female outlet contact
I totally get why they're mandated, but the problem is that they still don't work reliably.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,054
Location
Modesto, CA
Heres why its mandated to use arc flash
changed this one out that was behind a mattress
Relative said "well I had heard it sizzling for a while"
gezz could have burned the house down.
Had aluminum wire feeding it,but that wasnt the problem,it was the cheap outlet
and being under a strain pulled sideways,thereby losing the male plug/female outlet contact

Is that a CO/ALR rated outlet?


How do you know?
 

DC73

Well-known member
Joined
Dec 27, 2014
Messages
1,627
Location
Lubbock TX
I will call the inspector, but he will never be at my property as there are no permits to pull and no inspections.

In that case, I wouldn't waste one minute or one cent on AFCIs. Just put GFCIs where they are needed for safety and forget you know anything about AFCIs.

DC
 
OP
M

mrpizza

Well-known member
Joined
Nov 1, 2011
Messages
2,935
Location
IL
On another note, i need to run 120v line to a tower 700' away to power some internet equipment. It uses less than 1 amp. What wire would I use?
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
How do you know?

Come on, man. I told you that the complicated ceiling fan went south and tripped the AFCI. More than once. When I isolated the problem and fixed the fan with a kit, no more tripping.

In addition to that, we had record breaking storms in January as you did. I had water coming down the wall by my chimney and into a wall box that has a sconce on it. I have these lights on a dimmer and when I cranked up the voltage the breaker tripped. When all was dried out (and the roof fixed), the problem went away.

I don't care what anyone says about AFCI's, I like what they do.

Years ago, I lived in a Viet Nam era built house with AL wiring. As I was closing the garage door one evening I noticed some flashing coming through a wall plate. Had it not been dark, I wouldn't have seen it. There was an old fridge plugged into that receptacle and it drew significant current on start up.

I paused, got out a screwdriver and took a quick look. Sure enough, loose neutral had been arcing. Left the fridge unplugged while I was out but tightened the neutral before I left. Family was waiting in the car. The next week was spent pig tailing everything I could get to. Houses in that tract burned about one every year all do to the wiring. Had they had AFCI's, all those homes could have been saved from fire damage. Speculative, I know, but I stand my ground (no pun intended).

What does that mean?
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
11,000
Location
Rhode Island
Come on, man. I told you that the complicated ceiling fan went south and tripped the AFCI. More than once. When I isolated the problem and fixed the fan with a kit, no more tripping.
Sorry, but unless there was a physical arc, the breaker did not do its job. The fan controller likely had a noisy switching signal that tripped the breaker. My friends gaming computer trips his AFCI breaker just from the switching noise of the power transistors when he loads a game up.
In addition to that, we had record breaking storms in January as you did. I had water coming down the wall by my chimney and into a wall box that has a sconce on it. I have these lights on a dimmer and when I cranked up the voltage the breaker tripped. When all was dried out (and the roof fixed), the problem went away.
That's a GFCI trip, and has absolutely nothing to do with the AFCI portion of the breaker.
I don't care what anyone says about AFCI's, I like what they do.
Neither of your examples have anything to do with the AFCI portion of an AFCI breaker doing its job. I've seen multiple experiments with people purposely creating arcs/bad connections and the AFCI breaker just sits there and happily ignores it.
 

Dragfluid

ALLIANCE MEMBER
Joined
Sep 15, 2013
Messages
17,611
Location
Pillager, MN
Quote:
Originally Posted by Dragfluid View Post
Grats?

What does that mean? -Zeke

It means congratulations on what you think is working.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
I'll just say this one last time. I live in an 87 YO house that had K & T through out most of the original house. I had my share of "buzzers" over the years. Finally about 4 years ago during a storm, and outside porch light got flooded and somehow sent the problem to a box downstream. When I switched off the light, the fault went away. The downstream J box where somehow a ground wire and a neutral got in touch with one another (this was a circuit extension off one of the old K & T lighting circuits — my fault for doing that — this circuit eventually went into conduit that made contact with the earth providing a false ground) was burned inside. From that point on the plan for a whole house rewire was put into place. Working with a licensed electrician, we together did the whole enchilada in a few stages. My wife even helped feed cable when we were both under the house of in the attic.

I really have to do the garage now. Don't have enough service and once again, the GEC is not proper even though most of the garage wiring is in conduit and has an EGC at least AFA the conduit itself is concerned. But, it all needs to be bonded as there is a breech somewhere. I may not be using the term false ground correctly, but there is a presence of some ground potential simply due to the conduit system running underground. No EGC inside.

I will set a subpanel and ground rod. A little off topic, but I may just install AFCI breakers for the garage and put a GFCI at the beginning of each circuit ( I have all this stuff left over). And run a green wire on the existing that will be kept in service.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
That's a GFCI trip, and has absolutely nothing to do with the AFCI portion of the breaker.

Neither of your examples have anything to do with the AFCI portion of an AFCI breaker doing its job. I've seen multiple experiments with people purposely creating arcs/bad connections and the AFCI breaker just sits there and happily ignores it.

No GFCI on my house lighting.

I'm sure you know what you're talking about, but it doesn't add up here. You don't know what was in that ceiling fan as they are rare and haven't been made for 30 years. But it involves a pot, large heat sink and a a transistor as well as a small control board. It was infinitely adjustable to nearly zero RPM. Nice aesthetics but no worky forever. So when the magic smoke appears, what do you want to call it.

All the replacement kits have been bought up all over the US. Now you just hack into it and use a 3 speed on pull chain just like every other cheap *** chicom fan.

On to the experiments. I think I understand that a short period arc does not trip the current generation breakers. I also think that the variation of a non controlled contrived arc simulation is not the real world

YMMV, but AFA I'm concerned, leave it there.
 

nomadskidoo

Well-known member
Joined
May 11, 2013
Messages
218
Location
iowa
AFCI/GFCI Breakers Blow(Open circuit,BLOWS) New Home Elec Contractors says"Normal"before even Done.Delete this GJ.@10months & no responce from General Contractor/Electricial,contractor,@$45 each X20 &@$8,000 for Home,,,a Normal Home.So,I'll replace them as Normal Blowing!
 