Hello all,

Looking into getting an IR SS4L5. Can anyone help confirm the amp loads so we can wire it correctly?

startup amps 24.4
working amps 21.56472f360c77446fe0cede8633d655187.jpg

Sent from my SAMSUNG-SM-N910A using Tapatalk
 

Attachments

  • 6472f360c77446fe0cede8633d655187.jpg
    6472f360c77446fe0cede8633d655187.jpg
    90.2 KB · Views: 0
To avoid these ads, REGISTER NOW!

454ragtop

Well-known member
Joined
Mar 24, 2008
Messages
5,011
Location
Carver, MA
Believe SFA is Service Factor Amps, the 1.15 SF means it can deliver a little more power. I'd wire it with #10 and you'll need a magnetic starter.
 
OP
E
Joined
Apr 25, 2014
Messages
24
Location
PA
thank you, but nothing to get a solid number for the amps at startup?

Sent from my SAMSUNG-SM-N910A using Tapatalk
 

pcmeiners

Well-known member
Joined
Aug 13, 2009
Messages
7,899
Location
In the only town in Pennsylvania, Bloomsburg.
startup amps 24.4, this is not going to be the instantaneous inrush, which would be a lot higher.
It will run at 21.4 until the pressure builds, then will rise to about 24.4 at full pressure.

# 10 should be good as long as your far from breaker box, if you want more info google "#10 wire capacity".

Been running a 30amp breaker for 5hp units
 
To avoid these ads, REGISTER NOW!

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
From the countless threads on GJ where sparky's have educated us . . .
. . . .
. . . . . . HP (horsepower) on the compressor motorplate . . . IS . .
. . . . . . . . . what determines
. . . .
. . . . . . . . . . . . . a) wire size
. . . . . . . . . . . . . b) breaker size

OP . . . since your motor plate indicates 5.0 HP, then you size it based on 5 HP.
 

md21722

Well-known member
Joined
Nov 30, 2015
Messages
1,840
Location
Mt Juliet, TN
Wire size by code is #8 NM-b (Romex) or #10 THHN (in conduit). A 30A breaker is normally fine with a 5HP single phase motor, but code allows up to 70A. If the compressor is more than 50 feet or out of sight of the breaker panel then a disconnect is required.
 

DSLTRK

Well-known member
Joined
Jan 7, 2012
Messages
1,118
Location
PHELAN, CA
I imagine this is not a continuous duty application, but if it is, conductors need to be sized at least 125% of the FLC, per NEC 430.22.
 