I am setting up/wiring my new shop. The air compressor will be in the back corner, basically as far away from the entry door as possible. This gets it out of the way and should help with some noise. 220volt 5 HP. What kind of switch could I mount by the entry door to control the compressor. I would like to be able to leave it on at the compressor and kill power to it when not in use. I would rather not have to open and close the breaker panel. Anyone done anything creative for such a control?
 
To avoid these ads, REGISTER NOW!

R7237

Well-known member
Joined
Jun 4, 2010
Messages
125
Location
Georgia
Damn,,, and here I have been installing large safety switches when all I needed was an $11 light switch. Don't I feel like an idiot.
 

G_P

Well-known member
Joined
Jul 11, 2010
Messages
7,135
Location
Central CT
If it uses a magnetic starter, all you have to do is put a double pole switch in the wires going from the pressure switch to the mag starter. This will kill the coil and prevent the compressor from starting.
 

sublimate

Well-known member
Joined
Aug 4, 2010
Messages
776
Location
Colorado

That should work, but if the compressor is that far from the door that you don't want to walk over to turn it on and off then it's a long way to run the wiring. Sure, if your panel is near the door then putting the switch in between the panel and the compressor is fine. But if your panel is nearer the compressor then I wouldn't run the wiring all the way up to the door and then back to the compressor.

If you don't have leaks then your compressor shouldn't be running anyways when you're not using the air. Why do you need to turn it off?
 

HAP

Well-known member
Joined
Aug 24, 2011
Messages
856
Location
NE North Carolina
If it uses a magnetic starter, all you have to do is put a double pole switch in the wires going from the pressure switch to the mag starter. This will kill the coil and prevent the compressor from starting.

Thats what I did on mine when I got it.
 
OP
B

Bearkat

Well-known member
Joined
Dec 15, 2013
Messages
91
The wiring is not ran, I want to add a shut off within the wiring I run. Panel is right at the door. The distance isnt a huge deal, I can walk over and turn it off, I am just trying to think of all options. I'm setting it up, only want to do it once, and want it very useful. I turn the compressor off when not in use because it sits for most of the week unused.
 

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,866
Location
oregon
Last edited:
OP
B

Bearkat

Well-known member
Joined
Dec 15, 2013
Messages
91
http://www.leviton.com/OA_HTML/ProductDetail.jsp?partnumber=3032-2I&section=41455&minisite=10251

Checking at the Leviton site above you will find that the 3032 series switch is only rated for 2hp. So if you intend to use this in the primary wiring your overloading the switch. You cannot ignore the inrush current of a motor!

lg
no neat sig line

Thanks, that was my concern. As mentioned above a disconnect would work, I was just hoping for something smaller. Worst case I can just walk to the compressor.
 

WhoWhatNow

Well-known member
Joined
Feb 22, 2011
Messages
1,884
Location
Collegeville, PA
If you are going to switch between the box and the disconnect then you will need a 5 hp rated motor switch.

http://www.amazon.com/dp/B003AU724E/?tag=atomicindus08-20

If you switch between the pressure switch and the motor starter than a regular switch will do.

I used the above switch to control the disconnect at the compressor and wired in a light as well. This way when the compressor is powered on the light is on. My compressor is in my basement so it is completely out of sight.
 

MartyO

Well-known member
Joined
Aug 2, 2010
Messages
1,310
Location
N.W. Georgia
How long a run are you talking about from the switch to the compressor?

Remember, you will need pretty heavy wiring on a long run, heavy amperage circuit.

The man door to my shop is in front corner and the compressor is at the back opposite corner. it is set up with a simple switch on the 110 leg to control a contactor that turns on the compressor. Think of a switch turning on a switch - much the way we use relays in automotive applications so that a small switch can turn something on like your blower fan.

I will say this was one of the best things I put into my shop. When I walk in, I flip on the compressor and while I get ready to work it airs up. Plus it saves me weaving all the w3ay through the cars stored in my shop to turn on my compressor each time I am in the shop.
 

sands35

Well-known member
Joined
May 29, 2012
Messages
936
Location
St. Joseph, MI
I have a three pole Square D disconnect switch. Two of the poles are for the compressor and one pole is for an indicator light off another common outlet circuit. I paid about $30 for the disconnect off Ebay. It has a 60 amp rating at 7hp.

I wanted three poles so I could have the indicator light. I could have used the tap rule for circuits, but my AHJ was squishy on if I could do that. I think I could have done that with a 2P disconnect, but I found a 3P for the same used price so I didn't have to explain my intent on inspection.

My compressor is closer to the door, so no worries about distance. But using a common light switch and a contactor (as above) would be my 1st choice for a long run from the switch to the compressor disconnect.
 
Last edited:
To avoid these ads, REGISTER NOW!

C96

Well-known member
Joined
Nov 30, 2013
Messages
1,251
Just walk back and turn it off at the compressor disconnect switch each day. The tank and lines need to be purged of water daily anyway. This will remind you to do both, also it doesn't hurt to give it a quick visual while you're there just to make sure everything is sound. :thumbup:
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Skip all the trouble, run from the breaker to the unit. Its just extra stuff that you don't need. Only reason to put one in is personal protection when they are remote.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
If the compressor is hardwired, and at 5 hp it should be, it is required to have a disconnect within 50 ft of, and within line of sight of, the compressor. Do not plan on using a plug and receptacle. Even a 50 amp plug and receptacle is only rated for 3 hp. To go any higher, you would have to use very pricey pin and sleeve connectors.

If the compressor has a magnetic starter, and I would hope a 5 hp two stage does, the easiest way to prevent it from running is to take one of the wires going to the pressure switch, and run it, using 14 gauge Romex or something similar, to a regular light switch near the door, thru the light switch and back to the pressure switch. You do not need to interrupt both wires at the pressure switch, just one of them.

This leaves power on the magnetic starter, but prevents the pressure switch from powering the magnetic starter coil and operating the compressor.

If you do not have a magnetic starter, you possibly do not have a true 5 hp compressor, but will need to interrupt the main power going to the compressor and switch the full amperage of it, on and off. You will need a switch rated for the amps and the horsepower you are dealing with.

Charles
 

MartyO

Well-known member
Joined
Aug 2, 2010
Messages
1,310
Location
N.W. Georgia
Skip all the trouble, run from the breaker to the unit. Its just extra stuff that you don't need. Only reason to put one in is personal protection when they are remote.

doesn't that assume that his panel is near his entrance to the shop?
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
If the compressor is hardwired, and at 5 hp it should be, it is required to have a disconnect within 50 ft of, and within line of sight of, the compressor. Do not plan on using a plug and receptacle. Even a 50 amp plug and receptacle is only rated for 3 hp. To go any higher, you would have to use very pricey pin and sleeve connectors.

If the compressor has a magnetic starter, and I would hope a 5 hp two stage does, the easiest way to prevent it from running is to take one of the wires going to the pressure switch, and run it, using 14 gauge Romex or something similar, to a regular light switch near the door, thru the light switch and back to the pressure switch. You do not need to interrupt both wires at the pressure switch, just one of them.

This leaves power on the magnetic starter, but prevents the pressure switch from powering the magnetic starter coil and operating the compressor.

If you do not have a magnetic starter, you possibly do not have a true 5 hp compressor, but will need to interrupt the main power going to the compressor and switch the full amperage of it, on and off. You will need a switch rated for the amps and the horsepower you are dealing with.

Charles

That would work but he would need to fuse the #14 control circuit down to 15 amps or less.

I had one other idea, you could mount one of these to the enclosure to make/break the control circuit, then run 2 wire thermostat cable to a switch to enable the dry contact in the relay.

http://www.functionaldevices.com/pdf/datasheets/RIB21CDC.pdf

http://www.functionaldevices.com/building-automation/drycontact.php
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
That would work but he would need to fuse the #14 control circuit down to 15 amps or less.
I believe it could be 30 for 14 and maybe 50 if it was a 12? (whoops,,, I see he said romex)

doesn't that assume that his panel is near his entrance to the shop?
I believe it is but it wouldn't really matter, I thin k in this case in the same room of a modest garage,,, basically within sight. If there is a contactor there is a switch, oncwe the unit is on the pressure switch is automatic. If its connected to equipment that leaks fix it or use ball valve at tank.
 
Last edited:

MartyO

Well-known member
Joined
Aug 2, 2010
Messages
1,310
Location
N.W. Georgia
oncwe the unit is on the pressure switch is automatic. If its connected to equipment that leaks fix it or use ball valve at tank.

Personally, in neither of my shops am I prepared to leave my compressor on when someone is going to be absent for an extended period of time. And, in my home shop, if I have to go back to the compressor to open or close a ball valve at the compressor end of things, then I have to walk to the far end of my building and go outside to boot. Yep, I am lazy and I don't want to walk outside every time I start or stop work.

At the end of the day, my contactor set up works great and was relatively cost effective to install.

Y'all are free to come over, see it, and drink the cold beverage of your choice! :beer:
 

Mongo68

Well-known member
Joined
Aug 28, 2009
Messages
166
I used an HVAC style 24v coil contactor. Used a regular wall switch and decora nightlight to turn on the 24v doorbell transformer on a 120v circuit. Low voltage wiring from there to the contactor out back where the compressor is. Contactor in a box with a plug on it for the compressor. Even left the original wiring to the compressor intact to the breaker panel so its all protected still... Hope my description makes sense.
 

dirtybiker

Active member
Joined
Nov 11, 2013
Messages
34
Location
WI
I have a magnetic starter like others in here also. But I wanted to be able to control the air compressor from either room in my garage. I installed 2 3 way switches, from the pressure switch. Now that I have that installed I would like to set up a light informing me that I have have the compressor on. I got my magnetic starter from eBay. It was cheep and easy to install. I also have a disconnect from the breaker box to the compressor. I ran a drain line from the compressor up the wall to a valve and back down and out side. I have no excuses now not to drain my tank every day. The drain line is probably 1/8" black dot air line but it works has not plugged yet.
 

TheEquineFencer

Well-known member
Joined
Jan 15, 2009
Messages
9,273
Location
Farmville, NC 27828
That would work but he would need to fuse the #14 control circuit down to 15 amps or less.

I had one other idea, you could mount one of these to the enclosure to make/break the control circuit, then run 2 wire thermostat cable to a switch to enable the dry contact in the relay.

http://www.functionaldevices.com/pdf/datasheets/RIB21CDC.pdf

http://www.functionaldevices.com/building-automation/drycontact.php

And I thought I was the only one that used them. RIBS Are the best.
 

Stroonzo

Member
Joined
Jun 23, 2014
Messages
19
This is what I am using for my compressor switch. My compressor is not in the same room:

http://www.amazon.com/gp/product/B002MPQ51O/?tag=atomicindus08-20

Leviton MS302-DS 30 Amp, 600 Volt, Double- Pole, Single Phase AC Motor Starter, Suitable as Motor Disconnect, Industrial Grade, Non-Grounding, Black

In one of the legs, I am powering a 120v indicator light (small 25 watt green bulb) to let me know the power is on (so I don't accidentally leave it on). I thought about getting creative and using a studio "On Air" sign, but why waste $70?
 