I searched, but came to the conclusion that while you may see something similar, electricity is just too dangerous to settle on.
I installed a double gang box in place of a single gang in a GFCI series of outlets.
I had the IN wire (supply side) and another OUT wire to the next box in the circuit.
I used WAGO lever nuts to pigtail the IN (HNG) into two sets wires, one for each outlet.
The OUT wire was connected directly to the "second" outlet in the box using the second set of terminals on the sides of the outlet.
I feel that this was correct. My main concern is with proper grounding with the bare copper wires.
I used a WAGO to create two pigtails for each ground screw on each of the two outlets. The OUT wire is also connected to the WAGO. So all the ground wires share a connection. This is correct right?
My Klein outlet tester (GFCI version) says everything is a go and I tested all the outlets with the GFCI test button and all were successful.
I just want to be able to sleep tonight without a fire extinguisher by the bed and one eye open. I am comfortable tackling wiring but I can't help being overly cautious.
In my photos you'll see some red electrical tape on a hot and ground wire. Those are the two HOT side wires coming from the box
I installed a double gang box in place of a single gang in a GFCI series of outlets.
I had the IN wire (supply side) and another OUT wire to the next box in the circuit.
I used WAGO lever nuts to pigtail the IN (HNG) into two sets wires, one for each outlet.
The OUT wire was connected directly to the "second" outlet in the box using the second set of terminals on the sides of the outlet.
I feel that this was correct. My main concern is with proper grounding with the bare copper wires.
I used a WAGO to create two pigtails for each ground screw on each of the two outlets. The OUT wire is also connected to the WAGO. So all the ground wires share a connection. This is correct right?
My Klein outlet tester (GFCI version) says everything is a go and I tested all the outlets with the GFCI test button and all were successful.
I just want to be able to sleep tonight without a fire extinguisher by the bed and one eye open. I am comfortable tackling wiring but I can't help being overly cautious.
In my photos you'll see some red electrical tape on a hot and ground wire. Those are the two HOT side wires coming from the box