Another "what size wire" question

ottsville

Member
Joined
Aug 2, 2016
Messages
6
Been looking at calculators and searching this forum most of the morning and my head is spinning.
I have a new detached garage that will have a 100 amp subpanel in it. The garage panel is approx 130' from the house panel, so with risers at both ends let's call it 150'. Wire will be run in conduit and buried 18".

I got a quote for 1800 to run the wire and make all the connections. Considering running it myself (should save about 1k). Electrician quoted based on #3 THHN x 3 and a #8 ground. All the calculators I'm using(maybe I'm doing it wrong) call for #2 or #1. What is correct?

Garage has 4 circuits, 1 30amp rv outlet, 1 15amp of lighting(led shop lights and exterior lighting) and 2 20amp outlet circuits.
 
To avoid these ads, REGISTER NOW!

marklc

Well-known member
Joined
Nov 24, 2015
Messages
82
I'd go at least #2 or go with #1 if your concerned about voltage drop at all. But at 150' I think you'll be ok with #2. I'd probably up the ground to a #6 also JMO.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
You can use number 2 alum and feed it with a 60, this gives good solid service for garage loads of this nature and V drop isn't an issue. Wire about a buck and a half a foot. Breaker 10 or 15$
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
When talking about wire size make sure you state if aluminum or copper. #3 is probably copper vs. #2 or #1 being aluminum.
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,726
Location
SE Michigan
Personally I'd buy enough 2" PVC conduit, some sweeps and LBs, rent the trencher, call miss dig, and have a 500ft spool of #2 THHN/THWN copper and a #6 bare ready to go.
 
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,155
Location
SE MI
You can use number 2 alum and feed it with a 60, this gives good solid service for garage loads of this nature and V drop isn't an issue. Wire about a buck and a half a foot. Breaker 10 or 15$

To restate what sberry said, if you limit the feed to 60A (which is more than enough for 98% of the one-man shops in existence) you can use #2 aluminum wire, like 2-2-2-4 HF, and save a LOT of $$$ !

Keep the 100A box if you want to connect a lot of circuits. Many heavy loads need a separate circuit per load, but are not likely to be run at the same time (welder and a table saw).
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,011
Location
Modesto, CA
#3 THWN cu or #1 AL will work at those distances for 100a.

Use #8 cu or #6 AL for the EGC.

Make sure to isolate the neutral bar in the subpanel. U may need a ground bar kit.

Also need 2 ground rods.
 

revamped

Well-known member
Joined
May 23, 2012
Messages
312
Location
Bremerton, WA
Dude, its exactly what I just did. I ran 125ft of 2-2-2-4 AL MHF in 2" PVC from the house to the panel location and everything cost me about $400. I ran it 36" underground due to driveway and I buried it with low voltage 1" conduit, my water line and my gas line.