Been looking at calculators and searching this forum most of the morning and my head is spinning.
I have a new detached garage that will have a 100 amp subpanel in it. The garage panel is approx 130' from the house panel, so with risers at both ends let's call it 150'. Wire will be run in conduit and buried 18".
I got a quote for 1800 to run the wire and make all the connections. Considering running it myself (should save about 1k). Electrician quoted based on #3 THHN x 3 and a #8 ground. All the calculators I'm using(maybe I'm doing it wrong) call for #2 or #1. What is correct?
Garage has 4 circuits, 1 30amp rv outlet, 1 15amp of lighting(led shop lights and exterior lighting) and 2 20amp outlet circuits.