I spent most of last year building the shell of my detached garage and decided to wait until this Spring to run my trenches for the Power and Gas. Now that the weather is starting to turn for the better I'm itching to get back to it so that I can actually start running wire and using the dang thing.
I've been attempting to educate myself on what I'd like to do for the electrical side of things so hopefully you fellas can help me out.
Here's the current setup:
Meter Main on house (4 slots - 200A Service)
Now here's what I'd like to do:
Meter Main on house
New Breaker Box on house (100A 6-Slot)
The issue I have is that I've been given about 200 feet of leftover Aluminum USE-2 2/0-2/0-2/0 wire so I'm going to run that with another Aluminum 1 AWG wire for the ground in 3 inch PVC Conduit to the Garage (approx 130 feet away). I know the 2/0 is overkill, but it was the right price - FREE!
However, I'm having a hard time wrapping my head around how to connect my 3 inch conduit to the smaller breaker box (perhaps using a reducer to 2 inch?) and then how to connect the huge 2/0 wire down to the 60A breaker.
I know for the detached garage I will need a exterior junction box where I convert the wire from USE-2 to THHN or similar before it can enter the building, but I don't know how that's supposed to look either.
I've got some basic diagrams if they will help clear things up.
I've been attempting to educate myself on what I'd like to do for the electrical side of things so hopefully you fellas can help me out.
Here's the current setup:
Meter Main on house (4 slots - 200A Service)
1 - 125A Double Pull Breaker - feeding house panel in basement
1 - 30A Double Pull Breaker - feeding A/C Unit Disconnect
Now here's what I'd like to do:
Meter Main on house
1 - 125A Double Pull Breaker - feeding house panel in basement
1 - 75A Double Pull Breaker - feeding NEW breaker box
New Breaker Box on house (100A 6-Slot)
1 - 60A Double Pull Breaker - feeding detached garage
1 - 30A Double Pull Breaker - feeding A/C Unit Disconnect
The issue I have is that I've been given about 200 feet of leftover Aluminum USE-2 2/0-2/0-2/0 wire so I'm going to run that with another Aluminum 1 AWG wire for the ground in 3 inch PVC Conduit to the Garage (approx 130 feet away). I know the 2/0 is overkill, but it was the right price - FREE!
However, I'm having a hard time wrapping my head around how to connect my 3 inch conduit to the smaller breaker box (perhaps using a reducer to 2 inch?) and then how to connect the huge 2/0 wire down to the 60A breaker.
I know for the detached garage I will need a exterior junction box where I convert the wire from USE-2 to THHN or similar before it can enter the building, but I don't know how that's supposed to look either.
I've got some basic diagrams if they will help clear things up.