Anyone have a wago 221 handy?
jeepxj
When were they purchased? What is the amp rating printed on the side? Thanks
Knight511
TX
Purchased at the beginning of June. 300v 20amp
I have the Wagos for #10 as well, but they are out in the shop.
velillen01
Wyoming
I got some back in late September/early October time frame (from the vendor so date of manufacture I don't know).
One side has the UL logo and is 450V/32A
The other side (with PSE logo) is 20A/300V
J
jeepxj
so whats the difference between the 20a and 32a rating? stranded vs solid?
Knight511
TX
IEC Approvals
Ratings perEN 60664
Nominal voltage (II/2)450V
Rated surge voltage (II/2)4kV
Rated current32A
Legend (ratings)(II / 2) Overvoltage category II / Pollution degree 2
UL Approvals
Approvals perUL 486C
Rated voltage UL (Use Group C)600V
Rated current UL (Use Group C)20A
J
jeepxj
IEC Approvals
Ratings perEN 60664
Rated current32A
UL Approvals
so lemme guess: 32a in the whole wide world. only 20a in the us.
J
jeepxj
Knight511
TX
rlitman
Long Island
No, it's just that the original 221 series (221-41x) is limited to 12 AWG (down to 24AWG), or 0.2-4mm^2 in communist sizing.
The 221-6 series are fine for 30amp on the #10.
Right. Because the new 221-61x will accept 10AWG (down to 20AWG), or 0.5-6mm^2 in communist sizing.
J
jeepxj
ok im tracking.
this is a 221-413. so 20a.
this is a 221-???? since its only to 12g? which is 32a (isnt 32a the ring circuit size in brittan?)
and these are the 221-613s which take to 10g.
then what the hell are these to 41a?
they **** at labeling with model numbers vs specs.
rlitman
Long Island
...then what the hell are these to 41a?...
That's the 221-61x on the back-side. It corresponds with the 32A rating on the 221-41x.
Forget the amp rating, as it's not important to you*. All you really care about is the wire size.
*Simply put, you're not going to have more than a 30A breaker, or a 24A continuous heating load on a 10AWG wire. Yes, you might be able to put a welder fed with 12AWG on a 50A breaker in some circumstances, but it's still not overloading the smaller Wago since the Wago ampacity is always higher than the admissible wire gauge. So if you're following the code with regards to the wire, and use the Wago that accepts that wire, you're all good.
J
jeepxj
Ahh duh. if the wire can fit it can handle the amp rating on the wire at 90c chart.
thanks.