Are these two breakers on the same phase/leg?

marklbucla

Member
Joined
Dec 6, 2010
Messages
18
Please see the attachment. Are the two QOT tandem circuit breakers in the red boxes on the same phase/leg of the panel? I believe this to be a Square D panel and is a subpanel, not a main panel.
 

Attachments

  • Capture.JPG
    Capture.JPG
    140.9 KB · Views: 321
To avoid these ads, REGISTER NOW!

snyder

Well-known member
Joined
Dec 18, 2008
Messages
545
Location
Baltimore md.
I don't mean to be *******, but I only see one incoming hot leg in that pic. Where is the second phase at?
 

mark flucke

Active member
Joined
Feb 14, 2016
Messages
33
don't see much for grounding-hopefully the conduit isn't being used for ground-I hate that!:mad:
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
You can hate it all you want but its as good or better than a wire in these type of circuits. The code people seem to think its adequate. If there was a better way they would mandate it.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,991
Location
Modesto, CA
where is this panel located?

Is there another panel in the same building as this panel?

If not, then there are too many breaker handles without a main. I count 9.
 
To avoid these ads, REGISTER NOW!

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
Don't know if your panel is correct or not, you can always set your multimeter to AC Voltage above 240 range... and poke both hot legs ... it will either read 0 or 240-ish....

looks like, I am guessing the two blue are incoming hot legs protect by 60AMP, tape over white is neutral, and that untaped black is the ground... but I am guessing, make use of that multi-meter ?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,991
Location
Modesto, CA
Don't know if your panel is correct or not, you can always set your multimeter to AC Voltage above 240 range... and poke both hot legs ... it will either read 0 or 240-ish....

looks like, I am guessing the two blue are incoming hot legs protect by 60AMP, tape over white is neutral, and that untaped black is the ground... but I am guessing, make use of that multi-meter ?

nope.

Theres 2 black hot legs. The one on the left and the one on the right to the right of the neutral. you can see the screw next to the breaker.
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
nope.

Theres 2 black hot legs. The one on the left and the one on the right to the right of the neutral. you can see the screw next to the breaker.

yea needed new glasses for my eyes.... ;p

still the same for the OP though... otherwise, shut down everything and see how the breakers are connected or used multimeter... not that hard..... odd breakers...
 
OP
M

marklbucla

Member
Joined
Dec 6, 2010
Messages
18
where is this panel located?

Is there another panel in the same building as this panel?

If not, then there are too many breaker handles without a main. I count 9.

This is the garage sub panel. There is a panel outside that controls this along with another sub panel inside the house.

Does this still need a main?
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
If it is the only panel in the garage then its the service disconnect to that structure and needs a main if there are more than 6 spaces or switches in the panel. The use of tandem breakers makes it more in this case.
If this is the main in that structure to make it legal would need to remove the tandems and replace with normal breakers and feed another panel with some more spaces you need.
 