Backfeeding panel with generator power

trackwelder

Well-known member
Joined
Jun 22, 2005
Messages
2,608
Location
n.y
With the recent ice storm in the northeast I have begun to think of how to power my house incase the power goes out. I am not an electrician by any means but can change an outlet or wire a plug. My neighbor states that I can trip the main breaker off any run a lead to my dryer plug to backfeed the panel and run my furnace and fridge. Just looking for opinions or experiences with doing this. I plan on having a new panel installed this spring and will add a transfer switch also.
 
To avoid these ads, REGISTER NOW!

Junkman

Well-known member
Joined
Dec 18, 2006
Messages
6,611
Location
Northeastern CT
If you back feed the power from a generator without the proper disconnect switch, you are doing an illegal act. I know that in CT, if Connecticut Light and Power find you back feeding without the proper disconnect switch, they will cut the lines to your home. They will not reconnect them until you properly upgrade the service. They are very forceful about this, since some linemen have been injured/killed as a result.
 

IHI

Banned
Joined
Mar 6, 2008
Messages
464
Location
Iowa
Trackwelder, that is how i do my house, luckily only had to do it a few times though. JUST BE SURE YOU SHUT OFF THE MAIN BREAKER!!!!!!!! This cannot be stressed enough, it is a very concious thing that has to take place or you could possibly kill a man trying to fix the situation!!!!!

That being said, i just have a 10/3 wire drop i put a twist lock end on to plug into the 220V side of my generator, and i just feed that wire through my dryer vent from outside the house and disconnect a elbow so i can pull it through and plug the other end i put a dry outlet compatible plug on into the dryer outlet. I only have a 1200swft house but can power everything off the 6500W generator like nothing special. I dont let the wife to laundry obviously, but other than that, the entire house is fully functional heating or cooling wise.

but shutting off the main breaker is a priority, guy have been killed from this, and yes, if your going to upgrade service figure in a transfer switch and be done. When we get ready to add onto the house i have to move the service to the side of the house so that is when i'll have my sparkey put the transfer switch in.
 
OP
T

trackwelder

Well-known member
Joined
Jun 22, 2005
Messages
2,608
Location
n.y
I definitely don't want to hurt anybody or risk losing my connection to the grid. Its just a pain running several cords. My uncle is an electrician maybe I can get him to rig something up.
 

Junkman

Well-known member
Joined
Dec 18, 2006
Messages
6,611
Location
Northeastern CT
Northern Tool has a 200 amp disconnect switch that is reasonably priced. I have the same switch in my home, but I got it from the electrical supply house. They had a pallet of them and were selling them for $100 each. I only wish that I had bought more of them at the time.. This was about 4 years ago..
 
OP
T

trackwelder

Well-known member
Joined
Jun 22, 2005
Messages
2,608
Location
n.y
Thanks Junk now I just have to research that tommorow. Northern has a great selection to chose from, and I like the 30 amp waterproof twistlock outlet.
 

Junkman

Well-known member
Joined
Dec 18, 2006
Messages
6,611
Location
Northeastern CT
For inexpensive twist lock plugs and recepticles, watch ebay. I have found great deals on name brands such as Hubbel and Bryant. A lot of what I have is going to be converted to twist lock plugs. That way, people will stop asking to borrow my battery charger.... :lol_hitti
 
OP
T

trackwelder

Well-known member
Joined
Jun 22, 2005
Messages
2,608
Location
n.y
For inexpensive twist lock plugs and recepticles, watch ebay. I have found great deals on name brands such as Hubbel and Bryant. A lot of what I have is going to be converted to twist lock plugs. That way, people will stop asking to borrow my battery charger.... :lol_hitti

Thats a good thought, I might run with that.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,056
Location
Northern Virginia
There was a thread on here recently, where a bolt on metal plate is applied to the service panel - it locks out the main breaker while the generator back feed breaker is enabled - prevents having both breakers engaged at the same time. This interlock/cover modification turned your existing service into a transfer switch and you did not have to install a new panel and move your circuits over - very clever.

I have a 50A 220V exterior mounted weatherproof outlet and a 50A matching breaker in my service panel. I took two 50A 4 wire range cords and bonded them together - so yes I have a cord with 2 males on it. When the power goes out, kill the main and all the breakers, connect the generator to the outlet with my cord, start the generator. Then I engage its 50A breaker, and then one by one bring on critical circuits like fridge, lights, etc. Works sweet.
 

Torque1st

MEMBER EMERITUS
Joined
Sep 14, 2008
Messages
5,668
Location
KC Metro, Kansas
This plate?

scaled.php


There was a big thread a little while ago on this very subject. The subject probably comes up every time there is an ice storm or some other disaster anywhere in the country.
 

Tscott

Well-known member
Joined
Oct 17, 2006
Messages
1,484
Location
Keystone Heights, FL.
Not to beat a dead horse. Oh who am I kidding :deadhorse beat away.

Sorry, but this is a very important thing to let people know. As stated above if you do not cut the main breaker you will energize the transformer and a large portion of the high voltage grid. So it is not just isolated to your transformer, and could easily kill a careless lineman miles away.

I think you have already made the decision to do it the right way. I think this is best as it is very easy to forget to do something as small as flip the main.

Tom
 

dipper

Well-known member
Joined
Jun 27, 2007
Messages
759
Location
Rochester, NY
So it is not just isolated to your transformer, and could easily kill a careless lineman miles away.

The careless one would be the homeowner who didnt properly follow NEC codes when "rigging" up his generator cause he's cold or doesn't want his food to spoil....not the linemen who is out doing his job and is unaware.

Bottom line.....get a transfer switch!!!
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I go for the eimple transfer switch for most normal homes, put the critical and a convenience circuit on it, helps avoid overloading the genset also. If not that have a set of plug and cord setups ready to go, change the furnace to a cord and plug deal.
I like the transfer panels vs the breaker lockout, helps limit the load.
 
Last edited:

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,674
Location
Maine
The main breaker does not interrupt the grounded conductor(neutral). Back feeding a panel can kill an unsuspecting lineman. If you can afford a generator to run your home in an outage, you can afford a transfer switch. Have it installed by a compentent electrician
 

LoneGunman

Well-known member
Joined
Mar 27, 2007
Messages
2,081
Location
The Gunshine state
Thank you Walrus, one thing though, breaker interlock devices like the ones someone posted a pic of are a UL listed and acceptable means to feed a panel from a generator, they obviously do not break the grounded conductor either.

For the people who are so sure their main is off and feel good about it, you must not have run into any power crews doing repair work, they will not check to see if your main is off, they will see your illegal backfeed and either cut your drop away or cut your drop away and leave and be sure to tell your neighbors why they are leaving. This is not a rumor, I have seen it first hand here in Florida after the hurricanes a few years ago. I also witnessed two people arrested who thought they were not going to allow anyone on their property to cut their drop. I cut three or four myself.

Once the drop is cut, power is restored EXCEPT for the person with the cut drop, I heard of one guy who was out for two weeks AFTER the power was restored.
 

LoneGunman

Well-known member
Joined
Mar 27, 2007
Messages
2,081
Location
The Gunshine state
Any thoughts on the item in the generlink link. I am going to call the power company and see if thats approved by them.

I've probably installed over 100 of them, I like them, they are a lot less money to install and you have the flexibility to pick and choose what you want on which you canot do with a transfer switch unless you spend big money.

My only gripe is they are so outrageously overpriced, it's a piece of sheet metal and a drill bit, I wish I thought of it. Panel manufacturers are making their own now and they are a lot less money than the interlockkit.com ones
 

Red Green

Well-known member
Joined
Dec 5, 2007
Messages
1,905
Location
South Central Michigan
I have a couple questions how would having the Ground hooked up hurt someone? How would the power company know if you were backfeeding without a switch unless they came into your house?
 

LoneGunman

Well-known member
Joined
Mar 27, 2007
Messages
2,081
Location
The Gunshine state
I have a couple questions how would having the Ground hooked up hurt someone? How would the power company know if you were backfeeding without a switch unless they came into your house?

Nobody mentioned the "ground" the "grounded conductor" was mentioned, the "grounded conductor" is the correct trade term used for "neutral". In many places in Florida the dryer is in the garage, and the garages were usually open, easy to see the generator feeding the dryer receptacle.

In the cases where they had a backfeed they went door to door until they found it or just told whomever was outside gathered around their trucks looking for info, "we'll be back when there is no longer a generator backfeeding our lines" , the residents took care of the problem.
 
To avoid these ads, REGISTER NOW!

Red Green

Well-known member
Joined
Dec 5, 2007
Messages
1,905
Location
South Central Michigan
Ok if the Main breaker doesn't turn off the neutral or "grounded conductor" what about the master disconnect switch that has the 3 main wires from the meter does that cut the neutral or just the hot also?
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,056
Location
Northern Virginia
Help me out here. The UL listed and approved metal interlock plate prevents the back feed breaker and the main from being enabled at the same time - we all agree on this. When the main is off, Line 1 and Line 2 from the grid to the house are severed - the house ground still goes to the ground rod, and the common from the grid is still connected. Then, when the back feed breaker is enabled, Line 1 and Line 2 from the generator is then routed to the buss bars in the panel, while (in my case), the generator plug's ground and common are always directly connected to the neutral and ground bars in the panel.

Please explain the difference between this and a transfer switch - I don't see any. To my knowledge, and I may be wrong, the transfer switch is only realigning Line 1 and Line 2 from the grid to the generator, just like what is achieved by having the main closed and the generator breaker enabled. In my view, the metal plate and the transfer switch simply provide an interlock to protect people from themselves and ensure that its one or the other (never both), and are the proper Code way of doing things.

I don't understand the comments about how with the main closed one could back feed the grid. When the power company jerks the meter, you loose Line 1 and Line 2, nothing else. The same as the main being closed.
 

Muttly

Well-known member
Joined
Dec 11, 2007
Messages
215
Location
Mid-MI
That being said, i just have a 10/3 wire drop i put a twist lock end on to plug into the 220V side of my generator, and i just feed that wire through my dryer vent from outside the house and disconnect a elbow so i can pull it through and plug the other end i put a dry outlet compatible plug on into the dryer outlet. I only have a 1200swft house but can power everything off the 6500W generator like nothing special. I dont let the wife to laundry obviously, but other than that, the entire house is fully functional heating or cooling wise.

Posting this on the internet is dangerous, you don't know who will read and use this information in the future.

I don't know what's worse, the energized male plug end or the 10-3 wire off of a 6500 watt generator.

If you are doing this on your own home to get by in an emergency that is one thing, but posting it up in a public forum for who knows to read is bad.

I think of some poor soul reading this and handing their kid the end of the cord to plug in as they fire up the generator.

Or someone tripping over a cord strung thru the house and unplugging a live male cord end that is carrying 220 volts at 30 amps next to the metal washer and dryer.
 

MAD

Well-known member
Joined
Jan 27, 2007
Messages
2,701
Location
Western MA
With a properly wired transfer switch, the human error factor is mostly eliminated. Just because you may know what you are doing, does not mean you should be trusted to break the grid connection before the generator connection is made.

With a Transfer switch everything should theoretically be tested to be foolproof before the permit is signed by the inspector.
 
Last edited:

trainer

Well-known member
Joined
Nov 28, 2005
Messages
2,019
Location
Northern Ontario, Canada
Posting this on the internet is dangerous, you don't know who will read and use this information in the future.

I don't know what's worse, the energized male plug end or the 10-3 wire off of a 6500 watt generator.

If you are doing this on your own home to get by in an emergency that is one thing, but posting it up in a public forum for who knows to read is bad.

I think of some poor soul reading this and handing their kid the end of the cord to plug in as they fire up the generator.

Or someone tripping over a cord strung thru the house and unplugging a live male cord end that is carrying 220 volts at 30 amps next to the metal washer and dryer.

The other thing is if you happen to not be at home during an outage and your wife or neighbor or daughter's boyfriend decides to start the generator and doesn't know that the main needs to be switched off.

And good luck in court if a lineman in your neighborhood gets electrocuted, even if it isn't your fault!
 

Tscott

Well-known member
Joined
Oct 17, 2006
Messages
1,484
Location
Keystone Heights, FL.
The careless one would be the homeowner who didn't properly follow NEC codes when "rigging" up his generator cause he's cold or doesn't want his food to spoil....not the linemen who is out doing his job and is unaware.

Yes and no. Our linemen have the motto, if it's not grounded, it's not dead. So if they don't ground it and get killed, then yes they were careless. Yes the homeowner is at fault, but the lineman is the one trained to work the power system and they are ultimately responsible for their own safety.

Remember, gloves and grounds are a lineman's best friend.

Tom
 

Torque1st

MEMBER EMERITUS
Joined
Sep 14, 2008
Messages
5,668
Location
KC Metro, Kansas
Larry- Terminology:
When a switch or breaker is CLOSED the conductor path is continuous, -connected, power can flow.

When a switch or breaker is OPEN the conductor path is broken, -NO connection, NO power will flow.
 

MAD

Well-known member
Joined
Jan 27, 2007
Messages
2,701
Location
Western MA
Larry- Terminology:
When a switch or breaker is CLOSED the conductor path is continuous, -connected, power can flow.

When a switch or breaker is OPEN the conductor path is broken, -NO connection, NO power will flow.

I did not notice that bit of confusion when I quickly responded to that post.

To clarify even more:

Open = off

Closed = on
 

Attachments

  • open_switch.jpg
    open_switch.jpg
    10.1 KB · Views: 29
  • closed_switch.jpg
    closed_switch.jpg
    13.5 KB · Views: 23

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,674
Location
Maine
Thank you Walrus, one thing though, breaker interlock devices like the ones someone posted a pic of are a UL listed and acceptable means to feed a panel from a generator, they obviously do not break the grounded conductor either. .

Don't know anything about those interlocks. Never seen one nor would I install one. Transfer switches are the only safe way that I know to use a generator( I guess you could cord and plug everything but...).
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,674
Location
Maine
Ok if the Main breaker doesn't turn off the neutral or "grounded conductor" what about the master disconnect switch that has the 3 main wires from the meter does that cut the neutral or just the hot also?

Depends on the disconnect but I would assume just the hots. They do make disconnects that will switch the neutral, I doubt they would be used in a residential situation?
 

Tscott

Well-known member
Joined
Oct 17, 2006
Messages
1,484
Location
Keystone Heights, FL.
Our rule is : It's live until YOU prove otherwise.

We ground everything we work on. The guys still wear gloves and treat it as hot even when grounded. There is no flashing light or siren before the juice begins to flow, so it is impossible to tell whether it will stay dead.

Tom
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,056
Location
Northern Virginia
Torgue1st and Mad - Understand on the closed (enabled) vs on open circuit.

All the posts up to then were saying how this was back feeding the grid. Not possible with the main breaker open. So, if one has his wits together, open the main breaker (sever the grid), close the back feed breaker (make the circuit) and let there be light.
 
OP
T

trackwelder

Well-known member
Joined
Jun 22, 2005
Messages
2,608
Location
n.y
I've probably installed over 100 of them, I like them, they are a lot less money to install and you have the flexibility to pick and choose what you want on which you canot do with a transfer switch unless you spend big money.

My only gripe is they are so outrageously overpriced, it's a piece of sheet metal and a drill bit, I wish I thought of it. Panel manufacturers are making their own now and they are a lot less money than the interlockkit.com ones

I was wondering about the item that the power company would hook up on the meter. It is in the generlink link and was wondering about. The item mounts outside behind the meter and is not the sheetmetal lockout device.
 

tdkkart

Well-known member
Joined
Jun 17, 2006
Messages
6,887
Location
Eastern Iowa
All the posts up to then were saying how this was back feeding the grid.

Not possible with the main breaker open.


So, if one has his wits together, open the main breaker (sever the grid), close the back feed breaker (make the circuit) and let there be light.


Yes, it is possible to feed power to the grid with the main breaker open. All it takes is two wires swapped in your cord and you're feeding 110V onto the grid through the neutral wire, which is NOT disconnected by the main breaker.
Even if you have the interlock plate shown earlier in this thread it does not guarantee a complete disconnect.

Now, theoretically, the neutral should be bonded to ground in the main panel, which is then connected to a ground rod, so it SHOULD trip the breaker on your generator IF the generator is also properly grounded.

BUT, there's alot of IF and ANDS and SHOULDS in this situation, they are all ASSuming a proper installation was done on your original panel.

Make damn sure your's right before you fire up the generator.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,056
Location
Northern Virginia
Yes, it is possible to feed power to the grid with the main breaker open. All it takes is two wires swapped in your cord and you're feeding 110V onto the grid through the neutral wire, which is NOT disconnected by the main breaker.

This is an installation error. With all wired correctly and no wires swapped, open the main & close the back feed breaker - this is exactly what is achieved with a transfer switch. If someone is not competent enough to wire and keep the legs distinguished and terminated properly, they have no business doing this and need to hire qualified help.
 

GSSFC

Well-known member
Joined
Apr 13, 2008
Messages
423
Location
Wolfeboro, NH
This is an installation error. With all wired correctly and no wires swapped, open the main & close the back feed breaker - this is exactly what is achieved with a transfer switch. If someone is not competent enough to wire and keep the legs distinguished and terminated properly, they have no business doing this and need to hire qualified help.

A lot of people do things they aren't qualified to do and often times make mistakes in doing so. The important lesson here would be how to do it correctly, there is more at stake here than your house not "working" right.

Tim
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,056
Location
Northern Virginia
I agree on doing things correctly. The metal adapter interlock plate or transfer switch only prevent the main and backfeed breaker from both being closed at the same time. Beyond that, its just wiring.
 

NWOhioChevyGuy

Well-known member
Joined
Feb 20, 2007
Messages
1,921
Location
Buckeye Hill (Morenci, MI)
Anyone on here have the Generlink installed????
What does it cost, in round number??
This is perfect for my situation; House 200 Amp service and garage power pulled from meter location has small panel that runs my well pump. (is not a sub panel of the house)

I have been trying to figure out how to put in a transfer switch and power my well pump. With this I don't have to, just plug in the generator at the meter.
 