Basic wiring diagram/question

coleman10

Well-known member
Joined
Nov 12, 2012
Messages
871
Location
Fort Lauderdale, FL
I'm trying to run a couple hot receptacles and a switched receptacle for a light above my new work area.

The source is coming from an unswitched box on the center of my garage's ceiling. Everything will be run in schedule 40 PVC.

All of this will be placed in on the wall according to the image, the top receptacle being switched for the overhead lights, the bottom receptacles will be constant hot for power. I can't think of any reason why this design won't work, but I'd figure I'd get a few opinions before I start this. I don't want to end up like this guy: :shocking:

Please pardon my artistic inabilities. :)

Thanks, guys.
 

Attachments

  • wiring.jpg
    wiring.jpg
    42.9 KB · Views: 122
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
It will work, but if I understand your color code you are switching the neutral which is an improper install method. You will still have an engerized hot wire at the outlet with the switch turned off.




*
 
Last edited:

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,942
Location
Central New Jersey
It will work, but if I understand your color code you are switching the neutral which is an improper install method. You will still have an engerized hot wire at the outlet with the switch turned off.*

What if his blue and red lines are the hot and the brown lines are the neutral?

Then he would have an always hot set of outlets at the bottom and the switch would control the hot to the outlets on the top.

I think this is what he wanted to do.

Jim
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
What if his blue and red lines are the hot and the brown lines are the neutral?

Then he would have an always hot set of outlets at the bottom and the switch would control the hot to the outlets on the top.

I think this is what he wanted to do.

Jim

Yeah, if that's the way he is doing the wiring then it is fine. I don't know why he used those colors. I was looking at the diagram on a scuffed up screen on a smart phone and wasn't sure of what was what. The brown looked black.
 
To avoid these ads, REGISTER NOW!

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,942
Location
Central New Jersey
According to my wife brown is the new black this year...........

Sorry, I couldn't resist.

If the line going from the switch to the bottom set of outlets was red and blue also, then he is suggesting he is going to use some 12/2 wire from the source into the top outlet box, and then running 12/3 down to the switch box and then 12/3 to the bottom box with the set of outlets.

The red wire would be the switched hot, the blue would be the constant hot, and the brown would be the neutral. And the green is ground of course.

Jim
 
Last edited:
OP
C

coleman10

Well-known member
Joined
Nov 12, 2012
Messages
871
Location
Fort Lauderdale, FL
Sorry, guys. Those were the only colors I had available to me and I figured it was better than using blue for all the lines. :) My fault that I should have noted what the colors where. After midnight my brains turn to mush. Yes, brown is neutral, blue and red are hot, and green, of course is the ground.

The intent is to make the top outlet switched. The bottom outlet is constant hot. Romex is 12-2. It's on a 20amp breaker. I figured 12-2 was the right way to go.
 

FordTruckWench

Well-known member
Joined
Jan 8, 2015
Messages
539
Location
California
The intent is to make the top outlet switched. The bottom outlet is constant hot. Romex is 12-2. It's on a 20amp breaker. I figured 12-2 was the right way to go.

If you are using Romex, and **-2 Romex at that, then your diagram doesn't apply. With 12-2 Romex, you might as well run your supply down to the switch box. Use wire nuts to split it in two directions: One goes down to the always on receptacle. The other visits the switch and then heads back up to the switched receptacle.
 
OP
C

coleman10

Well-known member
Joined
Nov 12, 2012
Messages
871
Location
Fort Lauderdale, FL
If you are using Romex, and **-2 Romex at that, then your diagram doesn't apply. With 12-2 Romex, you might as well run your supply down to the switch box. Use wire nuts to split it in two directions: One goes down to the always on receptacle. The other visits the switch and then heads back up to the switched receptacle.

Not certain why it wouldn't apply, but after reading your suggestion, yours is definitely simpler would require fewer splices. Thanks.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
Not certain why it wouldn't apply, but after reading your suggestion, yours is definitely simpler would require fewer splices. Thanks.

Because with NM-B aka Romex, u would have to run 12/2 to the switched outlet from the source, then 12/3 between the switched outlet and switch and 12/2 to the lower receptacle.

It will be less work and fewer splices if u bring the source into the lower receptacle and then feed the switch.
 
Last edited:
OP
C

coleman10

Well-known member
Joined
Nov 12, 2012
Messages
871
Location
Fort Lauderdale, FL
Because with NM-B aka Romex, u would have to run 12/2 to the switched outlet from the source, then 12/3 between the switched outlet and switch and 12/2 to the lower receptacle.

It will be less work and fewer splices if u bring the source into the lower receptacle and then feed the switch.

I had thought about that, which is kind of where I was going with my initial diagram. I used the suggestion of running to source the switch box, then feeding down and up. Installed, works great, pleased with the results. Thanks, guys!
 