Fair enough.
210.11.C.3 Requires a 20a receptacle only circuit for bathrooms, but provides an exception if the circuit supplies only one bathroom and additional equipment on the circuit is in that bathroom and complies with 210.23.A.1 and 2. This exception does not say "receptacle outlets", but "other equipment", and uses the best possible language, "shall be permitted".
You are reading up fom 210.23.A.1 to get to the exception you have posted about "receptacle outlets". This exception (the exception to 210.23.A) is included to reinforce what has already been stated in 210.11.C.3, but doesn't include the already excepted information. That would become pretty redundant, listing exceptions within exceptions.
I do agree with one thing, however, in that I don't like light fixtures and receptacles on the same circuit.
210.11.C.3 Requires a 20a receptacle only circuit for bathrooms, but provides an exception if the circuit supplies only one bathroom and additional equipment on the circuit is in that bathroom and complies with 210.23.A.1 and 2. This exception does not say "receptacle outlets", but "other equipment", and uses the best possible language, "shall be permitted".
You are reading up fom 210.23.A.1 to get to the exception you have posted about "receptacle outlets". This exception (the exception to 210.23.A) is included to reinforce what has already been stated in 210.11.C.3, but doesn't include the already excepted information. That would become pretty redundant, listing exceptions within exceptions.
I do agree with one thing, however, in that I don't like light fixtures and receptacles on the same circuit.