I din't have one yet but it's in the plans and I am doing the wiring now. Can someone tell me if it needs a 2 or 3 wire 220V outlet.
I din't have one yet but it's in the plans and I am doing the wiring now. Can someone tell me if it needs a 2 or 3 wire 220V outlet.
I din't have one yet but it's in the plans and I am doing the wiring now. Can someone tell me if it needs a 2 or 3 wire 220V outlet.
Darkk what does it use the neutral for? I thought you only needed a neutral when there was a portion of the system that needed 110V like a digital readout.
I'm pretty comfortable doing the wiring myself. I've run 3 20amp lines and a 50 amp 220 for the welders already. No problems with those.
I din't have one yet but it's in the plans and I am doing the wiring now. Can someone tell me if it needs a 2 or 3 wire 220V outlet.
You too.You need a neutral and two hots, so 3 wires plus ground. Since you asked this question, I would highly advise you to hire an electrician