Sandusky, Mi
I just installed a big max 50000 Friday. Put nest thermostat on so I can adjust the temp before I go out the shed. Two times now I have noticed that when I go out and check the nest says heating but the heater isn’t running the led on the heater is flashing slow I think that means normal operation but no call for heat. I had the heat set to 55 and it was down to 40-42. If I turn the breaker off and on the heater starts up and runs fine. Any ideas thanks
 
To avoid these ads, REGISTER NOW!

jlv03

Well-known member
Joined
Jan 19, 2020
Messages
343
Location
SE IA
Just to make sure it isn't anything funny with the thermostat, do you have a Common ("C") terminal connected on the Nest?
 

ripperd

Well-known member
Joined
Jul 2, 2014
Messages
2,041
Location
Twin Cities, MN
Did you look at the troubleshooting codes to confirm the blinking?

If it says the heater is in normal operation, when this is happening, you could unplug the nest and cross the W and R signals to manually trigger a heat call.
 
To avoid these ads, REGISTER NOW!
OP
J

jdw8320

Active member
Joined
Jan 3, 2010
Messages
38
Location
Sandusky, Mi
It’s like the nest is coming up to temp the first time and not after but saying on the display it’s heating. I chatted with Google support she said maybe the voltage was too high coming from the heater she wasn’t very helpfull. When the heater is powered up but not running and the nest calling for heat there’s 26.9 volts between the r and all three other screws on the heater. I hooked up the old cheap Mr heater thermostat when the heater running there’s voltage between the r and c, g but zero to w.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,615
Location
Fargo, ND
I hooked up the old cheap Mr heater thermostat when the heater running there’s voltage between the r and c, g but zero to w.
Sounds correct.

If it runs with the cheap factory stat, it is fairly obvious the Nest doesn't play nice with the heater for some reason. As for the voltage, the 26.9 Volts doesn't concern me. I often found HVAC equipment that ran at 26 volts.
 