Anyone know what size circuit a 50k big maxx heater requires? Cant find anything in the manual. Thanks in advance.
 
To avoid these ads, REGISTER NOW!

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
How many watts and what voltage is it. Divide the watts by voltage and that gives you your amps
Example 50000 watts divided by 240= 208.3 amps
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
The manual says to use 18 gauge or larger wire for line power connection. So it must not pull much amps. So a 15A 120V circuit should be plenty.
 
OP
M

Mike Honcho

Well-known member
Joined
Mar 17, 2009
Messages
163
Location
SE Michigan
Thanks everyone, another dumb question....is a switch for disconnect required if the the heater is within 3 to 4 feet from the sub panel
 
OP
M

Mike Honcho

Well-known member
Joined
Mar 17, 2009
Messages
163
Location
SE Michigan
I understand that, however my inlaw found a flexible whip new at the flea market. And i have a switch laying around, so if i can use what i have that's all the better. I just need to know if a switch is needed with the heater that close to the panel. Thanks.
 

ForceFed70

Well-known member
Joined
Apr 27, 2010
Messages
3,441
Location
BC, Canada
The cord and plug act as the disconnect.

You can't hook the hard wire the cord directly to the power


Best to check with your inspector on this. That was my plan and the inspector would have none of it.

During electrical I wanted to put a plug box on the ceiling to plug the gas heater into later. Inspector asked what it was for and said he wouldn't pass it when time came. I had to coil wire up in the attic and pull it through the ceiling when the heater was installed. For a disconnect, a standard light switch with red "emergency shut off" plate will suffice if you planned for it during your electrical rough-in. Otherwise you can mount a disconnect box right on the heater.

FYI: When I asked the inspector "Why not?" he basically told me that a gas heater is a permanent fixture and it's not appropriate to use a standard plug/outlet for a permanent fixture. When I pressed him on it, he said that it could vibrate lose especially when installed on the ceiling, causing nuisance calls and potential arcing.

I personally think using an outlet would be fine, but speak with your inspector. If nothing else, you may want to consider a twist-lock plug.

Another note: By code, the heater is supposed to be on a dedicated circuit. If your inspector doesn't give you a hard time about using an outlet, he may give you a hard time about the dedicated circuit. Assuming you're going to need/involve an inspector tho ;)

Oh, and to answer your question: My 85k Big Max is rated at 4.7A or roughly 500W. I'd expect yours to be similar or slightly less.
 
Last edited:

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
... If nothing else, you may want to consider a twist-lock plug.

Another note: By code, the heater is supposed to be on a dedicated circuit. ...

My heater is on a dedicated circuit with a twist lock plug. I setup that way because the garage is not on the emergency generator circuit so if I need to I can unplug it and use one of my big 12 AWG extension cords connected to the house.
 