Bonding a neutral, generator
Britrider
CT, upstate NY
I have a powermate 5000 that was setup to run from a transfer switch, so the p.o. floated the ground. I want to run it as a stand alone in the field so need to bond the ground. Can I just run a jumper wire from a green ground terminal under the cap to a white neutral terminal? Thanks in advance
--RW
larry4406
Northern Virginia
Yes
Or take a male plug and jumper the neutral to the ground and then plug it it one of the outlets when you want to run it bonded.
I added a switch to mine.
58Yeoman
Central IL
For us non-electrical folks, what is the difference between bonded and floating? Why would you want to switch back and forth?
larry4406
Northern Virginia
I am no sparky.
When running generator as a portable, it is a separately derived system so neutral and ground should be single point bonded as there is no other bond.
When running generator in standby, it is connected to the house via 4-wire feed which means the neutral and ground bond is at the main panel or disconnect so you need to keep it separate. Hence term floating.
LS6 Tommy
Northern NJ
Yes
X2. Added a switch on mine, too. Just break the N on the genny frame.
Tommy
510ebl
Southern New Jersey
Tommy
This is on my short list of things to do...
For a 7KW/9.2KW open frame inverter gene, what should be switch be rated for? Would a 120/240V 20A SPST suffice?
Sorry about the Hijack, I hope this is somewhat relevant to the OP’s original question.
LS6 Tommy
Northern NJ
I honestly don't remember what switch I used.
I would use 10 AWG wire for you 9.2Kw genny, but I'm not sure if you can derate the switch since it's a ground.
Tommy