Bonding a neutral, generator

Britrider

Member
Joined
Sep 26, 2020
Messages
10
Location
CT, upstate NY
I have a powermate 5000 that was setup to run from a transfer switch, so the p.o. floated the ground. I want to run it as a stand alone in the field so need to bond the ground. Can I just run a jumper wire from a green ground terminal under the cap to a white neutral terminal? Thanks in advance
--RW
 
To avoid these ads, REGISTER NOW!

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,845
Location
Northern Virginia
Yes

Or take a male plug and jumper the neutral to the ground and then plug it it one of the outlets when you want to run it bonded.

I added a switch to mine.
 

Attachments

  • IMG_1035.jpg
    IMG_1035.jpg
    59.7 KB · Views: 55

58Yeoman

Well-known member
Joined
Oct 1, 2010
Messages
8,999
Location
Central IL
For us non-electrical folks, what is the difference between bonded and floating? Why would you want to switch back and forth?
 
To avoid these ads, REGISTER NOW!

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,845
Location
Northern Virginia
For us non-electrical folks, what is the difference between bonded and floating? Why would you want to switch back and forth?

I am no sparky.

When running generator as a portable, it is a separately derived system so neutral and ground should be single point bonded as there is no other bond.

When running generator in standby, it is connected to the house via 4-wire feed which means the neutral and ground bond is at the main panel or disconnect so you need to keep it separate. Hence term floating.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Yes

Or take a male plug and jumper the neutral to the ground and then plug it it one of the outlets when you want to run it bonded.

I added a switch to mine.

X2. Added a switch on mine, too. Just break the N on the genny frame.

Tommy
 

510ebl

Well-known member
Joined
Jan 20, 2015
Messages
518
Location
Southern New Jersey
X2. Added a switch on mine, too. Just break the N on the genny frame.

Tommy

This is on my short list of things to do...

For a 7KW/9.2KW open frame inverter gene, what should be switch be rated for? Would a 120/240V 20A SPST suffice?

Sorry about the Hijack, I hope this is somewhat relevant to the OP’s original question.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
This is on my short list of things to do...

For a 7KW/9.2KW open frame inverter gene, what should be switch be rated for? Would a 120/240V 20A SPST suffice?

Sorry about the Hijack, I hope this is somewhat relevant to the OP’s original question.

I honestly don't remember what switch I used.
I would use 10 AWG wire for you 9.2Kw genny, but I'm not sure if you can derate the switch since it's a ground.

Tommy
 