this is done all the time in kitchens, run a 3 wire from two breakers and they share the same neutral
Apples and oranges to the OP's question.this is done all the time in kitchens, run a 3 wire from two breakers and they share the same neutral
This is not allowed. If you want to run two different circuits to a two gang box, you need to get a box w/ a divider so when working on one, you can't touch the other. This means w/ the divider you can't bond the neutrals.
Without my code book in front of me, I believe the difference of potential needs to be 300V+. That's why when we do multiple 277V circuits in a switch box we need dividers.
You are not required to have a divider unless the circuits are of different voltages. As others have said, keep the neutrals separate, but tie all of the grounds together.
As mentioned above, you could run a three-wire branch circuit (shared neutral), but the wires must be landed on adjacent circuit breakers in the panel with a listed breaker tie handle (meaning both circuits on, or both circuits off).
NO.If you bonded the neutrals and had the two hot wires on adjacent breakers, wouldn't you effectively get 220 on the neutral?
This has nothing to do with "220" circuits. The point is ONLY the neutral assigned to the circuit should be attached to the circuit. The neutral is a current carrying conductor and it must only carry the current from said circuit(s).its already been said what you are doing is creating a 220v circuit which is fine for 220v
equipment on a shared receptacle. Not that it wouldnt work, people do it all the time but it isn't the proper way to do it. The nuetral will carries the unbalanced load of the two circuits and this could be dangerous. I've had the fire knocked out of me on jobs where so called electricians have shared the nuetral on multiple circuits...
You are not required to have a divider unless the circuits are of different voltages. As others have said, keep the neutrals separate, but tie all of the grounds together.
As mentioned above, you could run a three-wire branch circuit (shared neutral), but the wires must be landed on adjacent circuit breakers in the panel with a listed breaker tie handle (meaning both circuits on, or both circuits off).
Absolutely.So you can put two circuits in double gang box? I am working on my plan and would like to do that in a couple of locations.