bonding NOT grounding question
Alchymist
Central PA
The idea is to pop the circuit breaker should the water, gas or whatever line become energized.
Your water/gas lines coming into the structure served by the sub-panel should be ELECTRICALLY CONNECTED TO the sub-panel enclosure I.E. the equipment ground.
They should NOT be electrically connected to neutral in the sub-panel.
Just an observation - the definition of "electrically connected" - the above should technically read "mechanically connected". In true kibitzing - the bonding wire IS "electrically" connected to the neutral in the sub panel. It connects (mechanically, correctly) to the ground bar in the sub panel, which is directly connected to the ground bar in the main, said main ground bar in the main being bonded to the neutral, and the neutral in the main is directly connected to the neutral in the sub. Just being my usual :evil:
Orionrising
Western Maine
Yes, this could be worked on but it's 6 and need to go this morning. We might get back to it. In your case is the well casing steel? I should really fix a detail on my own but I forget it.
Nope concrete well tile. Only metal on that end is a brass foot valve.
Sent from my Moto G (4) using Tapatalk
LX-Markham
Markham, Ont.
I had a general idea of what 'bonding' was, as opposed to 'grounding'. Thanks for clearing up the 'why'. It makes sense now.
And now I'm confused again, LOL.
I have a similar situation in my detached garage. There is a 100A sub-panel in the garage fed from the house main panel. I just had a gas-line installed in the garage for a heater. It is fed from the house via underground poly pipe. The gas-fitter left me with a bonding kit. I know where to connect the clamp to the gas pipe, but I'm confused as to where to connect the other end?
sberry
Brethren, Michigan
No, we do not want anything that has current flow on it connected or bonded at the sub, if it did the neutral currents would have an alternate pathway back to the main, they wouldn't know which wire to take and take both. We want neutral currents to stay on neutral wire and the ground only to carry current in the event of a fault.
Right. GEC is required to be sized different than the bond as I recall but,,, that is recollection. I believe for bond it is the largest circuit likely to be energized and inspector didn't blink at 10 to gas on my last job and he was a pro. The other exception is to a steel building frame, like a modular etc,, 8 for 100 and 6 for 200.
no. bonds are sized based on what they are bonding to. has nothing to do with largest circuit that may energize them which is what table 250.122 is all about.
8 for 100 and 6 for 200 isnt a bond size. Thats an EGC size in a feeder. Table 250.122 dictates that.
You are the one confusing things.
please re-read what I said ...Its one ground called earth ground, I tend not to use misuse the word 'ground' the branch green wires I call SE safety earth.
see they how they twist and turn.
are u from austrailia? yes you are the one who is confusing things.
No where in the NEC is an equipment grounding conductor called an "SE safety earth" or "earth ground".
That right there shows that u are speaking from experience with a foreign electrical system and dont know how an equipment grounding conductor provides a low impedance pathway for fault current.
The "earth" has ABSOLUTELY NOTHING to do with clearing fault current.
yes you are confusing things. Please read the article i posted above.
The way an EGC works is it provides a low impedance fault current pathway via the connection to the neutral bus bar in the main service panel. Without this bonded neutral bar, there is no short circuit pathway established between hot and ground.
I have been on many service calls where either this bond was not present in the main panel or the plumbing wasnt bonded to the neutral bar and the plumbing ended up getting energized because of a separate issue. The breaker of the offending circuit did not know to trip because of the missing neutral bar bond.
Again, please try to understand that the "earth" doesnt provide any kind of fault current pathway WHATSOEVER.
Wherever or however u learned this, it is wrong!!
Grounding electrodes and the GEC connected to them is for grounding lightning. Due to earth's relatively high impedance, the current from a short circuit will not be a high enough magnitude after flowing through earth to cause a breaker to trip.
that's the safety return for fault currents on each branch. aka the 3rd wire its either green or bare. These are all 'bonded' together properly at the panel (use a modern panel with national safety approvals and you don't have to think about it too much)
Please tell me which NEC article calls an EGC a "safety return".
and there is no such thing as "national safety approvals". NTLs (national testing laboratories, such as U/L(that u claim to work at; below) dont APPROVE anything. THEY LIST. But u should know this if you work there...
BTW what do u do at U/L?
I reckon it depends what end of the stick yer looking from. I'm usually at the customer equipment end / Underwriters Laboratories u know the guys that deal with safety (where the rubber meets the road.)
There is no variance. NEC code calls it an EGC. Its not a safety earth SE or any of that other jargon you refer to it as.
SE definition never changes, NEC cant make up their minds:lol:
Again please show me where "SE" is in the NEC....The NEC has never changed their minds on this subject so Im not sure where u pulled that out of....
The point we were trying to make was while they are bonded together it's point is not to go to earth.
:+1: exactly
The earth has NOTHING to do with fault current pathways.
no go to earth ground at the main panel, really? the expert here is already talking 2 buried rods not more than 5 ft it?
yes the OP has multiple things going on here. The rods are for lightning suppression. And min spacing is 6' not 5'....
This is a separate subject than the gas line bonding which u have not brought up again despite giving incorrect advise to not bond it. Or the EGC subject....
i think reading comprehension is getting the best of you...
No one said it didn't get hooked to earth, the point is that it is supposed to get hooked to neutral service main, the earth is NOT a fault return path.
:+1: exactly. Im not sure if we are having a comprehension issue here with Infinia or a lack of understanding on his part.
sorry I don't know who 'we' ,'they' or it, is in reference to.
care to buy a noun or two.
NM I'll leave the OP in your,( their) hands. have fun!
sberry was referring to him and I.
First - I really appreciate all of the input, even though I didn't intend it to, it seemed to have derailed just a tad.
I'll hopefully complete the rough by the week after next.
For the record, I am in the process of collecting information and I am taking what I can get. As you mentioned (Infinia) it is really up to what the inspector wants and ultimately, that is going to dictate the final outcome, right or wrong. I do actually appreciate the initial comments on trying to find and electrician to inspect the work and be here for the inspection, that was actually solid advice.
I am not an electrician I don't claim to be. I like learning things and the best way that I know how to do that, is by taking bits of information from multiple sources. Not just one person, one book, etc. I appreciate all the time everyone took to respond. I am able to learn and take bits from EVERYONE that contributed and for that I thank you.
I hope maybe one day I can help some of you with some advice that I have gained through my profession.
That is actually misleading. The inspector cant want or require u to do something that is not code or a local amendment. And many inspectors have no idea what theyre talking about.
this is an interesting question for rural folks. My well pump is grounded, which I assume grounds the housing not just the motor, but it is more then 5' into the house. Other then the faucets, and one connector, there is no metal in the plumbing, it is all CPVC or PE....
depends on what type of pipe and casing.
There is specifics in the NEC for it to qualify as an electrode.
yes that is the idea.
water and gas line bonding is required to be connected to the GES- grounding electrode system thus eliminating the subpanel as a viable connection. The usual way this is accomplished is via the bonded neutral bar in the main service panel.
Then it doesnt qualify as an electrode. So u should have rods...or a UFER...
Does this heater plug into a an outlet?
The other end of the bonding wire should go to the ground bar in the subpanel.
But youre subpanel may be older than 2008 and may be 3-wire and have a bonded neutral bar instead.
Is the subpanel 3-wire or 4-wire? when was it installed? Do u have rods outside connected to subpanel?
:+1: :thumbup: right on the money as usual...
And this is especially the case where there is parallel metallic pathways...
Ok, the well having only grounded motor is fine. It changes things if this was a steel well with sub pump and/or steel drop pipe.
:+1: :thumbup: right on the money again. well said and explained....heres a :beer:
sberry
Brethren, Michigan
I get real curious when my memory fails a bit. I havnt read much of the book and only recall a different requirement for bonds when the piping - wasn't being used as an electrode, both it's location and size but again maybe 15 years since I really read it.
This is a reason I don't go in to many threads in areas other than what I do, I really dont know much about it or understand it well enough to be explaining it to others, my splainin is a problem for stuff I do.
I happen to work and live on simple single phase service and have a lot of this equipment. Learning this was a simple survivor skill, my traing along the way was often poor and I made a lot of mistakes, I work on those areas, I can see where others do the same so I am acutely aware.
sberry
Brethren, Michigan
This isn't meant to blow smoke up anyone's *** but i really learned the right way from guys on the internet like Wylie and others here that kept going over it until I finally got it, same stuff over and over and I am not the only one. There are a lot of people today now know how to ground a piece of equipment because of it. Prolly took a couple years for it to become the reflex it is.
teamextreme
Lakewood, CO
You can add me to the "we" as well. Wylies and sberry are spot on. Infinia, you are clearly using non-industry standard terminology, either due to the fact that your experience is from a country outside the US, or just plain lack any training or exposure to North American standards. Either way, you're off the mark on this.
sberry
Brethren, Michigan
I got nothing against infinia bringing this up. It is this kind of discussion that works it back and forth. Not all of us get it explained 1 way, i didnt get to my understanding overnight, took me a long time. I get in a hurry and get frustrated, maybe he gets it in his own way, he probably does the install correctly even with wrong term.
I believe the term electrically connected refers to the grounding conductor being in the same cable, pipe or raceway as the supply conductors.