moparsandharleys
Well-known member
Ok i have made myself pretty familiar with this furnace the last few days.
Exhibits normal startup and function all except for no Ignitor glow. Then goes into code 34- failure to prove flame. and eventually code 14- lockout.
THE IGNITOR IS NEW. Replaced by me yesterday.
Flame sensor has been cleaned.
Burner was dissasembled and cleaned.
Airflow from inducer motor was tested and found to be good. Also smell of natural gas is present in exhaust at startup so gas valve seems to be working properly.
I just can not figure out why the damn ignitor wont glow... Background. It did function 2 days ago sporadically with a cracked ignitor. Last time ran properly for a full cycle then have had problems since. Is it possible the NEW ignitor i purchased and installed is defective? HELP!!
Exhibits normal startup and function all except for no Ignitor glow. Then goes into code 34- failure to prove flame. and eventually code 14- lockout.
THE IGNITOR IS NEW. Replaced by me yesterday.
Flame sensor has been cleaned.
Burner was dissasembled and cleaned.
Airflow from inducer motor was tested and found to be good. Also smell of natural gas is present in exhaust at startup so gas valve seems to be working properly.
I just can not figure out why the damn ignitor wont glow... Background. It did function 2 days ago sporadically with a cracked ignitor. Last time ran properly for a full cycle then have had problems since. Is it possible the NEW ignitor i purchased and installed is defective? HELP!!
Last edited: