To avoid these ads, REGISTER NOW!

Calculating gas line size?????

blacty

New member
Joined
Feb 23, 2009
Messages
2
guys need some major help here. I am having a hard time sizing my needs for my gas line. I have a Reznor 200,000 btu heater that is 125' away from my tank. I would like to run the minimum size of gas line for cost reasons. Home depot says 3/4"(don't trust the knowledge) and my propane supply store says I can get away with 1/2". Does anyone have any tips on trying to calculate this?
 
To avoid these ads, REGISTER NOW!
OP
B

blacty

New member
Joined
Feb 23, 2009
Messages
2
Thats what I was thinking too! Don't know why he thought I could get away with 1/2" Thanks for you help!
 

Chris 50

Well-known member
Joined
Feb 4, 2007
Messages
86
Location
LaPorte IN.
Also, don't forget if you plan to run a gas water heater in the future, that will require more volume. I'm on natural gas and ran 1 1/4" line about 150'. The guy at the supply place had a chart showing what size to run based on BTU requirements, length of run and line pressure from the gas company.
 
To avoid these ads, REGISTER NOW!

calsaxe

Member
Joined
May 4, 2007
Messages
6
Here is the pdf file for the tankless water heater I am installing. On page 15 it has a chart for both natural gas and propane gas supply lines. The graph will show you the diameter of pipe needed to supply a certain volume of gas over a given length of run. I would definitely oversize for future appliances (gas water heater, gas furnace, gas stove, etc.).

http://www.takagi.com/download/product_manuals/T-K3-OS.pdf
 

38 Special

Well-known member
Joined
Feb 16, 2009
Messages
105
Location
Irondale, Alabama
You can run a smaller gas line if the regulator is put at the other end, 125' away from the tank. Check local requirements first.

Look at Two stage piping. In the REGO book above, page 20 shows 3/8" copper will flow 142,000 BTU at 10 PSI.
 

BrokeEF

Well-known member
Joined
Dec 24, 2008
Messages
341
Location
Elgin, IL
What is the supply pressure, how far away will the regulator be from the burner?

Sean
(Sales Engineer for a burner manufacturer)
 
To avoid these ads, REGISTER NOW!