I have a Maxjax that requires 30amp breaker. My garage is fairly new, but has 20amp breakers for wall outlets. Can I just replace one with a 30amp breaker to use for the Maxjax? Thanks,

Don Ivey
Smithfield, NC
 
To avoid these ads, REGISTER NOW!

bww_mnm

Well-known member
Joined
Dec 30, 2010
Messages
673
Location
Chicago area
I have a Maxjax that requires 30amp breaker. My garage is fairly new, but has 20amp breakers for wall outlets. Can I just replace one with a 30amp breaker to use for the Maxjax? Thanks,

Don Ivey
Smithfield, NC

No. Your wiring won't handle 30a. Potential fire hazzard.
 

djd99

Well-known member
Joined
May 4, 2009
Messages
1,006
Location
Owosso,Michigan
Everybody will say no because code says you have the have #10 wire for a 30 Amp breaker. I will say this I've been doing it for my air compressor and don't have any issues it's just not code.
I still won't recommend it for that reason but I will continue to do it as I cant rerun a #10 wire. My compressor will not run on a 20 amp circuit without tripping the breaker on startup so I threw in a 30 and haven't had a problem since. Don
 

plinker

Well-known member
Joined
Feb 28, 2007
Messages
4,285
Location
Northern Wi
For code, you will need to run 10ga or bigger wiring for the 30A breaker.
I would run 8ga wire myself.

Everybody will say no because code says you have the have #10 wire for a 30 Amp breaker. I will say this I've been doing it for my air compressor and don't have any issues it's just not code.
I still won't recommend it for that reason but I will continue to do it as I cant rerun a #10 wire. My compressor will not run on a 20 amp circuit without tripping the breaker on startup so I threw in a 30 and haven't had a problem since. Don

I dont know how many amps a lift pull's, but your compressor wont likely overload the circut as bad, I think.
 

dirttracker18

Well-known member
Joined
Aug 10, 2009
Messages
3,191
Location
Slate River, ON
Everybody will say no because code says you have the have #10 wire for a 30 Amp breaker. I will say this I've been doing it for my air compressor and don't have any issues it's just not code.
I still won't recommend it for that reason but I will continue to do it as I cant rerun a #10 wire. My compressor will not run on a 20 amp circuit without tripping the breaker on startup so I threw in a 30 and haven't had a problem since. Don

Very different for a compressor that sees a spike in amps when it turns on then likely levels out at something much lower. If your compressor is suppose to run on 20 amps (does it have a 20 amp plug on it? Rating on compressor?) and trips the breaker you have a problem and should get it fixed.

A heater on the other hand will see a continious pull of higher amps. Code is there to protect you not to be some kind of a hassel. Do it right and sleep well at night.

Simple answer is no, you are asking for a fire in your wall.

Run an external line (correctly sized and shielded if not in conduit) out of your panel to an new appropriate outlet directly below. Short and sweet and within code.

Perhaps an electrician can chime in here (or place this in electrical as well) and let us know if you can run it right next to your panel and how short it can be.
 
Last edited:
OP
D

DonIvey

Active member
Joined
Mar 25, 2009
Messages
35
Thanks for all the replys. I think the external line in conduit will suffice, and I'll feel safer when using it. Thanks again,

Don
 

1948

Well-known member
Joined
Oct 14, 2011
Messages
569
Location
IL WI border
ever look at how a lightbulb works? imagine that as your wires in your wall....... covered with a nice melt-able plastic.....
 

FreddiFiche

Well-known member
Joined
Aug 8, 2011
Messages
126
Location
Minnesnowta
Everybody will say no because code says you have the have #10 wire for a 30 Amp breaker. I will say this I've been doing it for my air compressor and don't have any issues it's just not code.
I still won't recommend it for that reason but I will continue to do it as I cant rerun a #10 wire. My compressor will not run on a 20 amp circuit without tripping the breaker on startup so I threw in a 30 and haven't had a problem since. Don

It's your garage.....but something to consider;

If you do have a fire (we all hope not!), whether this is the cause or not, your just setting yourself up for a fight with the insurance company. They are very good at the miss-direct, delay, 'find any reason to delay/reduce the payout.' If they bring in a fire investigator, one of the first things they do is run down the breakers, looking at sizing and wire tied to it. (And this doesn't have to be a 'total loss' fire either....)

Not trying to be preachy, just really don't want you to end up on the short end of the stick if something bad does happen. Any way to add a new run? (Even surface mount?)

Good luck.

Freddi
 

cw_racefan

Well-known member
Joined
Feb 7, 2006
Messages
254
I have a Maxjax that requires 30amp breaker. My garage is fairly new, but has 20amp breakers for wall outlets. Can I just replace one with a 30amp breaker to use for the Maxjax? Thanks,

Don Ivey
Smithfield, NC

On top of what everyone else has said, I questioned this when I first got my MaxJax, because they were inconsistent with what they said for ratings. Mine was an early one, so they may have changed, but the unit itself does not have a 30 amp plug on it. I called them and they said a 20 amp circuit would be fine. Been using mine for three years now and never had an issue on a 20 amp circuit (dedicated circuit).

Craig
 
Last edited:
To avoid these ads, REGISTER NOW!

djd99

Well-known member
Joined
May 4, 2009
Messages
1,006
Location
Owosso,Michigan
Very different for a compressor that sees a spike in amps when it turns on then likely levels out at something much lower. If your compressor is suppose to run on 20 amps (does it have a 20 amp plug on it? Rating on compressor?) and trips the breaker you have a problem and should get it fixed.

I have a 5hp farm duty that needs around 30 amps on startup





Thanks for all the replys. I think the external line in conduit will suffice, and I'll feel safer when using it. Thanks again,

Don

Probably they best solution is to run a new line.

It's your garage.....but something to consider;

If you do have a fire (we all hope not!), whether this is the cause or not, your just setting yourself up for a fight with the insurance company. They are very good at the miss-direct, delay, 'find any reason to delay/reduce the payout.' If they bring in a fire investigator, one of the first things they do is run down the breakers, looking at sizing and wire tied to it. (And this doesn't have to be a 'total loss' fire either....)

Not trying to be preachy, just really don't want you to end up on the short end of the stick if something bad does happen. Any way to add a new run? (Even surface mount?)

Good luck.

Freddi

thanks freddi but Id be screwed anyway as my garage is not insured......:shocking:
 

Viriiguy

Well-known member
Joined
Feb 5, 2012
Messages
185
Location
Knoxville Tennessee
Are you supposed to? no. However in my current rental.. The dryer was on a 20 amp breaker. It kept kicking it. two years ago I yanked it and put a 30 amp in it.

Never had an issue since.. And I have checked, the wires are not hot under load.

With that said... YMMV. Fishing a new wire is not that hard.
 

nmk_61802

Well-known member
Joined
Mar 6, 2008
Messages
965
Location
Central IL
On top of what everyone else has said, I questioned this when I first got my MaxJax, because they were inconsistent with what they said for ratings. Mine was an early one, so they may have changed, but the unit itself does not have a 30 amp plug on it. I called them and they said a 20 amp circuit would be fine. Been using mine for three years now and never had an issue on a 20 amp circuit (dedicated circuit).

Craig

I'll add this:

http://www.garagejournal.com/forum/showthread.php?t=37717&highlight=maxjax+breaker
 

mikeyr

Well-known member
Joined
Sep 16, 2005
Messages
1,971
Location
Santa Barbara, CA
I run my MaxJax on a 20amp circuit, not popped the breaker yet.

I would not change the breaker without changing the wires but I would try your MaxJax on the 20 and I bet it works, just like mine.
 

MoonRise

Well-known member
Joined
Nov 5, 2010
Messages
4,025
Location
NJ
Can you? Sure.

Should you? Different question and the answer is "It depends".

But in general the answer is "No, do not go and put a 30 amp breaker in place of a 20 amp breaker because the wiring is most likely 'sized' for the 20 amp load and -may- overheat if a 30 amp load is used with wiring sized for a 20 amp load."

Some (limited) exceptions may exist for things where "duty cycle" come into play.

But in general, for some "outlets" wired up on a 20 amp circuit breaker then the answer is almost always "No, don't replace the existing 20 amp breaker with a 30 amp breaker".
 

nmk_61802

Well-known member
Joined
Mar 6, 2008
Messages
965
Location
Central IL
Wrong thread, he is talking about a heater here.

Seems to me like he is asking about a Maxjax like everyone else believes:dunno:


I have a Maxjax that requires 30amp breaker. My garage is fairly new, but has 20amp breakers for wall outlets. Can I just replace one with a 30amp breaker to use for the Maxjax? Thanks,

Don Ivey
Smithfield, NC
 

gezn2

Well-known member
Joined
Oct 27, 2011
Messages
240
Location
SW WI
You might get by for years...
I've found myself tearing out and redoing 'safe enough' stuff I did years back as I learn more about what's required by Code.
The wisest advice I ever heard about wiring is that every single article in the NEC got there because Somebody Died.
 
To avoid these ads, REGISTER NOW!
Top Bottom