64coupedeluxe
Well-known member
Hi All,
Model # 59TN6A 2 stage 96%
IU (thermostat) SYSTXCCITC01-A
Software 131 493-14.02
Firmware 2.5.5.1.6.8
Natural Gas
Hi all,
This unit is just over 10 years old and never had an issue. I was getting a code 32 Low heat PS did not close or reopened.
If open for longer than 5 minutes, inducer shuts off for 15 mins before retry. If opens during blower on-delay period, blower will come on for selected blower off-delay.
Check for
Proper venting
Air leak between vestibule and blower compartment.
Restricted vent
Disconnected or obstructed pressure tubing.
Defective or miswired pressure switches
Excessive wind
Plugged condensate drain
Water in vent piping, possible sagging pipe
Defective inducer motor
Low inducer voltage (115v)
Not sure if this is just a coincidence but the infinity thermostat had not connected to the Carrier website/server for some months. This is an on going Carrier problem across all infinity thermostats. My heat had been working fine and then I noticed it was connected to wifi/carrier server. Well then my heat failed to work.
When heat is called for, the startup sequence commences. Gets to the inducer motor stage, which runs but goes no further. And just keeps running.
My early attempts to trouble shoot had me switching from heat/hold- how we always operate the system, to one of the pre set schedules. This got the furnace to run for 5 or so minutes. So then I switched back to hold and can't get it to operate again.
I cleaned out the condensate trap, it had little water in it but did have a very small amount of black grit in it. Cleaned all lines, no restrictions or problems. As far as I am aware, this style of trap does not need to be primed. Please correct me if I am wrong.
I removed the inducer motor and inspected the vent/******(known carrier problem). Totally clear and the motor housing is in good shape and clean.
Vacuumed both pvc vent lines and get really good suction. Got nothing out. Also put a fish wire up both from the outside for 25ft prior to vacuum.
HSI measured 46.5 ohms, which is in spec.
Purchased a manometer from amazon.
T'd in reading of .060 in hg. My pressure switches are rated at .30 and .75 in hg. Not sure if my cheap meter is reading right or not but it is lower than what the switches need. *Defective inducer motor is one of the culprits for code 32.
Disconnected vent elbow from inducer and got a reading of .119 in hg
I had also purchased new pressure switches as they were cheap and free return shipping and still had the same fault code. Replaced all vacuum lines with new vacuum line.
I then accessed the dealer/service icon on the thermostat. The fault code events are:
11/5 #31 High PS open 3 x
11/6 #32 Low PS open 3x
11/25 #31 HPS open 5x
11/25 #12 Blower on after startup 1x
11/26 #31 HPS open 1x
11/28 #32 LPS open 1x
11/28 #12 Blower on after startup 1x
12/4 #31 HPS open 9x
12/16 #32 LPS open 124x
12/16 #178 Indoor communication fault 5x
I forgot to mention that when the furnace first failed to provide heat I checked the Filter. It was on the dirty side and was due to be changed around now which is typically the time I get the yearly service. So I replaced it.
I was paying for the yearly service due to the warranty requirements from the installer/Carrier for the 10 year warranty. Which I'm pretty certain just expired a couple of months prior.
Code #31 High-Heat PS or relay did not close or reopened:
Check for:
Control relay may be defective
Gas valve mis-wired.
See status code #32
I watched a bunch of trouble shooting on Siglernorcal.com which is carrier tech training. So then I started to trouble shoot to see what voltages etc I had. Seeing I had in my mind about this all going **** up after it reconnected to the carrier server, I disconnected the IU (thermostat) from the wall to check my voltages. They all seemed good but when I reconnected the thermostat I got fault code 178 Indoor communication fault.
Thinking there was a break in my comms wires I cut back and reconnected. Same problem. Change to some spare conductors, same problem.
Took thermostat down to furnace and wired in short jumpers, same problem. Code 178
So I went into the Service icon, went to Installation and then hit Installation then Full Installation so that the IU (thermostat) could search for the indoor unit (furnace).
It could not find it after several tries and my only option was to select Demo Mode, which I can't seem to get out of...Help!
I have ohm'ed out both the board and the IU and they fall right around the carrier specs. Can supply these if req.
Voltage readings at ABCD connector(control board) with no UI connected
A-B 4.59VDC
A-C 4.6VDC
B-C .014VDC
C-D 28VAC
Voltage readings with C-D connected to UI but communications wires A-B disconnected from control board.
A-B 4.38-4.5VDC fluctuating
A-C 4.37-4.5VDC fluctuating
B-C 0.01VDC steady
C-D 28VAC steady
I saw one carrier video that stated during my second test with the UI partially connected that the first 3 readings should be fluctuating. Then watched another that stated they should be steady.
I saw mention to make sure that SW4-1 is turned off as this disables the communication lines, checked and was off.
Looked all over the board and nothing seems amiss.
At this point I feel like I'm nearly an authorized Carrier maintenance man
But am obviously a ways off, but feel like I'm close to getting this worked out, but need some expert advice. At this point it's not about paying for a service call, it's that I don't want to be defeated by this mongrel. We have a fire place insert that keeps the house warm so it's not an emergency.
We have a NG hot water heater that is working fine and also gas cooktop.
Not sure what I am missing as from my voltage and ohm readings the IU should be able to see and communicate with the furnace.
How do I get out of Demo Mode and what should my next troubleshooting steps be? Thanks for reading this far and any suggestions you can offer.
Model # 59TN6A 2 stage 96%
IU (thermostat) SYSTXCCITC01-A
Software 131 493-14.02
Firmware 2.5.5.1.6.8
Natural Gas
Hi all,
This unit is just over 10 years old and never had an issue. I was getting a code 32 Low heat PS did not close or reopened.
If open for longer than 5 minutes, inducer shuts off for 15 mins before retry. If opens during blower on-delay period, blower will come on for selected blower off-delay.
Check for
Proper venting
Air leak between vestibule and blower compartment.
Restricted vent
Disconnected or obstructed pressure tubing.
Defective or miswired pressure switches
Excessive wind
Plugged condensate drain
Water in vent piping, possible sagging pipe
Defective inducer motor
Low inducer voltage (115v)
Not sure if this is just a coincidence but the infinity thermostat had not connected to the Carrier website/server for some months. This is an on going Carrier problem across all infinity thermostats. My heat had been working fine and then I noticed it was connected to wifi/carrier server. Well then my heat failed to work.
When heat is called for, the startup sequence commences. Gets to the inducer motor stage, which runs but goes no further. And just keeps running.
My early attempts to trouble shoot had me switching from heat/hold- how we always operate the system, to one of the pre set schedules. This got the furnace to run for 5 or so minutes. So then I switched back to hold and can't get it to operate again.
I cleaned out the condensate trap, it had little water in it but did have a very small amount of black grit in it. Cleaned all lines, no restrictions or problems. As far as I am aware, this style of trap does not need to be primed. Please correct me if I am wrong.
I removed the inducer motor and inspected the vent/******(known carrier problem). Totally clear and the motor housing is in good shape and clean.
Vacuumed both pvc vent lines and get really good suction. Got nothing out. Also put a fish wire up both from the outside for 25ft prior to vacuum.
HSI measured 46.5 ohms, which is in spec.
Purchased a manometer from amazon.
T'd in reading of .060 in hg. My pressure switches are rated at .30 and .75 in hg. Not sure if my cheap meter is reading right or not but it is lower than what the switches need. *Defective inducer motor is one of the culprits for code 32.
Disconnected vent elbow from inducer and got a reading of .119 in hg
I had also purchased new pressure switches as they were cheap and free return shipping and still had the same fault code. Replaced all vacuum lines with new vacuum line.
I then accessed the dealer/service icon on the thermostat. The fault code events are:
11/5 #31 High PS open 3 x
11/6 #32 Low PS open 3x
11/25 #31 HPS open 5x
11/25 #12 Blower on after startup 1x
11/26 #31 HPS open 1x
11/28 #32 LPS open 1x
11/28 #12 Blower on after startup 1x
12/4 #31 HPS open 9x
12/16 #32 LPS open 124x
12/16 #178 Indoor communication fault 5x
I forgot to mention that when the furnace first failed to provide heat I checked the Filter. It was on the dirty side and was due to be changed around now which is typically the time I get the yearly service. So I replaced it.
I was paying for the yearly service due to the warranty requirements from the installer/Carrier for the 10 year warranty. Which I'm pretty certain just expired a couple of months prior.
Code #31 High-Heat PS or relay did not close or reopened:
Check for:
Control relay may be defective
Gas valve mis-wired.
See status code #32
I watched a bunch of trouble shooting on Siglernorcal.com which is carrier tech training. So then I started to trouble shoot to see what voltages etc I had. Seeing I had in my mind about this all going **** up after it reconnected to the carrier server, I disconnected the IU (thermostat) from the wall to check my voltages. They all seemed good but when I reconnected the thermostat I got fault code 178 Indoor communication fault.
Thinking there was a break in my comms wires I cut back and reconnected. Same problem. Change to some spare conductors, same problem.
Took thermostat down to furnace and wired in short jumpers, same problem. Code 178
So I went into the Service icon, went to Installation and then hit Installation then Full Installation so that the IU (thermostat) could search for the indoor unit (furnace).
It could not find it after several tries and my only option was to select Demo Mode, which I can't seem to get out of...Help!
I have ohm'ed out both the board and the IU and they fall right around the carrier specs. Can supply these if req.
Voltage readings at ABCD connector(control board) with no UI connected
A-B 4.59VDC
A-C 4.6VDC
B-C .014VDC
C-D 28VAC
Voltage readings with C-D connected to UI but communications wires A-B disconnected from control board.
A-B 4.38-4.5VDC fluctuating
A-C 4.37-4.5VDC fluctuating
B-C 0.01VDC steady
C-D 28VAC steady
I saw one carrier video that stated during my second test with the UI partially connected that the first 3 readings should be fluctuating. Then watched another that stated they should be steady.
I saw mention to make sure that SW4-1 is turned off as this disables the communication lines, checked and was off.
Looked all over the board and nothing seems amiss.
At this point I feel like I'm nearly an authorized Carrier maintenance man
We have a NG hot water heater that is working fine and also gas cooktop.
Not sure what I am missing as from my voltage and ohm readings the IU should be able to see and communicate with the furnace.
How do I get out of Demo Mode and what should my next troubleshooting steps be? Thanks for reading this far and any suggestions you can offer.
Last edited:
.......Now what?