To avoid these ads, REGISTER NOW!

Ceg single phase 230v motor need help

gmoscajl969

New member
Joined
Nov 25, 2017
Messages
1
Need help on how to connect this motor to my 240v plug need to know where the wires from my 240will go on the motor also can someone tell me how to read the information plate
 

Attachments

  • 20171125_013355.jpg
    20171125_013355.jpg
    139.5 KB · Views: 28
  • 20171125_011315.jpg
    20171125_011315.jpg
    145.7 KB · Views: 34
  • 20171125_014234.jpg
    20171125_014234.jpg
    148.5 KB · Views: 35
Last edited:
To avoid these ads, REGISTER NOW!

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
The pics arent clear enough for me to read but that is iec nomenclature. Do a google search for iec motor reconnection diagrams and you will find what you need
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,940
Location
NJ
It is a Permanent Split Capacitor (PSC) Motor.
It has a squirrel cage rotor and a stator. The stator has two windings – main and auxiliary winding. It has a capacitor hard-wired in series with the “start” winding. There is no centrifugal switch.

5 Hp = 3.7 KW
1690 RPM (4 pole)
230VAC, 60HZ = Rated voltage (95 – 105% rated voltage = rated output)
19.6A = Full Load Amps at rated output
Class F insulation = Insulation Temp Rise = 100C
Ser.S = 1 (Duty Cycle – S1 means continuous duty and Service Factor is only 1.0)
IP 55 ~ Dust tight, Protected from water jets
Power factor ~ 0.9
Capacitor = 70 micro Farad, Voltage rating = 460 VAC
Motor size (frame size) = 112

Screen Shot 11-27-17 at 06.11 PM.jpg
Anlauf = “Start” winding (determines direction of rotation)
Betrieb = Run winding

No mention of overload protection. Should install something.
 