Central air quit.... any tips?

John T

Well-known member
Joined
Nov 15, 2011
Messages
903
Raised ranch/ air handler in attic

the system is working but blowing warm air....



compressor lines are warm and looking inside,it is not sweating like when working normally.



system installed in 2007 never had any freon leaks / nothing rusted or rotted...

I guess a leak is possible of course..



Anything I can check /self diagnose before I call the HVAC guy to get over sometime next week..



I'm thinkin maybe a bad relay or switch? :dunno:



The dogs can't seem to figure it out either... :D

06ef379569e652b618be7526dab9ed1d.jpg

59a8b50f176dd6c1d7c67bbc75f5eb13.jpg
 
To avoid these ads, REGISTER NOW!
OP
J

John T

Well-known member
Joined
Nov 15, 2011
Messages
903
Wouldn't a bad cap prevent the compressor from starting?

Mine starts


Sent from my iPhone using Tapatalk
 
OP
J

John T

Well-known member
Joined
Nov 15, 2011
Messages
903
Cap looks ok
Not bulged

dccf56b1bebc4df573bf59165e86c493.jpg



Sent from my iPhone using Tapatalk
 
OP
J

John T

Well-known member
Joined
Nov 15, 2011
Messages
903
I'm going upstairs to take stuff apart

B4 it gets hot


Sent from my iPhone using Tapatalk
 

danski0224

Well-known member
Joined
Jan 29, 2005
Messages
13,466
Location
Near Naperville, IL
the system is working but blowing warm air....



compressor lines are warm and looking inside,it is not sweating like when working normally.



system installed in 2007 never had any freon leaks / nothing rusted or rotted...

Are you indeed sure that all of the components are operating (energizing)?

Lets see, 2016-2007=9. It is quite possible that there are leaks, most often from the indoor coil. Normally, these would not be obviously visible (nor is all of the coil surface area typically visible as-installed).

Leaks are a PITA to chase down. Less than honorable HVAC companies will instruct employees to cry "Freon leak" or "cracked heat exchanger" as a motivator or scare tactic to sell new equipment. The majority of residential HVAC companies operate on performance based pay, so selling a new system is far more profitable than repairing the old.

Unless it's painfully obvious to the naked eye, best thing to do is install UV dye, recharge, run the system and check back later. Note that not all of the coil surface area and joints are typically visible, and may not become visible without component dis-assembly.

It is acceptable to identify the "Freon leak" or "cracked heat exchanger" to the customer and then make an educated decision about system replacement, as spending what could be a grand or more on repairs may not be cost effective based upon system age.

More often than not, unsubstantiated claims are made as a scare sales tactic.

Good luck.
 
OP
J

John T

Well-known member
Joined
Nov 15, 2011
Messages
903
well,
my coil upstairs was quite dirty... I gently vacuumed brushed the big stuff.... going down for a can of foaming spray now...

not sure if that was 100% the problem... but it needs cleaning in any case..

272fd83c8455754a3372e088adc5c5ed.jpg
 

TractorJeff

Well-known member
Joined
Dec 8, 2013
Messages
3,309
Location
Elkhorn, WI
WOW!
That's really filthy!
What are you running for an Air Filter?
Hopefully not one of those cheap Fiberglass ones.
 
OP
J

John T

Well-known member
Joined
Nov 15, 2011
Messages
903
9 years

Yes i use a regular filter


Sent from my iPhone using Tapatalk
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
Are you indeed sure that all of the components are operating (energizing)?

Lets see, 2016-2007=9. It is quite possible that there are leaks, most often from the indoor coil. Normally, these would not be obviously visible (nor is all of the coil surface area typically visible as-installed).

Leaks are a PITA to chase down. Less than honorable HVAC companies will instruct employees to cry "Freon leak" or "cracked heat exchanger" as a motivator or scare tactic to sell new equipment. The majority of residential HVAC companies operate on performance based pay, so selling a new system is far more profitable than repairing the old.

Unless it's painfully obvious to the naked eye, best thing to do is install UV dye, recharge, run the system and check back later. Note that not all of the coil surface area and joints are typically visible, and may not become visible without component dis-assembly.

It is acceptable to identify the "Freon leak" or "cracked heat exchanger" to the customer and then make an educated decision about system replacement, as spending what could be a grand or more on repairs may not be cost effective based upon system age.

More often than not, unsubstantiated claims are made as a scare sales tactic.

Good luck.
A freon leak and a cracked heat exchanger are 2 completely unrelated issues.
Most freon leaks are find/repair are in the shRader valves where gauges hook up on condensing unit.
A valve core screwdriver for fixing car tires is a handy tool for tightening them up.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
well,
my coil upstairs was quite dirty... I gently vacuumed brushed the big stuff.... going down for a can of foaming spray now...

not sure if that was 100% the problem... but it needs cleaning in any case..

272fd83c8455754a3372e088adc5c5ed.jpg
Ive seen worse;)
Depending on where you live most box stores sell the basic pleated white filters for a couple bucks each,they work a lot better than the fiberglass ones.
Just make sure you check it every month,especially with dogs. (Ask me how I know this:lol:)
 

Attachments

  • 20160909_203159.jpg
    20160909_203159.jpg
    146.5 KB · Views: 38
OP
J

John T

Well-known member
Joined
Nov 15, 2011
Messages
903
I think the compressor is bad

I cant hear it running with my stethoscope
Only the fan


Sent from my iPhone using Tapatalk
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
One side of capacitor can be bad without it bulging,it may be worth a few bucks to gamble on a new capacitor before calling a service guy.
Just make sure to kill the power and discharge both sides of the old one first.
 
OP
J

John T

Well-known member
Joined
Nov 15, 2011
Messages
903
If the capacitor was bad wouldn't the fan stop working?

The fan starts up and works fine

Sent from my iPhone using Tapatalk
 
OP
J

John T

Well-known member
Joined
Nov 15, 2011
Messages
903
I need to find out which wires are which
So I can test continuity of the compressor
9dc3f2f3513258c6c7a5b21a564e4924.jpg



Sent from my iPhone using Tapatalk
 
To avoid these ads, REGISTER NOW!

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
If you want to check the compressor I'd pull the top off of the condensing unit,then just pop the cover off the leads going into the compressor.
Pull the wires off and check it there.
I'd test the cap first though.;)
 

gregtwojeeps

Well-known member
Joined
Jul 30, 2013
Messages
5,096
Location
Ky
Have you checked the load side voltage on the compressor contactor while it is pulled in to be sure you are getting 240 V to the compressor ? Sometimes a contactor can have one pole of the two bad and not allow enough voltage to the compressor and it will just hum. Just a thought.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
Have you checked the load side voltage on the compressor contactor while it is pulled in to be sure you are getting 240 V to the compressor ? Sometimes a contactor can have one pole of the two bad and not allow enough voltage to the compressor and it will just hum. Just a thought.

He seems to be getting 240v to run the fan anyway.
 

samss

Well-known member
Joined
Aug 20, 2014
Messages
502
Location
Conway, AR
The compressor terminals will be marked (C) common, (S) start, and (R) run.
Common (C) to Start (S) plus Common (C) to Run (R) should always equal Start (S) to Run (R).*@#$ (C-S) + (C-R) = (S-R).*@#$ Common to run should be the lowest reading.*@#$ Common to start should be the mid-range reading. Start to run should be the highest reading.

C-S 3.68
C-R 1.35
S-R 5.03
Of course, if any combination shows open the compressor will not run.
Also check the terminals to ground for a short.
 

chrispyny

Well-known member
Joined
Nov 7, 2013
Messages
467
Location
albany, ny
what was the grand total of repair costs please? Wondering what a visit like that costs in your area, or for that matter, mine...
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
Look at the shape and exact location of the hole.

It must have been vibrating abrading against the line right in front of it, until he bent it over a bit to separate them.

I assume the tech checked the previously touching pipe as well. Marc
Now I see it.
I really need to break down and buy a new computer,trying to look at stuff on my phone screen is driving me nuts/blind!:lol:
 

bonneyman

Well-known member
Joined
Apr 22, 2010
Messages
8,836
Location
Desert SW
I have the exact same weighing scale. :thumbup:

What gas did the tech install - one of the drop-in alternatives? Because the can on R22 is green, on R410a it's pink.
 
OP
J

John T

Well-known member
Joined
Nov 15, 2011
Messages
903
total
600 clams.

3.5 hours labor
227 gas.

company rates...:(

I got the guys # for future moonlight work.

yeah,
r22 substitute... supposed to be cheaper $$ R438A

2 tubes rubbing...

funny thing... pressure test showed no loss...

UNTIL I spotted the tube and separated them..... then a slight loss...
a slight cleaning of the tube revealed the hole.

the other larger tube was fine.

He used brazing rod and closed the hole.

ice cold house tonight. :bounce:
 