All wiring and panels are within the same 30x50 metal building.

The current service panel is 200 amps.

I am adding a subpanel on the opposite end of the building that I want to have 100 amps.

The length of the run from panel-new panel is approximately 90'. Total length needed is estimated at 360'. 90 (Hot A) + 90 (Hot B) + 90 (Neutral) + 90 (Ground).

I have calculated the voltage loss and have concluded the correct wire for this length is 1 AWG copper in order to maintain less than 3% loss.

The subpanel neutral and ground will be isolated.

I believe a separate gound rod(s) is not necessary for the new subpanel.

I intend to run the same 1 AWG THHN/THWN-2 copper back to main panel for both legs, the neutral and the ground in 1-1/2" schedule 40 pvc.

Do my calculations for gauge compute?
How do I calculate the appropriate ground size?
Is conduit necessary if the wires are setting on an open ledge? (Consider the potential of rodents)

Anything else I may be overlooking?
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
No, it doesn't compute.

I'd recommend #3 hots/neutral and a #8 green.

We'd run 1 1/4" emt for this feeder in a metal building or possibly MC cable if protected from physical damage.
 
OP
C

chevroletfreak

Well-known member
Joined
Aug 2, 2008
Messages
102
I used southwires' calculator. I used 100' run of 120v that has 100 amps and <3% loss.
 