chevroletfreak
Well-known member
- Joined
- Aug 2, 2008
- Messages
- 102
All wiring and panels are within the same 30x50 metal building.
The current service panel is 200 amps.
I am adding a subpanel on the opposite end of the building that I want to have 100 amps.
The length of the run from panel-new panel is approximately 90'. Total length needed is estimated at 360'. 90 (Hot A) + 90 (Hot B) + 90 (Neutral) + 90 (Ground).
I have calculated the voltage loss and have concluded the correct wire for this length is 1 AWG copper in order to maintain less than 3% loss.
The subpanel neutral and ground will be isolated.
I believe a separate gound rod(s) is not necessary for the new subpanel.
I intend to run the same 1 AWG THHN/THWN-2 copper back to main panel for both legs, the neutral and the ground in 1-1/2" schedule 40 pvc.
Do my calculations for gauge compute?
How do I calculate the appropriate ground size?
Is conduit necessary if the wires are setting on an open ledge? (Consider the potential of rodents)
Anything else I may be overlooking?
The current service panel is 200 amps.
I am adding a subpanel on the opposite end of the building that I want to have 100 amps.
The length of the run from panel-new panel is approximately 90'. Total length needed is estimated at 360'. 90 (Hot A) + 90 (Hot B) + 90 (Neutral) + 90 (Ground).
I have calculated the voltage loss and have concluded the correct wire for this length is 1 AWG copper in order to maintain less than 3% loss.
The subpanel neutral and ground will be isolated.
I believe a separate gound rod(s) is not necessary for the new subpanel.
I intend to run the same 1 AWG THHN/THWN-2 copper back to main panel for both legs, the neutral and the ground in 1-1/2" schedule 40 pvc.
Do my calculations for gauge compute?
How do I calculate the appropriate ground size?
Is conduit necessary if the wires are setting on an open ledge? (Consider the potential of rodents)
Anything else I may be overlooking?