Circuit breaker addition

zendriver

Well-known member
Joined
Dec 10, 2014
Messages
30,482
Location
Indiana
Only had this a couple years, but this as a Siemens load center in the garage

Trying to figure out the proper style of breaker to put in it want to add a couple of 20 amp for now

Thanks

IMG_1473.jpeg
 
To avoid these ads, REGISTER NOW!
OP
Z

zendriver

Well-known member
Joined
Dec 10, 2014
Messages
30,482
Location
Indiana
So, Siemens QP will be ok for other sizes as well?

I’ll probably add for a bigger air compressor later.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Yes, QP is the right style if you don't need gfci or afci in the breaker.

The "branch breaker" column is what you want to look at
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,107
Location
Central Iowa

 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,775

bronc076

Well-known member
Joined
Jul 17, 2023
Messages
190
Location
Ozarks
It's frustrating that some panels/ breaker combinations that physically fit are not approved, no doubt due to lack of testing and certification. I get it, it's all about safety. Maybe a square D breaker does not apply the proper clamping force on a Siemens bus, who knows why some are approved and some are not, it depends on vendor testing. Maybe it's politics or business! It would be nice if there was body like NIST or IEEE that developed standards for manufactures to follow, or at least comply with. It would be a lot easier to figure out what worked where. For now we just need to read the label on the panel, and who has time to read these days! :)
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,107
Location
Central Iowa
It's frustrating that some panels/ breaker combinations that physically fit are not approved, no doubt due to lack of testing and certification. I get it, it's all about safety. Maybe a square D breaker does not apply the proper clamping force on a Siemens bus, who knows why some are approved and some are not, it depends on vendor testing. Maybe it's politics or business! It would be nice if there was body like NIST or IEEE that developed standards for manufactures to follow, or at least comply with. It would be a lot easier to figure out what worked where. For now we just need to read the label on the panel, and who has time to read these days! :)
I don't remember what it was about but I know it wasn't breakers when I asked an inspector why I couldn't do something using a product that I thought would be better for the application. (I was looking for permission, there wasn't a failed inspection) He agreed but said because it's not listed. I asked why and the response was that the manufacturer has to pay to get a listing and then pay a fee for every listing for every product sold. Square D would have to pay for a listing to replace Siemens, then pay for at least two listings on every breaker sold. I don't think there is a darn thing different, design wise, between an Eaton BR and a CL, but they only have to pay for the extra listings on CL sales while they only pay for the BR listing with BR breakers. That whole thing might be rubbish, but it makes sense to me.

Now I'm gonna be up all night trying to remember what I wanted to do.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,775
It's frustrating that some panels/ breaker combinations that physically fit are not approved, no doubt due to lack of testing and certification. I get it, it's all about safety. Maybe a square D breaker does not apply the proper clamping force on a Siemens bus, who knows why some are approved and some are not, it depends on vendor testing. Maybe it's politics or business! It would be nice if there was body like NIST or IEEE that developed standards for manufactures to follow, or at least comply with. It would be a lot easier to figure out what worked where. For now we just need to read the label on the panel, and who has time to read these days! :)
SQ D /Schneider states that only SQ D breakers should be used in their panels & they would be hypocrites if they were to have breakers classified for competitive makes of panels.
 