Circuit question

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,388
Location
Texas
I’m just starting to lay out the circuits for my little 25’x25’ shop. It will be powered by a victron inverter and LiFePO4 batteries.

Essentially, a small inverter air conditioner, several quad boxes spread around, and LED lighting.

I’m reality, I’ll only be using one or two of the quads at any one time. Small table saw, drill press, etc.

I’m thinking I need to keep the lighting on a separate circuit to avoid interference. Is that right? Thanks
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Agreed, lighting is prudent to keep separate.

IMO, one 15a circuit for lighting with 14/2 and two 20a circuits for receptacles with 12/2. I would likely run a dedicated circuit for the a/c and 15a with 14/2 sounds fine for that.
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,388
Location
Texas
Thanks. I’ll run the numbers before pulling anything.

It’s odd for me to think of 14 gauge for anything. I’m so used to everything being 12 minimum from the old days.

I guess stuff like lighting is that much more efficient these days.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Thanks. I’ll run the numbers before pulling anything.

It’s odd for me to think of 14 gauge for anything. I’m so used to everything being 12 minimum from the old days.

I guess stuff like lighting is that much more efficient these days.
Copper has gone up a lot and with led's, you can run a lot of lighting on a 15a circuit. Just keep it to 12a or less since it would be a constant load (assuming 3+ hr use at a time)
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,000
Thanks. I’ll run the numbers before pulling anything.

It’s odd for me to think of 14 gauge for anything. I’m so used to everything being 12 minimum from the old days.

I guess stuff like lighting is that much more efficient these days.

talks of going to 16g for lighting circuits with 10a breakers
 
To avoid these ads, REGISTER NOW!

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,000

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,368
Location
Coastal NJ
Thanks. I’ll run the numbers before pulling anything.

It’s odd for me to think of 14 gauge for anything. I’m so used to everything being 12 minimum from the old days.

I guess stuff like lighting is that much more efficient these days.
How old are those days? I see plenty of houses from the 60’s with 15A circuits. Old 14 Ga. Romex.
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,388
Location
Texas
I guess I’ve been in my 50’s house for 30+ years. And older before.

An electrician opened one of my switches and saw a large bundle of soldered ground wires. “Not touching that.”
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,368
Location
Coastal NJ
My sons last house had BX with soldered connections wrapped in friction tape. I touched it. All of it. All gone now. I don’t know if it was 14 or 12. House was over 80 years old. I think it was built the day they first started using BX.
 

Mzungu

Well-known member
Joined
Sep 3, 2022
Messages
176
talks of going to 16g for lighting circuits with 10a breakers
Yep, 1.5mm2 (16awg) on 10 amp breakers is pretty standard for lighting in a lot of Europe and Africa. Of course they are also using a 230/400 volt system. I banned 1.5mm2 cable on my site because I caught the guys using it for sockets and A/C units.
 