Also, does it matter what buss bar I connect the ground to for this breaker(neutral or ground). My panel seems to have the neutral on the right and the ground on the left, correct? And they seem to be tied together, with neutral and ground from other circuits connecting to both. Is it just a matter of which one is closer?

From what I have read this is ONLY okay for the service panel, but not okay for a sub panel?
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
The idea is to insulate the neutral currents in a 4 wire system and hook everything thaty should be grounded together with a wire back to the service main neutral or ground bar in a service panel.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,020
Location
Modesto, CA
Also, does it matter what buss bar I connect the ground to for this breaker(neutral or ground). My panel seems to have the neutral on the right and the ground on the left, correct? And they seem to be tied together, with neutral and ground from other circuits connecting to both. Is it just a matter of which one is closer?

From what I have read this is ONLY okay for the service panel, but not okay for a sub panel?

The neutral and ground bars are bonded ONLY in the main service panel. After that they are to be separated on new installs and for detached structures post 2008 NEC code cycle. Pre 2008 neutral bus was allowed to be bonded to ground.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,756
It's just a switch, not a pull out disconnect. It's rated up to a 60A load and 10HP and is nonfused.

http://www.homedepot.com/p/Square-D...e-Over-Current-Protection-QO200TRCP/202353314

Q0200TR.jpg

It has a molded case switch installed in it, looks like a circuit breaker but is just a switch.
 
To avoid these ads, REGISTER NOW!
OP
G

GarageGuy89

Well-known member
Joined
Jul 12, 2016
Messages
367
Location
Olalla, WA
Is the panel pictured fed from another panel?

Nope.

Now I'm not the savy-est when it comes to this, but there is a separate line running from the power pole to the garage, separate meter, separate 200 amp service, and a separate bill from the power company. My deductive reasoning tells me that this is not a sub-panel. Was built in the early 90's.

So I take it that it's safe for me to tie the ground onto either bus bar?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,020
Location
Modesto, CA
Nope.

Now I'm not the savy-est when it comes to this, but there is a separate line running from the power pole to the garage, separate meter, separate 200 amp service, and a separate bill from the power company. My deductive reasoning tells me that this is not a sub-panel. Was built in the early 90's.

So I take it that it's safe for me to tie the ground onto either bus bar?

Yes. Both panels are main service panels since they are fed from separate meters.
 
OP
G

GarageGuy89

Well-known member
Joined
Jul 12, 2016
Messages
367
Location
Olalla, WA
Thanks guys. Got the circuit wired and everything running without getting buzzed. Was actually a lot easier then I though it would be.

Thanks again to everyone, couldn't have done it without you guys :beer:
 