I'm wiring up the "Texas Budget Self Build" and I have run into some confusion AND I've run into a new problem.
First, my specifics: 30x40x14 detached shop build; 200A service on the house (recent upgrade to support the shop build); 100A breaker in the Main panel in the house.
2AWG Cu THHN/THWN four-wire buried 20" deep, in PVC conduit for 50', new Sub Panel in the shop with 100A backfed main, 12/22 circuit box, will only use a few of them.
I will have a two-post lift (230V approx 20A). and a compressor (currently a little 3HP, planning to upgrade to 5HP). I have installed two 30A two-pole breakers 10AWG THHN in EMT. I will have three receptacle circuits and pretty minimal lighting.
At issue: I've read the myriad threads and stickied posts on sub panels and related subjects. These threads have been super-informative but have also added some fogginess to the subject in specific ways that I need clarity on. I have also talked with the inspector when I obtained the permit but I think he gave me some erroneous info. It was on the phone and I think I confused him on the build, he's not seen the site.
1.) The inspector told me that my EGC in my four wire feeder could be 10AWG. I installed it, but I'm fairly sure it needs to be 8AWG. I will replace it if need be.
2.) I've seen it stated here that the compressor must be hardwired, no plugs/receptacles allowed. If that's accurate, please tell me the criteria; is it based on application (compressor) or location (detached garage) or HP (current)? what about "portable" compressors on wheels? What about 3HP compressors?
3.) I read here that type MC (12/2 Cu) is "no different than NM cable in terms of its resistance to damage"....I assume it needs to be covered up (in a wall, etc). This messes up my plan! I bought a roll of the stuff and planned to make good use of it making drops to outlets from J-boxes along a common conduit. I had mentioned this plan to the inspector and he thought it was grand, so I don't think there's a problem with being accepted...but is it a *good idea*, or should I just go ahead and pipe each outlet? There will be pics attached below. I have run 3/4 EMT in three runs and planned to use the MC and clamps to provide drops to 4sq boxes mounted on the posts. Perhaps I need to get more pipe?
3a.) If it's no better than NM and not allowed in more locations/uses, then just what the heck is MC GOOD for? I mean, why do they even MAKE it?
3b.) I was planning to use the MC to go out to canopy lighting under the porch area. Can MC be used 'outdoors'?
4. The unexpected problem that must be addressed: I am running stranded THHN (10 & 12) and I have found that I am unable to get a secure connection on the neutrals and the grounds in the provided busses.
I have twisted the wire, folded it, doubled wires under one screw... The setscrew bottoms out, the strands spread/flatten and although you can't pull the wire out, you can easily move the wire. It is NOT a solid connection. I have older GE panels that don't have this trouble. What am I missing? What is the approved fix? I'm considering tinning (soldering) the wire ends; crimping something on them... what do you guys do for this?
5.) Known issues: I'm not finished with the work of course and I have not yet installed the ground rod(s). I do know I need this. My job is sending me out of town for a while so this is a good stopping point to get y'all's input on what I've got so far and how to proceed.
Please take a look at the pics, critique away, I want very much to know all of the details I have wrong so far.
The basis of the plan: a conduit run that crosses to the opposite corner of the shop, providing a drop for the two-post lift (red/blk 10AWG no neutral), a planned MC drop for the main lighting fixtures up into the peak area (blk 12 +neutral), two outlet circuits (red 12 +n and blue 12 +n) and then all the way to the corner for the compressor (brn&yel 10AWG no n). I'm sharing a single 12AWG EGC in this pipe. Is this OK?
There is another outlet circuit in the pipe above the panel (blue 12).
There are GFCI receptacles mounted at the panel and each outlet circuit is fed by one of these GFCIs.
While I won't skimp on wiring or safety-related things, everything else is budget directed. I'll be using things I have on hand, so the lighting will be two 4' LED shop lights over the work bench and on a 3way and two rather impressive high-bays, for now. Same with the AC: I'm going to put two 6000BTU air conditioners (120V, <6A) through the wall. Not ideal stuff, I know, but it's what I've got.
The light switch arrangement is a 3way for the bench lights; a switch for each of main lights, canopy light, entry light.
First, my specifics: 30x40x14 detached shop build; 200A service on the house (recent upgrade to support the shop build); 100A breaker in the Main panel in the house.
2AWG Cu THHN/THWN four-wire buried 20" deep, in PVC conduit for 50', new Sub Panel in the shop with 100A backfed main, 12/22 circuit box, will only use a few of them.
I will have a two-post lift (230V approx 20A). and a compressor (currently a little 3HP, planning to upgrade to 5HP). I have installed two 30A two-pole breakers 10AWG THHN in EMT. I will have three receptacle circuits and pretty minimal lighting.
At issue: I've read the myriad threads and stickied posts on sub panels and related subjects. These threads have been super-informative but have also added some fogginess to the subject in specific ways that I need clarity on. I have also talked with the inspector when I obtained the permit but I think he gave me some erroneous info. It was on the phone and I think I confused him on the build, he's not seen the site.
1.) The inspector told me that my EGC in my four wire feeder could be 10AWG. I installed it, but I'm fairly sure it needs to be 8AWG. I will replace it if need be.
2.) I've seen it stated here that the compressor must be hardwired, no plugs/receptacles allowed. If that's accurate, please tell me the criteria; is it based on application (compressor) or location (detached garage) or HP (current)? what about "portable" compressors on wheels? What about 3HP compressors?
3.) I read here that type MC (12/2 Cu) is "no different than NM cable in terms of its resistance to damage"....I assume it needs to be covered up (in a wall, etc). This messes up my plan! I bought a roll of the stuff and planned to make good use of it making drops to outlets from J-boxes along a common conduit. I had mentioned this plan to the inspector and he thought it was grand, so I don't think there's a problem with being accepted...but is it a *good idea*, or should I just go ahead and pipe each outlet? There will be pics attached below. I have run 3/4 EMT in three runs and planned to use the MC and clamps to provide drops to 4sq boxes mounted on the posts. Perhaps I need to get more pipe?
3a.) If it's no better than NM and not allowed in more locations/uses, then just what the heck is MC GOOD for? I mean, why do they even MAKE it?
3b.) I was planning to use the MC to go out to canopy lighting under the porch area. Can MC be used 'outdoors'?
4. The unexpected problem that must be addressed: I am running stranded THHN (10 & 12) and I have found that I am unable to get a secure connection on the neutrals and the grounds in the provided busses.
I have twisted the wire, folded it, doubled wires under one screw... The setscrew bottoms out, the strands spread/flatten and although you can't pull the wire out, you can easily move the wire. It is NOT a solid connection. I have older GE panels that don't have this trouble. What am I missing? What is the approved fix? I'm considering tinning (soldering) the wire ends; crimping something on them... what do you guys do for this?
5.) Known issues: I'm not finished with the work of course and I have not yet installed the ground rod(s). I do know I need this. My job is sending me out of town for a while so this is a good stopping point to get y'all's input on what I've got so far and how to proceed.
Please take a look at the pics, critique away, I want very much to know all of the details I have wrong so far.
The basis of the plan: a conduit run that crosses to the opposite corner of the shop, providing a drop for the two-post lift (red/blk 10AWG no neutral), a planned MC drop for the main lighting fixtures up into the peak area (blk 12 +neutral), two outlet circuits (red 12 +n and blue 12 +n) and then all the way to the corner for the compressor (brn&yel 10AWG no n). I'm sharing a single 12AWG EGC in this pipe. Is this OK?
There is another outlet circuit in the pipe above the panel (blue 12).
There are GFCI receptacles mounted at the panel and each outlet circuit is fed by one of these GFCIs.
While I won't skimp on wiring or safety-related things, everything else is budget directed. I'll be using things I have on hand, so the lighting will be two 4' LED shop lights over the work bench and on a 3way and two rather impressive high-bays, for now. Same with the AC: I'm going to put two 6000BTU air conditioners (120V, <6A) through the wall. Not ideal stuff, I know, but it's what I've got.
The light switch arrangement is a 3way for the bench lights; a switch for each of main lights, canopy light, entry light.