I am installing a 75,000 BTU Modine Hot Dawg heater. It will be vented vertically with double wall vent pipe, through the insulated attic (Blown-in fiberglass). Can I blow-in the fiberglass insulation and have it be in contact with the pipe?

Thanks
 
To avoid these ads, REGISTER NOW!

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
No you need a 1" clearance, a piece of single wall pipe 2 sizes larger is an easy way to do it, 6 inch pioe for a 4 inch b vent.

Sent from my SM-G965U using Tapatalk
 
OP
B

Best0186

Member
Joined
Dec 25, 2019
Messages
16
Location
Bismarck, ND
Thanks, I was looking at the class B venting and it said 1" clearance from combustible materials. I didn't know if fiberglass blow-in insulation was a combustible.
 
To avoid these ads, REGISTER NOW!

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,408
Location
N CA
Whenever you see a clearance you are best of to simply observe it. Splitting hairs with your insurance adjuster is not a winning hand
 

cadunkle

Well-known member
Joined
Feb 13, 2011
Messages
472
Location
NJ
The few times I've done B vent through a ceiling I've used a firestop support and boxed out the framing to ensure clearance and no insulation can touch the vent. I nail flashing to the box so it's a noncombustible surface and extends above the level of insulation. Use a ceiling collar on the inside to cover gap in drywall or whatever ceiling finish material you use.

https://www.ameri-vent.com/products/fsp/firestop-support
 
Last edited: