Comfort Zone CZ220 Heater

BearsFan315

Well-known member
Joined
Jun 12, 2014
Messages
689
Location
Portsmouth, VA
was pondering a way to more efficiently heat my 600sq ft garage so that i could do a little work out there. To darn cold here, been in the teens !! plus snow on the ground as well. Sorry, I am NOT good at dealing with the COLD.

read a few post on here about vairous heaters and methods. I have a Mr Heater 35-55k adj Torpedo heater, and that thing heats the garage up pretty quick. Only thing is it is LOUD and puts out Co2 & HUmidity in the air.

I spend most of my time in the garage working on restoring my 1929 Chevrolet. Also looking for something to keep the temps above freezing at all times.

Found this post Great price for a garage heater by pablo94sc and sparked my interest. It is a Comfot Zone CZ 220 it iss a 220v heater, adjustable thermostat, variable output, 3k, 4k, 5k as well as it can be ceiling mounted out of the way. Other perks are safety features for overheating, etc...

CZ220 Instructions & info
CZ220 Specs
 
To avoid these ads, REGISTER NOW!
OP
B

BearsFan315

Well-known member
Joined
Jun 12, 2014
Messages
689
Location
Portsmouth, VA
Broke down and ordered one on Friday !!

Just got notification that it was Shipped today (Monday) and is on its way.

Will post up picts when it comes in and wiring it up and mounting it.

Plan on mounting it up in the front corner, as it is close to the sub panel for wiring, as well as out of the way of traffic & walking around, also can project out over the shop easier from that angle.
 
OP
B

BearsFan315

Well-known member
Joined
Jun 12, 2014
Messages
689
Location
Portsmouth, VA
UPS Notification says Delivery By Thursday, so maybe an install this weekend ?!?

Really depends on the weather, snowing now and more on the way...

So over the Cold weather and Snow !!
 

trdirks

New member
Joined
Feb 7, 2015
Messages
1
I have 2 CZ220's sitting next to me waiting to be installed in my 24x32. I am not really ready for them since I have not added a sub-panel yet but I couldn't pass up the sale. Let us know how you like it.
 
OP
B

BearsFan315

Well-known member
Joined
Jun 12, 2014
Messages
689
Location
Portsmouth, VA
Got heater in last night, Surprised UPS delivered it in the Snow we are having... Going to unpack it and get it up this weekend, I hope. May not get it wired up but it should be installed...

Pictures are coming !!
 

pablo94sc

Well-known member
Joined
Jul 28, 2014
Messages
2,049
Location
Memphis
Take the front panel off and tighten the nut holding the fan blade on. It's loose from the factory and will cause the unit to vibrate like mad.
 

Gerald O

Well-known member
Joined
Mar 5, 2013
Messages
1,884
Location
NC
I put a long 10g wire cord on one of these and plug it into my welder outlet as a portable heater. The mounting bracket works as a carrying handle. Only downside is that the cord cost nearly as much as the heater.
 
OP
B

BearsFan315

Well-known member
Joined
Jun 12, 2014
Messages
689
Location
Portsmouth, VA
Was really hoping to get my New Heater installed and running this weekend to warm up the garage. since we were in the upper 20's most all weekend, would have been NICE :!
I went out to unpack and install my Heater... Unfortunately Found Out it was Damaged !!

Looks like it was dropped pretty hard on one corner. So took some picts and sent an email to them Saturday Afternoon. They called me back today and have to say customer service was very nice and asked NO questions, other than did i want a replacement or just to return it !! I asked for a replacement so they are sending me another one, as well as sending UPS Label so I can send this one back.

So will pack it back up, print and stick the label on the box and drop it off at UPS Store.

What I Got:
Heater Box 01
Heater Box 02
Heater Pict 01
Heater Pict 02
Heater Pict 03
Heater Pict 04
Heater Pict 05
Heater Pict 06
Heater Pict 07

Just looking at it Have to say it looks well built, and sturdy... Hence it had to be dropped pretty hard to do this damage. Hoping to get breaker installed and wire ran this week, so when the replacement arrives I can just install and hook it up. I will also put a 3/8" lag bolt and washers for the install. Plan to install so that I can rotate/ spin the unit, as I will mount it in the front corner of my garage by the man door.
 
OP
B

BearsFan315

Well-known member
Joined
Jun 12, 2014
Messages
689
Location
Portsmouth, VA
I put a long 10g wire cord on one of these and plug it into my welder outlet as a portable heater. The mounting bracket works as a carrying handle. Only downside is that the cord cost nearly as much as the heater.

Luckily a friend had some extra 10/3 he had left over from his garage build that was laying around so he brought it in and told me to use what i need, hopefully it will be enough to run from the panel to the heater location. Will just tie off the extra leg in the 10/3 since Heater only needs 10/2.

Like the Plug Idea, makes it Truly Portable !!
 
OP
B

BearsFan315

Well-known member
Joined
Jun 12, 2014
Messages
689
Location
Portsmouth, VA
Well dropped on the Damaged one today with UPS, it is on its way back, Replacement should be shipping soon...

I Hope . . .
 
OP
B

BearsFan315

Well-known member
Joined
Jun 12, 2014
Messages
689
Location
Portsmouth, VA
Got notification last night that the replacement has shipped !!
estimated arrival is Friday, so maybe install job coming this weekend

so far customer service has been top notch
 
OP
B

BearsFan315

Well-known member
Joined
Jun 12, 2014
Messages
689
Location
Portsmouth, VA
Well heater delayed until monday due to SEVERE Weather !!

So went out and ran the wire, installed the breaker, and drilled hole for mounting.

10/3 Wire & 30 AMP Breaker


30 AMP Breaker Installed in Sub Panel

Wire Ran & Coiled Ready for Heater

3/8" Lag w/ Washers Installed

I am going to install the Heater using the Center Hole so that I can rotate/ Swivel the Heater IF Needed. Other Option they offer is two holes spread out in bracket to SOLID mount.

Now waiting for the heater, rescheduled for MONDAY !! that should be a quick job... so I hope
 
Last edited:
OP
B

BearsFan315

Well-known member
Joined
Jun 12, 2014
Messages
689
Location
Portsmouth, VA
lol, same here, we almost hit 70 yesterday, and supposed to be 55-65 all week !!

considering the last 3+ weeks we have barely hit freezing temps !! lucky to get above 30
 
To avoid these ads, REGISTER NOW!
OP
B

BearsFan315

Well-known member
Joined
Jun 12, 2014
Messages
689
Location
Portsmouth, VA
Wooo... Replacement is Here, Looks like they FLAGGED the box as FRAGILE, not sure that helps any... seems more like a TARGET !!
Box As it Arrived Last Night
Comfort Zone CZ220 - Front View
...You can see the louvers that are independently adjustable
Comfort Zone CZ220 - Side Angle View
...You can see the Knobs for hanging bracker and angle adjustments
Comfort Zone CZ220 - Bottom Angle View
Comfort Zone CZ220 - Rear View

Hoping to get it installed here this week or weekend if time permits... Granted it is Supposed to be in the 60' all week, so really do not need it for HEAT. but will fire it up and test it out anyways !!

Also per others Recommendation and Comments, I removed the cover and tightened up the Nut on the Fan.
 
Last edited:
OP
B

BearsFan315

Well-known member
Joined
Jun 12, 2014
Messages
689
Location
Portsmouth, VA
Well took a few minutes and went out and installed the Heater. Since all the leg work was done, was a quick task. Under 30 minutes. Taking my time.

Bracket Mounted
Heater Mounted to Bracket
Internal Wiring
Wiring Diagram
All Wired Up
All Done and Ready to GO
All Happy in its New Home

Have to say it looks great in the corner. Granted it was 70 deg out, I fired it up and let it run to make sure it worked. on setting I (3000 W) I let it run, and using my Laser Thermo coil heat was around 200 deg F. switched over to setting III (5000 W) and coil heat was around 300 deg F. That little fan easily pushes the air out and around. do not want to stand in front of it tool long, may melt ya !!

If we get a cold day I will go out and fire it up to test its ability to warm up the garage !!

Happy and content with it so far... all in for under $150 I am happy
 

Burl

Well-known member
Joined
Sep 21, 2007
Messages
791
Location
Where Mountaineers are free
I got mine up over the weekend, works good. I kinda wish it had a stronger fan though. Also, I just got 2" of wet snow, supposed to be 50s tomorrow, 60s Wed.-Thurs.
 
OP
B

BearsFan315

Well-known member
Joined
Jun 12, 2014
Messages
689
Location
Portsmouth, VA
mine worked great, never an issue
set the fan speed and thermostat where i wanted it to maintain, and then turned it up when i went out there. the fan is NOT powerful but worked great in my 600sq ft area
 

akjose

Active member
Joined
Mar 30, 2012
Messages
33
Location
WV
mine worked great, never an issue
set the fan speed and thermostat where i wanted it to maintain, and then turned it up when i went out there. the fan is NOT powerful but worked great in my 600sq ft area
Does yours have a fan speed option. I thought there was only 1 knob or does it control both?

Any up dates on how it works in the colder temps?
I think this will work, and i plan on working on it some this weekend. I am not 100% that the contactor will work using the W wire for heat call.

I believe the fan on this model does not run after the element kicks off.

The reason i put this after everything was so you could still see that the unit had power. after thinking about it some more. you could put it between incoming line and the L1/L2 contacts and you would get the same thing and unit would kick on with heat call. Would have to have the transformer before the contactor so the thermostat always had power.

I also think the honeywell Aube 120/24 control transformer would work in this setting as well but i believe a dedicated 120v circuit would be needed somewhere (either inside the unit or nearest where the thermostat is.

If anyone has any criticism on this wiring, please feel free to beat me up.

5000w heater.jpg
 
Last edited:
OP
B

BearsFan315

Well-known member
Joined
Jun 12, 2014
Messages
689
Location
Portsmouth, VA
Thermostat/Fan control is on knob.
heat settings was the switch

heat on fan on

heat off fan off

like your thought of using a thermostat to CALL for heat when needed, and cutting off when not
 

zippi

Well-known member
Joined
Dec 31, 2020
Messages
90
Location
Southern Indiana
Got the Comfort Zone 5000 watt heater for Christmas. I knew my kids were getting it for me since I told them what I wanted. I ran 10/2 (orange) wire inside the wall to my panel and connected it to a 220 30 amp breaker. I bought a 6' whip wire to go from the junction box I installed on the ceiling to the heater. It is hardwired so I just use the breaker when I want to turn it on. My garage is 20'X25' with 10' ceiling and 3 walls have no insulation. The bracket to hang the heater seemed a little flimsy to me so I used 3 bolts to secure it to the ceiling.
Yesterday it was 32 degrees outside and within 1 1/2 hrs it was 55 degrees in the garage. That's plenty for me so that's where I set the thermostat. Well worth the $89.
 

Attachments

  • 20201228_124325.jpg
    20201228_124325.jpg
    65 KB · Views: 43
  • 10-2 Whip Wire.jpg
    10-2 Whip Wire.jpg
    56.6 KB · Views: 24

Loose Nut Buster

Well-known member
Joined
Apr 6, 2020
Messages
117
Location
Near my house in Houghton Lake MI
How bad does it beat you up on your electric bills, the cost of electric hear scares me
My detached garage is 26x36 W/10' 2x6 walls, cathedral ceiling & heavily insulated. Currently using an LP tanktop 30k radiant and easily heats it from 28° to 40° in an hr or so, Its connected to a 15' hose inside keeping it movable to where I'm working & plumbed to 100# tank outside. I use a small 6" fan to move the air around.
I stopped using my ceiling mount LP Reznor that has a standing pilot, I'm considering changing it to a hot surface ignition n not wasting the gas when I'm not using it.


Sent from my SM-T387V using Tapatalk
 

zippi

Well-known member
Joined
Dec 31, 2020
Messages
90
Location
Southern Indiana
How bad does it beat you up on your electric bills, the cost of electric hear scares me
My detached garage is 26x36 W/10' 2x6 walls, cathedral ceiling & heavily insulated. Currently using an LP tanktop 30k radiant and easily heats it from 28° to 40° in an hr or so, Its connected to a 15' hose inside keeping it movable to where I'm working & plumbed to 100# tank outside. I use a small 6" fan to move the air around.
I stopped using my ceiling mount LP Reznor that has a standing pilot, I'm considering changing it to a hot surface ignition n not wasting the gas when I'm not using it.


Sent from my SM-T387V using Tapatalk

I've just installed mine and I don't run it that much. Shouldn't see much difference. Maybe someone that has had theirs longer can chime in about their bill.
 

akjose

Active member
Joined
Mar 30, 2012
Messages
33
Location
WV


This wiring does work. The W1 and w2 wires only put out 8v when heat is off and 28v when heat is on. You can select either in the ecobee settings. Ecobee thought it was a boiler set up since I only had the Rc and c wire hooked up.
C does not go to ground, it must be to common back to the transformer. I also used a different contactor than the picture, I ordered the one listed but I was sent a dc coil version and it was much taller and wouldn’t fit, and it was dc.
So the ecobee wires are Rc (rh would not power it), C (24v common), and w1 or w2 (heat call).

After digging into this, I believe you could isolate the fan wires to their own contactor and have the ecobee control that contactor if you wanted to run the fan only, as well as, have it run for a few minutes after the heat call is off.

I still have to run the wiring and mount this thing. I currently have it wired into the panel with the whip hose I am going to be using and my thermostat just using really short wires. I hope to do this tomorrow. I’ll take pictures.

I think another thing that could be done is separate the 3k/4k/5k switch into two separate switches/relays (maybe a spdt) and have the emergency heat call from thermostat trigger the second stage ( I know some thermostats won’t run stage 1 and aux/emerg at the same time but the ecobee can be configured to run both simultaneously as well kick in the Aux if the temp delta is larger than a set value.




Sent from my iPhone using The Garage Journal mobile app
 

zippi

Well-known member
Joined
Dec 31, 2020
Messages
90
Location
Southern Indiana
Update on my Comfort Zone 5000 watt heater. I have been using it off and on now for a couple weeks. The heater works fine and gets my garage up to 50 degrees in about an hour are so with it being 32 degrees outside. Not bad since my ceiling and 3 of the walls have no insulation. The thermostat on this unit is the problem. When you have it running and set the thermostat at 50 degrees it seems to work ok. When I fire it up the next morning or a couple days later it runs and the temperature will go above 55 degrees or higher. For me it's not a big issue since I'm in the garage working and when I get hot I turn it down and when I'm on my pc I turn it back up so I'm playing with it all the time. Still a good unit and well worth the money.
 

krcoomer

Well-known member
Joined
Jul 22, 2016
Messages
379
Location
Bluegrass region
How bad does it beat you up on your electric bills, the cost of electric hear scares me
My detached garage is 26x36 W/10' 2x6 walls, cathedral ceiling & heavily insulated. Currently using an LP tanktop 30k radiant and easily heats it from 28° to 40° in an hr or so, Its connected to a 15' hose inside keeping it movable to where I'm working & plumbed to 100# tank outside. I use a small 6" fan to move the air around.
I stopped using my ceiling mount LP Reznor that has a standing pilot, I'm considering changing it to a hot surface ignition n not wasting the gas when I'm not using it.


Sent from my SM-T387V using Tapatalk

I just picked mine up. The way I have figured cost was multiplying the 5000W maximum by my kWh rate on the electric bill times how many hours a day I expect to use it. In my case it is 5,000X0.09278(my rate from the last bill)=46.39 cents per hour on high or about $1.85/day running 4 hours on high. I picked 4 hours because I seriously doubt I will keep it running very hard once I get the temp up in the morning. On a 30 day billing cycle and anticipating using it 25 of those days, I am looking at about $50 for being comfortable.
 